Type Test of LV Switchgear Assemblies

11/07/2012 9:07 PM

Does a panel builder have to subject each rating of his panels to type test? Say, a PCC for 4000A rating has undergone the type tests as per Standard. Now, if he makes a 2000A PCC, can he not prove by calculations that the deisgn of the panel is adequate for the given bus bar size, clearances, etc.? I think, it is highly impractical to subject each rating of switchboards that are manufactured to type test. Of late, I have come across sucg demands from some clients. Is the demand correct?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Type Test of LV Switchgear Assemblies

11/07/2012 10:08 PM

If they want to pay for it, any demand is correct.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: Type Test of LV Switchgear Assemblies

11/07/2012 11:45 PM

Basically all the panel manufacturing had already have the standard of the busbar size, clearance distance and other the type test for all the different size and capacity of the panel. The insulation test for all the panel manufacturing is standard unless if the customer need some special test like temperature rise in which the customer willing to pay for it.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#3

Re: Type Test of LV Switchgear Assemblies

11/08/2012 5:11 AM

Hello Mr. Shivakumar.. logging in after a long time. The question asked by you is a common one and all panel builders are in doubt. I will try to decode this point.

Basically in IEC 61439, the main tests to be conducted are short-circuit withstand, IP test and temperature rise test. The main test is short circuit withstand. if we use 100 mm x 10 mm - 4 runs for 4000 A and conduct short circuit withstand of .. say...50 kA with the required bus bar supports and with adequate distance, and the busbars pass this test. Now.. if for 2000A i use 100mm x 10mm - 2 runs, then, in order to pass the test, the distance between supports need to be changed. This means that for each current levels, if the dimensions and no of runs for busbar is changed, then yes.. a separate test need to be conducted. you are true.. its impractical ... because in oder that busbars withstand 50 kA short-circuit level, the design of the supports and the distance between the supports should be constant. This means that irrespective of the normal current that busbars carry, they would have to be designed in the same manner for all the current ratings. Also, it is easier to prove theoretically by calculations, but those calculations need to be practically implemented. The above question needs to be elaborately discussed since it is a huge subject and all the view points cannot be explained in writing on the web.

Anyway.. to other forum members.. please convey your opinion on this matter, since in the new IEC 61439 series, totally type testing on panels is recommended.

Thank you

Register to Reply
Active Contributor

Join Date: Sep 2010
Posts: 17
#4

Re: Type Test of LV Switchgear Assemblies

11/08/2012 8:30 AM

If you see the chart, many tests can be done by assessment and comparison. Especially short circuit test. you can show this to your client .

Or u can ask the client to pay additional costs for fully type testing the panel.

Is 61439 already implemented in India? i thought it wasnt compulsory until 2015.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jul 2011
Posts: 48
Good Answers: 1
#5
In reply to #4

Re: Type Test of LV Switchgear Assemblies

11/09/2012 4:18 AM

@harrybrown, thanks for visiting our website It is good to see it being put to use elsewhere.

While the table shows the various options open to carry out design verification, there are rules and limitations applied to each of them, so it is important to understand what they are before you begin the process.

We would recommend that initially if you are not fully familiar with IEC61439 you should look to increase your knowledge by working with a specialist in that subject. This would allow you to make the correct decisions on this type of question. Unfortunately without seeing drawings and your current design verification reports it is not possible to say if your could use an alternative method of design verification or not.

Just to clarify one point made by @shanbhag there are 12 main clauses, as can be seen in the above table. To comply with IEC61439 you require design verification to each clause, you cannot pick and choose which ones to comply with and equally each is deemed to be important for the safe operation of your assembly.

Finally, don't forget that you must also implement a routine verification system (RVS) that proves your production assemblies still comply with the design verified assembly (s)

Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#6

Re: Type Test of LV Switchgear Assemblies

11/09/2012 5:37 AM

I thank you all for the further clarifications. As explained by Mr. Harry Brown, There are 12 clauses mentioned in the IEC and all are very important for the safe operation of the panel. As i mentioned, IEC 61439 is a vast subject and since the protection requirements are not standard and varies according to customer's requirement. Hence, the interpretation of IEC and the clauses has to suit the site conditions.

As regards in India,as per my experience and observation, very few know that such a standard exist, Even if one does know, No one really carries out all the tests for various current ratings of busbar. Since the market is a cost compeitetive one, the dimensions of the enclosure will not be standard. Hence it is not feasible to carry out all the tests on each panel, since the costs will be huge.

I thank all our forum members for sharing their opinion on this forum. Please go through websites of ABB or Schneider for further clarifications, since they do carry out fully type testing on their panels.

Thanking you

Register to Reply
2
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#7

Re: Type Test of LV Switchgear Assemblies

11/09/2012 5:45 PM

My view points are limited to Indian Context only. In my opinion if the manufacturer has got type tested the panel say 4000 Amps for thermal rating and 50 kA for short circuit rating it should be accepted for any ratings upto 4000 Amps and 50 kA. Supporting calculations for other ratings can be accepted, However for higher ratings it would be preferable for one more test to be conducted, it would be better for the manufacturer also.

When I had set up SSI unit in 1981, there were very few Panel builders and with test for 3200 Amps and 50 kA, we could convince our customers and all the leading consultants for orders without any insistence for tests for all the ratings.we could manage for almost 30 years.

But one thing I had to confess that we were very strict in our approach in submitting supporting calculations and following the design of the any panel as per type tested panel without compromising the quality and standards

Now scene has changed, there are many Panel builders in the market who makes one sample panel with the help of consultant gets their panel type tested just for marketing purpose to get orders. But these panel builders do not follow design of the type tested panel in regular production, for example one leading panel builder cum contractor in Chennai got somehow tested the Panel for 50 kA with supports of 20 mm thickness and support distance of 350 mm.The same contractor/cum panel builder in their regular panels uses 10 mm supports with support distance of 700 mm.But most of the panel builders follow the same tactics, this is not correct.

In Chennai one consultant made sample panel got it type tested for same rating for 5 different panel builders and obtained certificates for all the manufacturer.

Another aspect is that many of the consultants/customers do not even see the type test report and verify the product even when they visit for inspection. This is sad situation and panel builder take advantage of the situation.

The type test certificate has become just a tool to reject a vendor in view of the hectic competition

The customer/consultant can review the type tested report and calculation of the proposed panel, capability and Engineering background of the manufacturer and take appropriate decision whether to insist test certificates for all the rating or not. If there is change in design one more test with new design is preferred.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Good Answer (Score 2)
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#8
In reply to #7

Re: Type Test of LV Switchgear Assemblies

11/10/2012 1:12 AM

Dear Ram Vinod Sir,

You have hit the right spot with your good opinion and the real practicality going on in the present market . As regards the support thickness and the distance between the supports, i have a doubt. Suppose if a panel incomer is 800 A ACB and 80 x 10 mm- 1 run has to withstand a short-circuit of 50 kA, then i think that it would be a little tough call. Because the amount of heat generated and the mechanical stresses induced during the shor-circuit for 800 a BB system would be too large compared to a 4000 A bus bar system( 200mm x 10mm- 2 runs). Also the material of busbar is a important criteria. Short-circuit withstand for the same dimensions for a copper BB is different than that of Aluminium BB. So my logic, according to laws of physics is that , if a 800 A BB system can withstand Short circuit of 50 kA and this design is standardised, then we can prove by calculations that for any current levels for greater than 800 A can also be proved. Also the dielectric strength and thickness of busbar supports is important. Another doubt is that, what about the dropper busbars where the outgoing feeders are connected. infact if a 100 A BB system is connected to the droppers than , it calls for even more stringent design. I think as per the new IEC 61439, the panel has to be totally type tested, which includes not only the incomer, but also the busbar droppers and the outgoing feeders.

Yes, this is very vast subject and the application of the standard is highly subjective.

I request our forum members to share their good opinion on this matter

Thanking you

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#9

Re: Type Test of LV Switchgear Assemblies

11/10/2012 9:58 AM

"Does a panel builder have to subject each rating of his panels to type test?"

The short & long answer is yes. There should be no arguments.

Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

3PhaseDesign-Craig (1); harrybrown (1); Joshi (1); ramvinod (1); shanbhag (3); Simon Wan (1); Tornado (1)