Dear All
Just a quick and straight forward question. I apologise in advance for asking such query but sometimes the simple things gets you a bit confused. The scenario is as follows:
We have a 45 KVa generator so if I am not mistaken this should provide a running current of approximately 63 Amps. The electrician wired the generator with a 4 x 16 mm2 4 core thermosetting cable through a 100 Amp MCB.
The situation is as follows:
Sporadically everytime the generator gets in during a loss of electrical mains the 100 Amp MCB latches thus not allowing the generator to supply power to the electrical system.
To my understanding the start-up (in-rush) current of a generator may be up to 5 times the running current so the combination of this the thickness of the cable and the rating of the MCB maybe affecting the tripping time of the MCB.
Would this community please answer the following questions:
1) Is the MCB tripping because of the generator in-rush initial currents?
2) Is the MCB tripping because it is a non-ideal wiring design?
3) Is the MCB to be replaced by an isolator? If so how the cableis to be protected against fault trips (short-circuits)?
With Kind Regards
RC