10/15/2012 4:39 AM
Is there any problem in quality of online UPS output (parallel redundant), if we isolate the battery bank. I heard that ripple content may go higher in the UPS output. Is it true? Or any other problem occurs on battery isolation except for non availability?
Pls help.
"Know something about everything and everything about something"
Re: UPS battery bank isolation
10/15/2012 4:46 AM
There is a philosilly basey fundamold that needs to be tackled first:
  • Either isolating the battery bank, or switching the unit to bypass, turns an UPS into an IPS.
Why would one want to do this <rhetorical question - NNTR>?
If one were worried about ripple with the battery bank isolated, the safer approach would be to put the unit in bypass instead.
As it is undoubtedly the best source of advice, one presumes the UPS unit manufacturer's telephone number is to hand?
Good Answers: 102
Re: UPS Battery Bank Isolation
10/16/2012 2:24 AM
It should be OK as the UPS will static switch straight through ie bypass.
As well as UPS functionality an online UPS is an excelent line filter (if a battery is present.)
Why do you ask?
10/16/2012 3:04 AM
I would like to know how the ripple content in the UPS output is getting affected if we isloate the battery bank for replacement/capacity testing etc........As clearly indicated by PWSlack,I can get the answer but I wanted to know opinions of the brilliant CR4 enginers wordwide also.(During battery isloation,we don't go to bypass,just let the UPS flow as it is.)Hope my question is here.
Good Answers: 102
10/16/2012 4:13 AM
Should be OK.
The rectifier will connect directly to the invertor which will ensure a clean sin wave output. (it is true sin and not modified sin right?)
A correctly designed and built UPS will have battery circuit breaker or fuse that when open will not impact operation unless you have a primary power outage of course.
If possible perform these tests when on generator and not grid supply to eliminate risk of outage outside your control. Check how much fuel you have or it could get embarrassing.
10/16/2012 8:47 AM
In an Online UPS, the Battery is necessary for a good reduction of ripples at the input of the Inverter part. The Output is normally filtered for a true sine wave UPS, but no battery will affect the voltage stability. The output may have extra ripples.
isolating the battery from the UPS is not an improuvement, therefore avoid it if possible.
Also, if the battery is out of circuit, why do you need the online UPS? If the main supply goes off, the UPS will also go off.
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member
10/16/2012 5:00 PM
Missing some important information here.
What size is the UPS?
Is it dual conversion or online?
How many Battery Strings are we talking about?
What Voltage are the battery strings?
All these questions will impact your approach.
For example if you have two (2) or more battery strings, you may be able to isolate one (1) string at a time safely, without impacting the UPS.
If it is a small office or self contained UPS, you are probably better off just going to by-pass and working on the unit offline.
If this is going to be a long term situation....just take the UPS offline and remove it.
If you are not going to replace the Batteries, the UPS is just a line filter and an overhead cost you don't need, not to mention a new failure point.
Regards,
Sapper
It's all about the Boom! - MythBusters
10/17/2012 4:19 AM
10/17/2012 4:21 AM
1.Its 25KVA UPS for DCS & other critical supplies.
2.It's a parallel redundant UPS similar to one shown below.
MY question is how the ripple content is affected when the battery bank is isolated.Battery would come in line only when incomer supply fails.
10/17/2012 4:01 PM
Giri,
The batteries in these UPSs is Always online unless there is maintenance being performed on them. The Battery Breaker is always closed.
The UPS will maintain the float (operational) Voltage and onliy discharge the battery on mains failure.
The example you have shown is a double conversion UPS with the battery on the DC bus. Unless you manually open the breaker the Battery will always be online.
If you do Open that breaker, you will be left with a very expensive line filter, depending on the UPS it will either operate with an Alarm of go ingto bypass after a preset time.
Back to the ripple... The AC ripple in the rectifier should be next to nothing in a good quality UPS to protect the batteries...Batteries do not like AC Ripple so the rectifier should be fully regulated.
Regards,
Sapper
10/25/2012 6:10 AM
Thank you Sapper...But my doubt still not cleared.How the ripple content in this UPS output affected when the battery bank is isolated.
10/25/2012 4:13 PM
Giri,
The Short answer is that the ripple is going to be 50/60Hz at the UPS output.
The output of the UPS is going to be AC at 50 or 60Hz depending on location.
Since the DC from the Rectifier is fully regulated to the DC bus there will be No Ripple left to impact the Inverter. You are only isolating the batteries...Not the DC Bus.
Regards,
Sapper
10/26/2012 2:28 AM
Sapper,
Extremely sorry for unable to understand the thing that why the ripple goes up in the UPS output if the battery is isolated(curse my mind!).The DC from the Rectifier is always fully regulated irrespecctive of battery in-line or not.
10/28/2012 5:08 PM
Giri,
The Output of the UPS is AC. Therefore 50 or 60Hz depending on spec or location.
The output of the Rectifier will be 0% or very close, regardless of the batteries.
Regards,
Stuart
10/17/2012 4:25 AM