Portable Generator

10/19/2012 10:03 PM

Back in ancient history, my wife bought a portable generator for Y2K. It is a Coleman Maxa 5000 ER Plus, Powermate model PMO 525302.02. We have lost the manual which would probably answer this question. It has both 110 and 220 receptacles. Using the manual, my son made up a cord which has a 110 V plug, and has a hot and ground wires connected together. The other hot wire is not connected.

Can anyone explain what this cord does and how to use it? Thanks.

__________________
Lehman57
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Portable generator

10/19/2012 11:34 PM

The 120V cord should have a hot and a neutral (grounded), but they should not be connected to each other. Your description seems unclear about this.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Mar 2012
Location: Hot Humid Houston
Posts: 229
Good Answers: 29
#2

Re: Portable generator

10/20/2012 1:49 AM

The cord is made for confusing parents. This is what sons do, and it worked!

I'm confused about how he made a cord using only a manual...haha.

If the cord has a 110/120 (household edison NEMA code 5-15 or possibly 5-20 for your cord) plug on it, then it can't really have a hot and ground (tied together) and then have "the other hot wire" as there is only one hot, one neutral, and one ground in a proper 120V cord. Perhaps the cord was made with the intention of tying the neutral and ground together, leaving the third conductor for the hot. BAD IDEA.

This would be very wrong and very dangerous, and might not trip a non-gfci breaker.

The cord could be used to blow a breaker, ruin your generator, start a fire, or hurt someone, and therefore should not be used until assembled correctly.

If you can send a drawing, or photo, of the cord in question, some CR4 folks can probably get this set straight.

Please don't use that cord until you know what's going on.

One more thought, and I have not googled your unit to see if it has this feature -some generators in this smaller size have a feature to tie two generator outputs together to provide more amperage. Perhaps your son was following the manual to make one of these jumper/tie cords? See? Now he's confused me too! Still - no using that cord till you get a definite answer.

__________________
txmedic3338
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#6
In reply to #2

Re: Portable generator

10/20/2012 5:45 PM

txmedic: He wasn't trying to confuse me--it was too long ago. Maybe just a mistake due to his youth; I won't be using this cord.

__________________
Lehman57
Register to Reply
Guru
Popular Science - Weaponology - New Member Hobbies - Fishing - New Member

Join Date: May 2007
Location: Aloha or
Posts: 659
Good Answers: 19
#11
In reply to #2

Re: Portable generator

10/22/2012 7:22 PM

Perhaps a call or letter to the manufacturer could help you:

Coleman powermate 525302.

4970 airport road
po box 6001
kearney, ne 68848

1-800-445-1805
1-308-237-2181

generally a power plug prong twisted 90 degree goes to 30AMP PLUG. I kinda doubt that this is the truth for your unit. Ask your son if he has the manual.

__________________
Closed biased minds are utterly impervious to any factual evidence which contradicts their beliefs
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#3

Re: Portable generator

10/20/2012 5:05 AM

A. 120 V, 20 Ampere Duplex Receptacle

This duplex is split so that 20 amps of current may be drawn from each half of the receptacle. However, total power drawn must be kept within nameplate ratings. These receptacles may be used along with the twistlock receptacle provided the generator is not overloaded.

B. 120/240 V, 20 Ampere Twistlock Receptacle

A maximum of 20 amps may be drawn from the 120/240 volt receptacle, provided it is the only receptacle used. However, current must be limited to the nameplate rating. If the 120/240 volt receptacle is used along with the 120 volt receptacle, the total load drawn must not exceed the nameplate ratings.

A. Two identical Receptacle , side by side

B. One Twistlock Receptacle, centred below Two identical Receptacle at A above

C. Circuit Breakers

The receptacles are protected by an AC circuit breaker. If the generator is overloaded or an external short circuit occurs, the circuit breaker will trip. If this occurs, disconnect all electrical loads and try to determine the cause of the problem before attempting to use the generator again. If overloading causes the circuit breaker to trip, reduce the load. NOTE:

Continuous tripping of the circuit breaker may cause damage to generator or equipment. The circuit breaker may be reset by pushing the button of the breaker. These two buttons are located at either extremes of 120 V, 20 Ampere Duplex receptacle.

I am unable to paste the image from PDF manual. Manual can be downloaded at:

http://www.manualslib.com/download/134031/Powermate-Maxa-5000-Er-Pm0525202-02.html

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#7
In reply to #3

Re: Portable generator

10/20/2012 5:52 PM

Joshi: I got the manual OK, but it is not quite the same despite the model. There is no twist-lock receptacle. The 110 & 220 receptacles are on a panel not on the end-bell of the generator. The 220 receptacle is similar to a 110, but with one prong turned 90 degrees. As said above, I won't be using this cord. Probably will destroy it.

Thanks for your extensive response.

__________________
Lehman57
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#4

Re: Portable Generator

10/20/2012 10:50 AM

Maybe to make sure the breaker trips on the generator. Possibly he was checking it for safety?

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply Score 1 for Good Answer
Participant

Join Date: Oct 2012
Posts: 1
#5

Re: Portable Generator

10/20/2012 2:41 PM

This makes no sense please revise the question

Register to Reply
Commentator

Join Date: Oct 2012
Location: Located in South eastern North Carolina, I am a retired Supt of Public Works. also I am wheelchair confined due to an INdustrial accident of the Bends (Caissone Disease) from a construction Diver/underwater mechanic.
Posts: 64
Good Answers: 2
#8

Re: Portable Generator

10/21/2012 12:13 AM

Each hot leg should be 110 vac and then the third one is ground, use a multi meter to check the power. From your description you should be either dead shorted or a 110 circuit. Or I am not reading your question correctly.

Register to Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#9

Re: Portable Generator

10/21/2012 9:11 AM

When in doubt hire a licensed electrician.

That is what I did for our portable genset, switchgear and wiring.....tied into the circuit breaker panel.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10

Re: Portable Generator

10/21/2012 11:34 AM

I found a similar link to the other one posted, I do not know if the manual is identical or has the difference that was mentioned, check it out:-

http://www.powermate.com/pdfs/2007/11/17/manual_pl0525202.02.pdf

Best of luck.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Participant

Join Date: Oct 2012
Posts: 2
#12

Re: Portable Generator

10/28/2012 10:30 AM

Yes, In order to get the 240v to work you must use the plug that you have described !!! I don't know why...I think it is the way that the panel box is wired. I lost my manual and I am trying to figure out why it was wired that way. I will post again when I find the wiring diagram

Register to Reply
Participant

Join Date: Oct 2012
Posts: 2
#13
In reply to #12

Re: Portable Generator

10/28/2012 11:03 AM

I believe that since the coleman is using a floating neutral on the three prong 240, connecting the neutral to ground on the 120 creates a "bonded neutral" . Does this make sense? I have been afraid to use it. BTW my generator came with the exact plug as described by the original post.

Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Bob Sullivan (1); CaptMoosie (1); frand603 (1); Joshi (1); Lehman57 (2); ozzb (1); silvCrow (1); Tom Wakefield (2); Tornado (1); txmedic3338 (1)

Previous in Forum: Making a Pump, Remote Relay Controller and a Load Controller Work Together   Next in Forum: Earth or ELCB?

Advertisement