Low Forward Power Protection

10/27/2012 4:17 AM

Why are we using low forward power protection relays for Turbo generators?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: LOW FORWARD POWER PROTECTION

10/27/2012 7:30 AM

Do your homework.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Low Forward Power Protection

10/27/2012 11:22 AM

Imagine your captive generator is in sync with the grid. The EHV side breaker of your transformer has tripped due to some fault. Now, you would not want to feed the excitation power of the HV/EHV Power Transformer. To avoid this situation, a low forward power relay is used.

Register to Reply Score 1 for Good Answer
4
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#3

Re: Low Forward Power Protection

10/29/2012 4:16 AM

Turbo generators are run by steam turbines. In case of turbine trip, if the generator remains connected to the grid, the generator will run as motor and rotate the turbine. With no steam in turbine, there will be air in the turbine casing. Turbine blades, specially low pressure turbine blades will offer heave windage loss thereby increasing the temperature of blades to very high value which will damage the turbine. When turbine is run by steam, temperature is limited to that of the steam. But when steam is not there, temperature will go dangerously high. So forward power relay is used to trip the generator thereby preventing the motor operation of the set. This saves the turbine from high temperature. Some utilities prefer reverse power relay over forward relay.

Register to Reply Good Answer (Score 4)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: Low Forward Power Protection

10/29/2012 9:23 AM

But this is called reverse power protection and NOT low forward power protection.

Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#5
In reply to #4

Re: Low Forward Power Protection

10/29/2012 9:41 AM

The purpose of both, reverse power and low forward power relays is same namely, to prevent damage to the steam turbine. In low forward power protection relay trips the generator circuit breaker when the power delivered to the grid drops below a certain level (typical setting being 0.5 % of full load). In reverse power protection relay operates immediately after the generator starts drawing power from the grid instead of delivering power to the grid. Both the philosophies are followed.

Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (2); Joshi (1); pcchatur (2)

Previous in Forum: High Voltage Cable Protection   Next in Forum: Stepper Motor

Advertisement