Participant

Join Date: Oct 2012
Posts: 1

Volt Free Contacts on Boiler (UK)

10/15/2012 9:18 AM

I am somewhat confused by Volt Free Contacts, i have seen some sources say they are powered by low voltage from within the boiler and others say external.

Some seem shocked when i ask the above question, i am trainee technical and need to get my head round this.

Are the contacts powered by boiler main PCB or other? if other, what?

what would be connected to them?

Please explain in a full simple discription volt free contacts

Register to Reply
Pathfinder Tags: boiler PCB volt free contact
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: Volt Free Contacts on Boiler (UK)

10/15/2012 9:20 AM
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: Volt Free Contacts on Boiler (UK)

10/15/2012 1:49 PM

Go to Maplins and pick up a normally open momentary action pushbutton switch. You will be holding an example of a volt-free contact. That's all there is to it. Any mention of "internal power" or whatever is a contradiction of terms.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#3

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 3:11 AM

The volt free contacts are exactly what they say they are. A relay on the circuit board operates and drives a pair of contacts.

In some circuits the contacts might pick up 24VDC or 230VAC to switch on a device, lamp, relay etc so they would be 24V or 230V switched.

The advantage of voltfree is that within the parameters of the relay you decide the operating voltage. If you need to operate a water pump then you will put 230V live to one side of your volt free contact. The switched live then goes to the pump and the other side of the pump to neutral.

If you were switching a 24V relay you would introduce 24V to one side of your contacts etc.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#4

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 8:59 AM

To cut it short and avoid surprises, please understanVd the following:

Volt free contact: This contact is meant that you use an external contact to close it!

the internal Board requires you to close this (pair) of contact, just with a contact only, with out applying any voltages. It is not a contact on an internal relay!!! the internal board supplies the voltage! This is like having a push button to close a contact on a circuit and initiate an action ...

You can check it by energising the board and check the voltage between the contacts, using a voltmeter. You will read a small voltage, usually DC

THIS IS NOT A CONTACT TO ACTIVATE SOME EXTERNAL DEVICE. YOU JUST SHORT IT TO INITIATE AN ACTION OR GIVE A SIGNAL TO THE INTERNAL BOARD for further actions ...

CHECK the manual and be carefull. Any voltage applied to it from Outside will damage the board (Usually).

Register to Reply Off Topic (Score 6)
Anonymous Poster #2
#6
In reply to #4

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 9:16 AM

Do you ever read back what you wrote? It is garbled rubbish and misleading at best.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#9
In reply to #6

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 9:44 AM

Well I cannot judge YOUR level of comprehension since you are Anonymously logged in!

But in any case, which part was misleading?

A Volt Free means No voltage should be applied to the contacts, i.e. you cannot considere it as a relay contact, on an internal relay! BECAUSE if you do this, then using it to drive an indicator light, for example, you will be applying a voltage to drive the said light! Right? Then you will cause a damage to the board!

Volt Free means you can close this contact, using the contacts of an external relay, for example, in order to initiate an action within the board.

Any other meaning to this "Volt Free Contact" is misleading!! or correct the English!

Register to Reply Off Topic (Score 6)
Anonymous Poster #2
#13
In reply to #9

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 10:43 AM

I have underlined where you were VERY unclear (not what the OP needed!), the bold words are wrongly spelled according to the CR4 spell checker, or have a capital letter where one is not needed or not have one when one was needed:-

Volt free contact: This contact is meant that you use an external contact to close it!

Total rubbish, what did you mean????

the internal Board requires you to close this (pair) of contact, just with a contact only, with out applying any voltages. It is not a contact on an internal relay!!! the internal board supplies the voltage! This is like having a push button to close a contact on a circuit and initiate an action ...

WHAT INTERNAL BOARD? It will often be a pair of contacts on a relay, the exact opposite of what you wrote!!!

You can check it by energising the board and check the voltage between the contacts, using a voltmeter. You will read a small voltage, usually DC

What board again and why will you read a voltage on a pair of voltage free contacts? Somehow it seems to be missing the focal point....

THIS IS NOT A CONTACT TO ACTIVATE SOME EXTERNAL DEVICE. YOU JUST SHORT IT TO INITIATE AN ACTION OR GIVE A SIGNAL TO THE INTERNAL BOARD for further actions ...

Totally wrong! Often (as several people have already posted) it is used to link two pieces of equipment without the voltages of one affecting the other.

For example:- Heating systems are often controlled by a thermostat with a pair of voltage free contacts, my home system does. Also burglar alarm sensors often offer such a pair of contacts for use either by the main alarm controller, or to switch a light fitting or whatever.....It could even be that a heating boiler, has such a pair of contacts to turn on a remote indication of running or not for example. Maybe that is what the OP needs to know....

CHECK the manual and be carefull. Any voltage applied to it from Outside will damage the board (Usually).

Please tell us what board/manual you are talking about!!!!

I certainly could not understand from your post what a voltage free contact is, and I have been using them for very many years.....nobody could, certainly not the poor OP.

My level of comprehension is still top notch.....

Just to help you understand what we here are talking about properly, someone else wrote about it quite well, I forget who, check around for a recent, simple and easily understood post from today I think.....though it might have been yesterday....I will search it out and tell you the Post #....

Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#29
In reply to #13

Re: Volt Free Contacts on Boiler (UK)

10/17/2012 7:11 PM

Since we are at it, I do not think that the confusion has been removed completely:

Take a control device that has Input points and Output points:

1)- on a Boiler, you can have a [controller] that has inputs from a thermostat or a pressure regulator or a safety device. If all these devices were ON/OFF types, they will just close or open a contact which will be connected, each, to a dedicated input on the boiler [controller]. Therefore, the controller label for these inputs will be "Dry Contact" or "Volt Free" contact. This means that you should not have any external voltage source connected to them.

2)- On the same Boiler [controller], You will have some Output points to bring On the burner and other devices. These contacts could be labelled the same as above if they are operated by relays inside the control unit, and do not drive the devices directly from the controller power source. But this is not the same as 1) it will be a wrong labeling since there is a voltage applied from the external source. These should be labelled as relay outputs or SSR etc.

Therefore, it depends from the point of view:

In 1) above, it is a "Volt Free" contact for the boiler controller. This volt free contact is provided FOR the controller.

In 2) above, it is a "Volt free" contact for the Boiler panel ( everything outside the boiler [controller]). The volt free contact is provided BY the [controller].

{If you are critical about punctuations, use of capital letters and that sort of things, my apologies. English is not my mother tongue but I am sure that I can accommodate you if I wanted to waste more time on these matters. Anyway sorry for the inconvenience...}

Register to Reply Off Topic (Score 6)
Anonymous Poster #2
#31
In reply to #29

Re: Volt Free Contacts on Boiler (UK)

10/18/2012 3:40 AM

You are about 25% correct in this post.

Getting better!!

Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#33
In reply to #31

Re: Volt Free Contacts on Boiler (UK)

10/18/2012 5:18 AM

No need to be condescending.

I am sure that I am 100% correct.

A "Dry Contact" or a " Volt Free Contact" is relative to the equipment on which the labeling is affixed. Otherwise, the manual and the electric drawings should clearly show what they really are.

That's it. keep your assessment Or un-cloak.

Register to Reply Off Topic (Score 6)
Anonymous Poster #2
#14
In reply to #9

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 10:45 AM

Post # 8.

Register to Reply Off Topic (Score 5)
2
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#7
In reply to #4

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 9:22 AM

A volt free contact is what it says - it does not have a voltage.

It might be you need to operate a boiler with a voltfree contact such as a thermostat. The voltage the thermostat will see will come from the boiler and that might be say 24V.

The boiler might also have a relay with voltfree outputs. Like the thermostat this could be used in another circuit lets say to building management system or similar to say the boiler had fired up. The voltage would be derived from the building management system.

A voltfree contact is just that - no volts - and the voltage is derived from somewhere else.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10
In reply to #7

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 9:56 AM

As I commented just before:

Your first paragraph works well with me. The thermostat will need to have a volt free contact that closes or open depending on the temperature settings, to signal to the board that a set point was reached or exceeded ... BUT the thermostat does not rely on the supply from the board, via THIS particular contact, to operate.

Your last paragraph has nothing to do with "Volt free Contact" in the normal jargon of the control circuit Industry. It is an auxiliary relay (or transistor) contact point that is attached (figuratively) to a particular function of the board: remote Alarm , remote indicator of some status like Normal run, Standby, High water level, low water level etc that the user can use to trigger his own designed action based on these sontacts being closed or opened by the board circuitry.

If the manufacturer of the board has confused the meaning of 'Volt Free Cntact' then you will have a nasty surprise. Check carefully.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#12
In reply to #10

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 10:34 AM

the thermostat is volt free. There needs to be a voltage from somewhere and this somewhere is the circuit board. The boiler is asking for a volt free input. Without volts from somewhere it won't work.

The last part has everything to do with control circuits. The last thing you would want is for the boiler to push a signal that was biased to say 230V to a DCS system that wasn't expecting it.

Agree completely you need to check the wiring diagram and more so when it has been translated from something that involves symbols and squiggles rather than letters.

Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#5

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 8:59 AM

Un-assigned, unused, "spare" contacts that can be used when needed for the purpose of interlocking permissives and/or other control logic required to make the control circuit and/or machine operate.

In order to understand what voltage source is controlling the operation of the contact (make or break) you must consult the wiring or schematic diagrams to determine which control circuit or power circuit is providing power to the operating coil.

Example: Spare "voltage-free" contacts on a "sudden-pressure" transformer protective trip relay can/could be used to trip (de-energize) an auxillary breaker/contactor when the transformer trips to ensure the transformer is completely unloaded before re-energizing it.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 9:29 AM

Volt free (or potential free) contacts have no voltage on them from the device that is controlling them.

It will usually be a relay where the coil is being activated and deactivated by something like a controller or other machine, but no voltages are being applied to the contacts themselves from that machine.

It could even be the contacts from a push button that you are pressing with your finger......

Its just a pair of contacts opening and closing.....nothing more, nothing less......

If a voltmeter shows a DC voltage across them, either the voltmeter is defective or its simply not "volt-free".........

There is a very faint chance of an induced voltage when the contacts are closed, this will be an AC voltage, very tiny in level, so using the DC part of the meter will allow you to totally ignore it.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#11
In reply to #8

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 10:12 AM

Andy, I am sorry to disagree and also you have a contradiction in your comment:

"It could even be the contacts from a push button that you are pressing with your finger......"

This sentence resumes it clearly! The others are contradictory.

IF The contacts, which are from the interna board, have no voltage at all (0.00), then when you connect a push button and press, the contact will close (Short the contacts) on nothing, and nothing will happen!

Ex: If you have a PLC (programmable logical Controller) with Digital Inputs (DI). You can use these DIs to indicate that a push button was pressed ON. this DI is Volt FREE because you are closing the contact to send back a 24V DC from the PLC Common point: i.e. DI1 -- P/B -- Com of the 24VDC from the PLC internal circuit etc

The DOs (Digital outputs) are also volt free from the PLC, being relay contacts or Solid State contacts, and are used to operate external devices, BUT these are not Volt Free contacts since you have an external power source connected via these contacts.

If you use a "volt Free " Labelled contact like if it was an internal relay contact, then good luck! {In any case you will apply a certain voltage accross it to operate anything(!!?) }

Register to Reply Score 1 for Off Topic
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#15
In reply to #11

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 11:00 AM

this just isn't right. If you have a contact in the boiler circuit and an external contact you have 2 contacts in parallel.

The input to the boiler isn't a contact it is part of a circuit that needs a voltfree switch or contact to operate it.

A voltfree DO from a PLC is voltfree - it has no voltage. You bring an external voltage to the contact and then switch your circuit.

If the whole lot is voltfree then you need to get volts from somewhere and the PLC common 24V bus is usually a good place.

I think you are getting mixed up with a volt free contact and a circuit that needs a volt free contact to operate.

Register to Reply Score 1 for Good Answer
Anonymous Poster #2
#16
In reply to #15

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 11:37 AM

GA.

Register to Reply
Power-User

Join Date: Oct 2007
Location: S. California, USA
Posts: 279
Good Answers: 12
#17

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 12:43 PM

Every technical discipline has its own jargon.

For me the term Volt Free Contact is a confusing as we all know that a contact is of no value if it cannot switch a voltage or current.

In the discipline of controls, the term just means that the terminals are not connected and are available to connect to what every you wish. This is important distinction to the controls guys as frequently in a control system contacts have one of the terminals pre-connected to voltage bus.

The computer world would use the term "Isolated Contact". A device with a "Volt Free Contact" and a device with an "isolated contact" may be physically identical and manufactured on the same production line. They just have a different name because of the industry that uses them. The names of the same thing also change from country to country.

Confusing, you bet.

Register to Reply Score 1 for Good Answer
2
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#18
In reply to #17

Re: Volt Free Contacts on Boiler (UK)

10/16/2012 2:53 PM

The terminology I prefer is "Potential free" contact. But each to his own.....

I found the following:-

http://answers.yahoo.com/question/index?qid=20070601040505AAc51qB

http://wiki.answers.com/Q/What_is_potntial_and_potential_free_contact

http://www.plctalk.net/qanda/showthread.php?t=16832

http://www.control.com/thread/1012835604

http://www.control.com/thread/1026238307

http://www.eng-tips.com/viewthread.cfm?qid=80771

and this:-

I think that covers the question quite well........and shows that certain people here do not have a clue as to what it is......

Are you all happy now?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#19

Re: Volt Free Contacts on Boiler (UK)

10/17/2012 10:39 AM

I think in USA we use expression "Dry Contact". Think of it like a central heat/air cond system. The thermostat in my house is electronic, powered by 2 AA batteries. When the electronics senses the house is colder than the set point it energizes a relay in the thermostat. This closes a set of "Dry" or "Volt free" contacts. The thermostat does not send its 3 volt DC to the furnace. The furnace, on the other hand, does not know why the contact is closed. It just knows that when wire "A" is connected to wire "B" it should start into its heating mode. This could be because a manual switch has be closed, a relay activated or direct acting thermostat changed position. Your boiler seems to have everything in it to operate when told to by simply connecting one terminal to another, again, by a simple hand operated switch or more a complicated control system that closes a set of contacts.

All this said, don't think that there is no consideration of the voltage/current needed. Very small current at low voltage will require different contacts than a line voltage control system. Also, the wiring method (Conduit or just wire) will change.

Hope this helps. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#20

Re: Volt Free Contacts on Boiler (UK)

10/17/2012 2:13 PM
Register to Reply
Power-User

Join Date: Oct 2007
Location: S. California, USA
Posts: 279
Good Answers: 12
#21
In reply to #20

Re: Volt Free Contacts on Boiler (UK)

10/17/2012 2:45 PM

Joshi - This is a repeat of one of the links that Andy pointed out in his post #18 which is the best answer so far. (Of course, I think that post #17 is pretty good too.)

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#22
In reply to #21

Re: Volt Free Contacts on Boiler (UK)

10/17/2012 2:54 PM

It is not a repeat exactly. Please compare letter to letter in both the links, you will, I am sure, find the difference. Both the links may open the same web page, that is entirely a different matter.

Register to Reply
Power-User

Join Date: Oct 2007
Location: S. California, USA
Posts: 279
Good Answers: 12
#23
In reply to #22

Re: Volt Free Contacts on Boiler (UK)

10/17/2012 3:02 PM

Sorry - you are correct.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#26
In reply to #22

Re: Volt Free Contacts on Boiler (UK)

10/17/2012 3:45 PM

The minor difference is because one is for "voltage free" contact and the other is for "potential free" contact, which as we all here know are one and the same thing.

Minor wording changes only between the two entries....

Do remember that a "dry contact" is also the same thing. There may even be other names for such contacts that we have not even heard of up to now!!!!

Just all different words for the same thing.

You need to understand that, but if you still think that there is a difference, you may not understand correctly what it is!!!!!

We will see what you know and understand the next time you post....but do not get upset by my post, even if your understanding is at fault, you are certainly not alone here!!

Have a great day....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#28
In reply to #26

Re: Volt Free Contacts on Boiler (UK)

10/17/2012 4:03 PM

I do understand that Volt Free Contact is same as "dry contact" & rest assured, I will remember all that you said.

"We will see what you know and understand the next time you post...."

Who is "We", by the way?

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#30
In reply to #28

Re: Volt Free Contacts on Boiler (UK)

10/18/2012 3:37 AM

What a simple question to answer! Thanks!

"We" are the people on CR4 who follow such blogs as these, see that the blog is "going in the right direction & accurately" and feel no need to chime in and add to the general furor discussion themselves. CR4 is not a war zone.....

I even get private emails from some saying "well done" or similar. Sometimes even criticizing a particularly obtuse opponent!!!

I am sure that I am both not alone in receiving such email posts, as well as being one who also sits back and occasionally sends such personal posts when I see the need to support a CR4 colleague....

I would like to just add, in case it was not apparent to you, that your recent comment:-

I do understand that Volt Free Contact is same as "dry contact" & rest assured, I will remember all that you said.

Could possibly be taken (maybe wrongly) to mean that a "potential free" contact is not included. My apologies if I misunderstood your post in this manner.

Just in case that is so, please remember that a voltage can also be described as a "Potential difference".....so "Potential free" is the same as "volt free".

Do you feel the need for any further information on this subject? I will do my best to help.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#32
In reply to #30

Re: Volt Free Contacts on Boiler (UK)

10/18/2012 4:17 AM

I appreciate your reply. Thanks a lot Andy. I understand you better after reading your reply. Thank you once again. God be with you.

Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#34
In reply to #32

Re: Volt Free Contacts on Boiler (UK)

10/18/2012 5:24 AM

Thank you kind Sir!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#24
In reply to #21

Re: Volt Free Contacts on Boiler (UK)

10/17/2012 3:20 PM

Post #17 was pretty good....

At least since Posts # 17 & 18 "our friend" has not posted anymore of his daft, inaccurate, dangerous and misleading explanations......he knows who he is, as we do too!

Now if he is basically clever, he will not post here again....we will see!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#25
In reply to #24

Re: Volt Free Contacts on Boiler (UK)

10/17/2012 3:40 PM

Come on Andy, don't take it to heart. Live & let live.

Live and let live

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#27
In reply to #25

Re: Volt Free Contacts on Boiler (UK)

10/17/2012 3:50 PM

As such contacts can carry high voltages, start and stop heating systems or heavy plant, a wrong explanation could cause injury or worse......which is why I take it so seriously......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#35

Re: Volt Free Contacts on Boiler (UK)

10/18/2012 10:25 AM

Now its all sorted lets hope no ones spoils it with a question about contact wetting which is very different and does not involve water!

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#36
In reply to #35

Re: Volt Free Contacts on Boiler (UK)

10/18/2012 10:52 AM

Awww! Come on, why spoil the fun? -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#37
In reply to #35

Re: Volt Free Contacts on Boiler (UK)

10/18/2012 11:07 AM

LOL!!!!

....as against "dry" contacts?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#38
In reply to #37

Re: Volt Free Contacts on Boiler (UK)

10/18/2012 2:13 PM

Dry contacts can often be cleaned with wet'n'dry, unlike wetted contacts. (Methinks this line of thought has some potential !).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#39
In reply to #38

Re: Volt Free Contacts on Boiler (UK)

10/18/2012 2:25 PM

Good humor!

Great!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#40
In reply to #38

Re: Volt Free Contacts on Boiler (UK)

10/18/2012 3:14 PM

(Methinks this line of thought has some potential !).

Only if it is current! -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Register to Reply 40 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (9); Anonymous Poster (6); Circuit Breaker (3); JohnDG (2); Joshi (5); LAA_Lucke (6); SHOCKISCAN (1); silverfox (5); Snave (3)

Previous in Forum: 11kV Voltage Grade   Next in Forum: Flying Saw

Advertisement