Basic Generator Setup Question

12/22/2012 1:29 PM

Dear All

Just a quick and straight forward question. I apologise in advance for asking such query but sometimes the simple things gets you a bit confused. The scenario is as follows:

We have a 45 KVa generator so if I am not mistaken this should provide a running current of approximately 63 Amps. The electrician wired the generator with a 4 x 16 mm2 4 core thermosetting cable through a 100 Amp MCB.

The situation is as follows:

Sporadically everytime the generator gets in during a loss of electrical mains the 100 Amp MCB latches thus not allowing the generator to supply power to the electrical system.

To my understanding the start-up (in-rush) current of a generator may be up to 5 times the running current so the combination of this the thickness of the cable and the rating of the MCB maybe affecting the tripping time of the MCB.

Would this community please answer the following questions:

1) Is the MCB tripping because of the generator in-rush initial currents?

2) Is the MCB tripping because it is a non-ideal wiring design?

3) Is the MCB to be replaced by an isolator? If so how the cableis to be protected against fault trips (short-circuits)?

With Kind Regards

RC

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#1

Re: Basic Generator Setup Question

12/22/2012 4:43 PM

It's always a good idea to hook things up exactly as specified. Your problem lies within the things that were done differently. Redo them according to the manual.

PS- Your "electrician" might be nothing more than a residential wire puller.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Basic Generator Setup Question

12/22/2012 5:02 PM

1) Is the MCB tripping because of the generator in-rush initial currents? What is the inrush/staring current of everything powered by the generator?

2) Is the MCB tripping because it is a non-ideal wiring design? No way to tell. How long is the run?

Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#3
In reply to #2

Re: Basic Generator Setup Question

12/22/2012 6:48 PM

I didn't mean to be hard on the OP, but I had a certified "electrician" come to my house to do some wiring. It took me 6 months to fix it.

I don't see it as a loss though. Knowledge gained.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
2
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4

Re: Basic Generator Setup Question

12/23/2012 12:13 AM

Dear sir

You have not indicated the out put voltage. The cable size and MCB rating depends upon voltage rating. You have not indicated the cable material copper or Aluminum

Let us assume the voltage is 415 V.

Then full load current of the generator will be 62 Amps.

Open air rating of 16 sq.mm Copper cable is 90 Amps after deration for temperature and method of laying the derating factor will be 0.7, then current carrying capacity of the cable will be just 63 Amps.

Both cable and MCB ,according to the above calculations are just sufficient. However for any electrical device it is better to have 25 % factor of safety.

Leaving apart, the MCB should not trip as long as the load current is within 63 Amps. Please check the load that will be connected to the DG and restrict it to 63 Amps.

Do not connect all the loads suddenly to DG, apply the loads gradually then MCB should not trip.IF it trips even then , there might be problem with the MCB.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #4

Re: Basic Generator Setup Question

12/23/2012 5:46 AM

...in which case it would be better to change the breaker for a 63A-trip-rating one.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jul 2011
Posts: 43
#12
In reply to #10

Re: Basic Generator Setup Question

12/23/2012 6:19 AM

Dear PWSlack

I think that it is the solution since with a 63Amp both conditions i.e. fault tripping one as well I<1.45Iz will be satisfied.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5

Re: Basic Generator Setup Question

12/23/2012 12:40 AM

Dear Mr.RyanC83,

You have not indicated the connected load details, and which one you are starting first. From working point of you, the highest H.P motor, should be started first, and the small motors later.

When the Higher H.P. Motor is started last, the kick load, which depends upon the type of motor, starter etc., will be a limiting factor.

DHAYANANDHNA.S

Register to Reply
Active Contributor

Join Date: Mar 2011
Posts: 17
#6

Re: Basic Generator Setup Question

12/23/2012 2:15 AM

As already pointed out by forum members, you have not indicated the voltage in order to arrive at the current rating.Probably the name plate detail will tell you the current rating.

I have not heard of start-up (inrush ) current for any generator though there may be inrush current for transformers and starting current for motors. I would suggest to keep tall the loads OFF during generator starting and and running.Switch on the loads one by one,the largest first and then the other loads in descending order allowing for few minutes in between each load.You will be able to locate the problem if any from the load side.For me it appears there is no problem with the rating of cable or the MCCB though they are rated critically assuming the voltage is 415 V, 3 phase and copper conductor cable

Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 10
#7

Re: Basic Generator Setup Question

12/23/2012 2:55 AM

Further to the previous comments from the forum members, please be advised that the isolator does act as a non auto circuit breaker (MCCB or MCB) so it will not trip for an overload but it will protect the incoming cable for short circuit current.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #7

Re: Basic Generator Setup Question

12/23/2012 5:47 AM

How?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 10
#15
In reply to #11

Re: Basic Generator Setup Question

12/25/2012 1:51 AM

Check the technical catalogues of circuit breakers & Isolators such as ABB Group Schneider and others,

Register to Reply
Member

Join Date: Dec 2012
Location: DK 7000
Posts: 6
#8

Re: Basic Generator Setup Question

12/23/2012 5:03 AM

If You want to switch a generator to a f.ex 440 v grid, You must set the generator no load voltage to 445 V and then syncronize the generator and the grid before switching.

then there will be only a small current running.

You can then adjust the reactive current ( kVAr ) by raising og lowering the voltage.

And You can raise the kW by increasing speed on the diesel governor.

Register to Reply
Associate

Join Date: Jul 2011
Posts: 43
#9

Re: Basic Generator Setup Question

12/23/2012 5:05 AM

Dear Forum Members

Thanks for your response and apologize for not answering straight away, I was sleeping:) it was night here.

To answer your queries the terminal voltage is 415 V that's why I have told that the full load current out of generator is approximately 63 Amps (sorry for not telling).

The problem is that the electrician has replaced the 100 Amp MCB twice already and still the problem persists. to my understanding you need to multiply a factor of 1.45 to a type C MCB thus it is actuallyrated as 145 Amp for a specific amount of time.

Now having the following data:

Vt=415V

Genset = 45Kva

Ib (design current i.e. full load of generator)=63Amps

In (rating of MCB)=100 Amps

Ct (derating factor temperature of 45 deg. Cel.)= 0.71

thus Iz=141 Amps

From the above data a 4 x 16mm2 cable is not sufficient since such a cable delivers approx. 90-99Amps

Now taking the situation that 4 x 16 Amps are used

condition Ib<In< Iz is not satisfied.

Can anyone tell whether my understanding is correct? or I am confusing things.

With much appreciation

Ryan:)

Register to Reply
Participant

Join Date: Aug 2009
Location: Mumbai, India
Posts: 3
#13

Re: Basic Generator Setup Question

12/23/2012 7:51 AM

Mr. Ryan,

A MCB tripps under two conditions:

1. Overload i.e. exceeding rated current

2. Short circuit

Overload at power on may be due to inrush current.It can be many time the actual load for a brief duration. During over load MCB trip by thermal action.Hence a delay.

When short circuit is MCB trips due to magnetic action hence instantaneous.

MCBs are two type: For normal electrical load

For Motor Load

Normal electrical load MCB operates faster under overload/inrush current than motor grade.

You can either select as 1.5 times calculated max. current or use motor grade MCB.

Detailed graphs are on manufacturer's data site.

D D Daga

Bubble Electronics

Register to Reply
Associate

Join Date: Jul 2011
Posts: 43
#14
In reply to #13

Re: Basic Generator Setup Question

12/23/2012 8:33 AM

Dear Mr. dmdaga

I concur with all what you have said. :)

Ryan

Register to Reply
Commentator

Join Date: Mar 2011
Location: off the beaten track, not quite whoop whoop nor humptydoo
Posts: 57
#17
In reply to #14

Re: Basic Generator Setup Question

12/29/2012 6:00 PM

What "type" of circuit breaker is it - B, C, or D-curve? Is it suitable for the load, ie. motors?

__________________
Everything works out in the end, just not neccessarily how you want
Register to Reply
Member

Join Date: Dec 2012
Posts: 7
#16

Re: Basic Generator Setup Question

12/25/2012 7:42 PM

Dear Ryan,

Herewith is my answer to your questions:

1. MCB tripping has nothing to do with the in-rush current since you have just started the generator without load. In rush current occures only after your generator stabilized at no load and switching on the MCB with transformer load.

2. MCB tripping has nothing to do with wiring design since your generator has started only and no load.

3. It is not advisable to replace your MCB with Isolator since it is your main protection of the generator. I woul advise to install more protection on your generator such as overcurrent / overcurrent ground faulth relay, Over/Under Voltage relay, Over/under frequency relay and overload protection.

The possible caused of the MCB tripping is your generator AVR wherein the voltage is not stabilized. There are MCB with internal over voltage protection that possible caused the tripping at no load.

Regards

Arnulfo Palacio

Register to Reply
Register to Reply 17 comments