Diodes Blowing Under Load on my 550kw Diesel Generator

10/31/2012 3:16 AM

i have a cummins 550kw diesel generator that keeps on blowing the diodes when under load and current at about 750amps and the rating for the generator is 901Amps. The plate on which the diodes are installed is heating up after.

I have changed the AVR and thats ok.

Under no load the generator is running ok, with all phases balanced.

Anyone who can help?

Register to Reply
Pathfinder Tags: Generator
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Diodes blowing under load on my 550kw diesel generator

10/31/2012 4:08 AM

Cummins can help. Make the call.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Oct 2012
Posts: 3
#2
In reply to #1

Re: Diodes blowing under load on my 550kw/625kva diesel generator

10/31/2012 10:37 AM

Thanks PWSlack, but i had called them prior to posting this and They were suggesting i replace the alternator which is not an option for me at the moment as i want to try something else before comitting to the cost of a new alternator.

The alternator has been rewound both stator and rotor and all phases seem to be balanced. LIke i said before all phases at no load the voltage is a steady 400V, 400V and 399.0V

Generator rating is 400/230 V.

The diodes(70A) that are blowing are 3 of the +VE only. They blow at a load current of 700A and the rated full load current is 902A.

Any help as to what i must check would be great.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#3
In reply to #2

Re: Diodes blowing under load on my 550kw/625kva diesel generator

10/31/2012 10:31 PM

What is the voltage rating of the diodes?Check for loose connections on the load which could spike the voltage above the rating of the diodes.

If available, install a line monitoring recorder across the diodes to see what they are actually feeling when loaded.

What are the specs on your diodes?

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Power-User

Join Date: May 2008
Posts: 380
#4
In reply to #2

Re: Diodes blowing under load on my 550kw/625kva diesel generator

11/01/2012 2:17 AM

How did you measure the load current? is it a new design or was it working until now? If it is a new design, did you check the "I²•t" of diodes?...Seems the given data is too short.-

Register to Reply
Commentator

Join Date: Aug 2012
Posts: 68
#5

Re: Diodes Blowing Under Load on my 550kw Diesel Generator

11/01/2012 2:46 AM

If you have changed the diodes also with not same type .try to change them with fast diodes type (up to 500Hz ) high current more than (70 amp) and check the diodes heat after running not the heatsink plate ,should be little heat .check the rotor exciter(three phase coils connection ) and the main rotor exciter .

good luck.

Register to Reply
Participant

Join Date: Oct 2012
Posts: 3
#8
In reply to #5

Re: Diodes Blowing Under Load on my 550kw Diesel Generator

12/01/2012 1:17 PM

thanks. i have used high frequency diodes and temp is ok. MY new problem that has arrised is when loading the generator now says low frequency on the computer and shuts down power to the loaded equipment.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6

Re: Diodes Blowing Under Load on my 550kw Diesel Generator

11/01/2012 8:04 AM

Is this Alternator Brush-less? (Your Diodes are mounted on the Rotor Shaft?).

If Brush less: The AVR is driving the Exciter unit. This AVR has its own set of diodes to produce the required DC for the exciter. Are you referring to these diodes? if so, definitely the diodes should be rated more than 70A, more like 110 A for the 901A Generator. But then, the AVR is supposed to be already built for this rating!! Have you changed the AVR without checking the AVR's output?

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 24
Good Answers: 4
#7
In reply to #6

Re: Diodes Blowing Under Load on my 550kw Diesel Generator

11/02/2012 12:09 AM

This comment raises the relevant question, what is the current requirement of the exciter when the generator is at full load (900A) across the operating range of power factor. If more than 70A then this is likely to be your problem