Protection Relay Settings

11/27/2012 7:12 AM

Hi,

We have incomer with 34.5 KV system. and as per our contract demand we can draw power up to 25 MVA. from our electricity board we have been asked to set the Over current setting to 350 Amps. we have SEPAM Relay.( SCHNEIDER). but if we calculate, 350 amps works out to be 21.1 MVA. when we bought this to electricity board notice, they informe us that our VIT( very inverse trip curve ) is type1.2 hence !.2*1.732*34.5KV*350 corresponds to 25 MVA. I am not able to understand this TYPE1 and TYTPE 1.2 Curve setting. Is it ok to set like that. Czan any body throw some light on it

Thanks and Regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Protection Relay Settings

11/27/2012 9:55 AM

Yes, RTFM (Read The Fine Manual) that came with your relay to learn exactly how the settings affect the operation. In your case the electricity board has decreed that you are not allowed to exceed 25 MVA (peak) nor are you allowed to operate in the band between 21.1 to 25 MVA for any appreciable time.

The VIT curve allows you to operate for limited periods just above 21.1 but as you get closer to 25 MVA the time shortens quite rapidly. This is a form of variable demand limiting, and you will have to be very careful not start any loads with a high transient starting current (like a big motor) when you are on the steep portion of the curve or you may be dumped before the transient is over.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
2
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: Protection Relay Settings

11/27/2012 9:56 AM

The logic for the SEPAM relay's trip curves has a pickup setting "Is" that you specify (in this case 350A). The various time trip curves might pick up at that value, but if you look at the curve (most of which are some form of a time-inverse function), at minimum pickup it will take an extremely long time until tripping occurs.

For the Very Inverse Trip (VIT) curve, as well as some of the others, Schneider does not specify an actual time to trip value for less than 1.2 x Is. Since this is done in digital logic, it gives some "buffer" around the pickup setting. Only when current reaches 1.2x pickup will the relay actually start the timing of its trip circuit. Schneider calls it the "minimum operate threshhold."

You didn't say which model of SEPAM relay you have (although I think they all use the same curves), and which particular VIT curve specified (IEEE, IEC, IAC), but the snapshot of one of the types shows the curves not starting at 1.0x pickup, but rather at a somewhat higher point.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3

Re: Protection Relay Settings

11/27/2012 10:08 AM

I think the electricity board is correct. Look into the VIT Type 1.2 curve for the relay (http://www.powerlogic.com/literature/63230-216-208C1.pdf). With this type of the curve, the relay will not trip with I/Is less than 1.2.

However, I would suggest you to confirm it with the relay vendor.

Hope it helps.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

msamad (1); PeterT (1); RAMConsult (1)

Previous in Forum: Container Crane   Next in Forum: HRG on Medium Voltage Systems?

Advertisement