My Utility Company Wants to Change my Supply from 230VAC

03/12/2013 2:33 PM

I have a 25 year old property on the small Caribbean Island of Nevis. There are 4 main structures spread over a 2 acre lot.

The island supply is officially 2 wires (L+N) 230V 60Hz and the property is wired and equipped accordingly, including 16kva diesel backup generator.

The increasingly dominant supply of North American appliances running off 110v means that step-down transformers are used everywhere, and all the younger houses in our neighborhood have hard wired transformers and mainly wired for 110v throughout (except where 230v is essential - pumps, heaters etc.). I too have added 110v circuits on hard wired step-down transformers to provide socket outlets for American products.

Step-down transformers hum away using energy even if no appliances are in use and my neighbors are acutely aware of this bearing in mind the high cost of electricity on the island. The utility company has agreed to convert our neighborhood to the American 3 wire system ( which I understand is 110/120v L1, 110/120v L2 plus N) provided all the residents agree.

But the fact remains that all our original socket outlets (still used for a large variety of equipment), water heaters, lighting and security lighting, fans and pumps still operate on 230v wired circuits. Even more important is the fact that our generator set and its associated gear is all designed to operate and feed on the two wire 230v standard. Changing the property to the new system would entail an enormous cost, not only financial , but in terms of disruption and inconvenience. Added to that, I do not have the confidence in local (mainly American trained) technicians to make reliable modifications to the European manufactured generator set.

So, reluctantly, I am the odd man out, all other residents being in agreement. Needless to say, I do not wish to hold the other residents back.

So my question is:

Is there some piece of equipment (bearing in mind the size of the property) which I can instal which will convert a new 3 wire supply back to 230v 2 wires as it enters the property? I also live in UK so pointing me in the direction of a UK supplier would be helpful. Thank you.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: My Utility Company Wants to Change my Supply from 230VAC

03/12/2013 3:23 PM

American-style supplies L1 and L2 are already at the correct voltage between them, so all that needs to happen in the absence of any applicable standards is a different connection at the distribution board, the change of all breakers from 1-pole to 2-pole ones and some re-jigging and removal of the existing step-down transformers. An electrician could do it in a day.

Make sure, though that the plugs and sockets for the two voltages supplied around the home are different: the last thing that needs to happen is for a 110V appliance to be plugged into a 230V supply!

Oh, and don't use fused plugs to British Standard 1363: there would be no fuse in the L2 wire and that's not a good thing as far as safety goes.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Member

Join Date: Mar 2013
Posts: 6
#4
In reply to #1

Re: My Utility Company Wants to Change my Supply from 230VAC

03/12/2013 4:59 PM

Thanks your prompt reply PWSlack. I am already aware of most of the points you have raised. I think you have underestimated the size of the property (see the size of our generator), and the fact that there are long distances involved (2 acres). A lot of the wiring uses 1.5mm cable which I fear will be inadequate for the lower voltage in each wire. (although I do not understand much about cable sizes)

We have 5 distribution boxes. There are probably 50+ single pole light switches which would have to be changed to double pole for safety, and in the case of 2 or 3 gang switches they may not fit into existing wall boxes. Our 230v ring main socket outlets are British type 13amp using square pin fused plugs. Your advice about fused plugs would mean we would have to change these as well. Then how to distinguish between the different voltage outlets?

The least hassle would mean an answer to my original question. If that leads to a prohibitive cost, then we will have to follow your advice, for which many thanks.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #4

Re: My Utility Company Wants to Change my Supply from 230VAC

03/12/2013 7:01 PM

<...1.5mm cable...inadequate...lower voltage...>

The original premise was about getting 230V from L1 + L2, so the voltage hasn't changed. It is current that determines conductor size, not voltage. Voltage determines the insulation quality.

The ring main installation new information is worrying, as it is designed for use with BS1363 fused plugs. With the change from L+N to L1+L2, there would be a live wire on the former neutral pin and BS1363 would be inapplicable. However a ring main is protected at 32A, so it is not applicable to non-fused plugs of a lower rating.

This is fast becoming a redesign-and-rewiring job rather than something an electrician could do in a day. How are other residents intending to cope?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#2

Re: My Utility Company Wants to Change my Supply from 230VAC

03/12/2013 3:57 PM

As far as the 16 VA gen set is concerned a common 5 - 8 KVA 120/240:120/240 step up/down transformer set up in an auto transformer configuration with the center tap as the common ground (L+N+L) would solve the compatibility issue.

Being you are already stepping much of your system voltages down by half the odds are you already have a number of compatible transformers around or know where you can get one that's large enough.

Register to Reply
2
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#3

Re: My Utility Company Wants to Change my Supply from 230VAC

03/12/2013 4:52 PM

"Is there some piece of equipment (bearing in mind the size of the property) which I can instal which will convert a new 3 wire supply back to 230v 2 wires as it enters the property? I also live in UK so pointing me in the direction of a UK supplier would be helpful. Thank you."

You indicated you don't want to use transformers because of their burden power load doing nothing. but if you really want to leave everything the same, install a 1:1 isolation transformer of the required full load KW, feeding 220 on the primary, no power source neutral connection, then the secondary of this isolation xformer, ground one of the lines, this then will be a neutral, and the other line will be L keeping every thing the same, and connect this to your existing circuit breaker panel. Your backup gen set will stay connected on the secondary side of this isolation xformer as normal, with a power transfer switch to isolate back feeding of power,

You still will need your step downs for the 115 uses. Or you could have a separate circuit breaker panel from the new island power system. You do want to keep these two power systems separate. If you size this panel large enougn, you could add 230 double pole breakers as needed when you switch over to new water heaters.

I don't know what your wire color code is for this 230volt system. I'm going to assume neutral is white or gray as it does not matter if a 115 or 230 volt system. But the L1 and L2 must be a color black and red being the typical 14/3 or 12/3 wire (non metalic or UF) with ground and neutral.

I think I understand what you are wanting.

__________________
ignator -
Register to Reply Good Answer (Score 2)
Member

Join Date: Mar 2013
Posts: 6
#5
In reply to #3

Re: My Utility Company Wants to Change my Supply from 230VAC

03/12/2013 5:11 PM

Your suggestion sounds hopeful, although I think I am getting completely out of my depth. Thank you.

Color codes are somewhat chaotic in this old property in a very small country!

Register to Reply
4
Power-User

Join Date: Sep 2011
Posts: 267
Good Answers: 7
#7

Re: My Utility Company Wants to Change my Supply from 230VAC

03/12/2013 11:56 PM

Lets go back to basics: The OP said The utility company has agreed to convert our neighborhood to the American 3 wire system ( which I understand is 110/120v L1, 110/120v L2 plus N) provided all the residents agree.

I'm not sure you understand the American system. There are really 4 wires. L1, L2, Ground and Neutral and we run at 60 Hz.

60 Hz equipment is likely to run on 50 Hz with some side effects, but systems designed for 50 Hz may not run on 60 Hz.

Simplifying.

What it looks like on the premise side is nothing more than a 240 V Center-tapped transformer. Ground and Neutral are connected at one point. The ground rod for the premise.

So, N and ground are at the same potential.

Between L1 and Neutral there is 120 V and between L2 and neutral there is 120 V.

Between L1 and L2, there is 240 V. Ground is protective and provides a reference and a place for fault currents to go.

The main breaker panel gets L1, L2, N and Ground. Neutral and Ground are connected together at this panel ONLY. Sub-panels keep the N and ground separated.

Breaker panels are known as "main Breaker" or "main lug". For this discussion a "main breaker" panel has a breaker that interrupts all the circuits in the panel. A "main lug" panel does not.

Since you mentioned generators, some panels can be purchased with an "a mechanical interlocked breaker". This allows "backfeeding" a panel through a breaker, but will not allow the main and the backfeed breaker to be on simultaneously.

The Neutral conductor carries the difference current between L1 and L2 and can change direction.

The panels are designed to accept 1 or 2 pole breakers. A 1 pole circuit is a 120 V circuit and a 2 Pole circuit is a 240 V circuit. The two pole breakers are mechanically interlocked. If one turns on, the other must. If one trips, the other must trip.

The 120 V Circuits consist of either (L1 or L2), Neutral and Ground. In the US they are wired with 14 AWG for a 15 A circuit and 12 AWG for a 20 Amp Circuit. The NEC requires stuff like 20 Amp circuits in Kitchens and GFCI's in certain locations. The wire is called things like 12/2 with ground. The ground conductor is uninsulated within the cable and is of a smaller gauge.

Our larger appliances and pumps are wired for 240 V. They can be 240 3-wire or 240 4-wire. Both schemes have L1, L2 and Ground. The Neutral is added in the 4-wire scheme.

That being said, an electric water heater or a large pump doesn't require a neutral.

Electric clothes dryers have problems all to themselves, but now 4-wire systems are required.

Now, many stoves etc are being made with electronic controls and to avoid using a 120 V controls transformer a Neutral is pulled.

Clothes washers and clothes dryers and window air conditioners typically use plugs. Water heaters, 240 V furnaces and central air conditioners use disconnects nearby.

The one thing we NEVER do is fuse the neutral. So watch British stuff.

120 VAC is common for controls in the home. 24 VAC for low voltage control wiring such as the central air conditioner.

Rewiring is bound to inconvienience somebody.

For the utility, it could just mean rewiring the transformers, a few locations at a time. At home, 4 homes are on one transformer. For the homeowner, he has to change the distribution main panel and who knows what else.

I'd suspect, that your set-up will mostly work as is except for the main panel and the transformer connections and neutral to the house. Your generator might cause a glitch in how that's wired. i.e. the output transformer there may have to be changed.

Once you have the 240 system in place, most stuff would likely work. Your 120 step-down stuff might likely work too. You would then remove your 120 step-down stuff as needed.

You would end up with a 240 system that was wired differently allowing the homeowners to run 120 V circuits as needed. They would likely have to be new because of the wire gauge problem.

Your "upgrade" becomes a stepping-stone, so to speak. I doubt that you would be able to convert the existing 2xx outlets to 120 V and to eliminate the 2xx/120 V transformers new wiring would have to be run, but it's not an IMMEDIATE problem.

Register to Reply Good Answer (Score 4)
Commentator

Join Date: Nov 2012
Location: Sunnyvale, CA
Posts: 62
Good Answers: 10
#8

Re: My Utility Company Wants to Change my Supply from 230VAC

03/13/2013 3:37 AM

I'm not sure if was clear from PWSlack's first answer, but the American 3-phase distribution system supports both 110 / 120 V and 220 / 240 V circuits. It simply depends on what taps on the supply transformer are used to make the circuit. If your utility changes to the American system, you will no longer need the step-down transformers you currently use to power 120 V appliances, but neither will you need step-up transformers to power your 220 V equipment. What you will need is separate circuits for the two classes of equipment, with different styles of plugs so that you can't inadvertently plug an appliance into the wrong circuit.

The American system has three lines in and four lines out of the supply transformer. The fourth line is the neutral line from the common point of a "Y" configured 3-phase transformer. A 120 V circuit is made by connecting between any of the 3 phase lines (L1, L2, or L3) and the common. A 220 V circuit is made by connecting between any two of the phase lines.

It's not truly 220 V; if the amplitude of the individual phase lines is really 120 V, the the amplitude between any two of them will be 2 * 120 * cos (30 degrees), or 208 V. But supply voltages normally vary a lot, depending on where one sits on the distribution lines and what other loads are operating. 208 V is generally adequate for appliances that are nominally 220 / 240 V.

An important caveat is that this "American style" 220 V circuit is not identical to a European style 220 V circuit. Besides the slightly lower voltage and the 60 vs. 50 Hz. issue, the major difference is that in the American system, both the power and return wires are "hot". In the European system, only the power wire is hot; the return wire is neutral. Normally that shouldn't matter; it would be a violation of safety codes and common sense to design a 220 V appliance that depended on the return wire being neutral.

If you suspect that any of your 220 V equipment is, nonetheless, so designed, then don't make a 208 V circuit between two of the phase lines. Use a 2:1 step-up transformer connected to one of the 120 V circuits, and tie one side of the secondary to ground. That will be the neutral return side.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Apr 2011
Posts: 188
Good Answers: 6
#9

Re: My Utility Company Wants to Change my Supply from 230VAC

03/13/2013 8:23 AM

Clear as MUD?

Better get a Qualified electrician....

Register to Reply
Member

Join Date: Mar 2013
Posts: 6
#10

Re: My Utility Company Wants to Change my Supply from 230VAC

03/13/2013 12:03 PM

I would like to thank everyone for the time and trouble you have taken.

KeepItSimpleStupid gave a child's guide to the American system which expanded my limited knowledge. Thank you!

As I indicated in my first post, re-wiring and re-equipping the entire property to match the proposed American supply, was never really an option due to the disruption involved. I just wanted some simple guidance as to how to change the new power supply as it enters the property to match the present setup.

Yes corbinstein, I will be getting a qualified electrician. I just need to understand what are his/her intentions, as I would for my car mechanic, doctor, dentist etc.

It looks like I will be going for

either (A) 1:1 isolation transformer idea suggested by Ignator meaning we would need to bring an extra wire in from the street

or (B) the 2:1 step up transformer suggested by Silverthorn where I assume we can just use the existing 2 wires from the street.

Now I have to think of cost/efficiency. Any views advantages/disadvantages of (A) & (B) would be much appreciated.

Register to Reply
2
Member

Join Date: Oct 2007
Location: Dayton, Ohio, USA
Posts: 8
Good Answers: 3
#12
In reply to #10

Re: My Utility Company Wants to Change my Supply from 230VAC

03/13/2013 4:43 PM

Ignore option (B).

Silverthorn describes a three-phase wye-connected distribution system, common in industrial installations. My plant uses such a system to provide 120 VAC from any of the three phases to the neutral and 208 VAC between any two of the three phases. I seriously doubt your utility is going to replace a 220/240 VAC 2-wire distribution system with a 4-wire 3-phase distribution system, especially in a non-industrial setting.

Option (A) does NOT require a fourth wire.

A 3-wire (L1-N-L2) distribution uses only three wires, one neutral and two "hot". The distribution at the street normally will "ground" the neutral there, along with the transformer ("pole pig") case, and the center tap on the low-voltage 220 VAC secondary. The "pole pig" transformer typically accepts high voltage, single phase, 2-wire and transforms it down to single phase 220/240 VAC 3-wire through a center-tapped secondary winding. The center tap is the neutral or N and is connected to earth ground, typically with a heavy gauge uninsulated solid copper wire stapled to the pole and connecting between a driven copper-clad steel rod, the transformer case and the secondary center-tap.

At the service-entrance distribution panel, the neutral is bonded (permanent electrical connection) to the "safety ground" SG in the panel and to another earth ground, typically a buried metal cold water pipe or another driven rod. From this point on to the user load there are either three or four wires: L1 and L2, N, SG for 220/240 VAC loads; L1 or L2, N, SG for 110/120 VAC loads. Most 220/240 VAC appliances do not need the N wire, but most do require the safety ground (SG) to be attached to the appliance metal frame. This type of load (typically a water heater or a motor) only needs three wires: L1, L2, SG. Most 110/120 VAC loads also only need three wires: L1 or L2, N, SG.

The line drops from the utility pole to the service entrance are typically in air and the wire is oversized somewhat to be sustainable against ice loading (not in your location of course!), wind loading, and weight. Only the two "hot" lines are insulated and they are usually loosely wrapped around the uninsulated neutral which actually supports most of the weight. Because the wires are in open free air, they are capable of much higher current (and resistive heat dissipation) than the same gauge wires installed in a wall or conduit. This means you probably would only have to run ONE additional wire to the street, along side your existing 2-wire feed. Even though the two "hot" wires in a 3-wire service drop will carry twice the current as the same load in a 2-wire drop, the original outside 2-wire installation should easily accommodate this extra current so that you only need to add one wire to obtain your 3-wire drop.

Hop

__________________
"Things should be explained as simple as possible, but not simpler." --A. Einstein
Register to Reply Good Answer (Score 2)
3
Member

Join Date: Oct 2007
Location: Dayton, Ohio, USA
Posts: 8
Good Answers: 3
#11

Re: My Utility Company Wants to Change my Supply from 230VAC

03/13/2013 1:51 PM

You must be very confused by now, considering all the "advice" posted. In my not so humble opinion, ignator gave the best and only advice you should follow for now: install a 1:1 isolation transformer between the 3-wire (L1-N-L2) feed from the utility and your existing 2-wire (L1-N) feed to your property. The secondary of the isolation transformer replaces the existing 2-wire utility feed. For reasons I will explain later, the secondary should be center-tapped.

Size the isolation transformer to handle the full load expected, say, 16 KVA if your backup generator fully replaces the power normally delivered by the utility service, larger if it does not. Fuse the L1 and L2 feeds from the utility to the primary of the 1:1 isolation transformer accordingly. Do not fuse the N wire. Connect the N wire from the utility feed to the N wire of your existing 2-wire feed and to a local grounding rod at the service entrance.

You may be able to find a suitable convection air-cooled transformer on the used equipment market… try E-Bay or other on-line market places. The efficiency will not be as great as a complete re-wire of your property would provide, but the cost will be significantly lower. If you later desire to "improve" the property, the changes to a 3-wire distribution can be made gradually over a period of several years on an "as needed" basis. It is absolutely imperative that you hire a qualified electrician to oversee these changes.

If you do "bite the bullet" and decide to make a full changeover to 3-wire, the same 1:1 isolation transformer can be re-purposed to connect the backup generator to the property feed in place of the utility feed, provided the isolation transformer secondary winding has a center-tap for the neutral connection. Plan accordingly when you initally purchase the isolation transformer.

You will need to install a double-pole double-throw break-before-make changeover switch that will disconnect the 3-wire utility feed and then connect the 3-wire backup generator feed coming from the center-tapped secondary of the isolation transformer. You probably already have a single-pole double-throw switch in place now that disconnects the utility 2-wire feed and replaces it with the generator 2-wire feed. However. in this case (complete changeover to 3-wire property wiring), the generator connects only to the isolation transformer, through an appropriately sized fuse or circuit breaker, instead of directly to the property wiring. You need to install a double-pole double-throw changeover switch in the isolation transformer's center-tapped secondary because you are now switching two "hot" wires (L1 and L2).

All that is much further down the road. Just remember to buy a 1:1 isolation transformer with a center-tapped secondary. Quite often such a transformer will have two primary and two secondary windings, each winding rated for 120 VAC. That makes it easy. Just connect the two primary windings in series and connect the two secondary windings in series. The connection between the two secondary windings serves as the center-tap. The connection between the two primary windings serves as an unused center-tap of the primary.

Hop

__________________
"Things should be explained as simple as possible, but not simpler." --A. Einstein
Register to Reply Good Answer (Score 3)
Member

Join Date: Mar 2013
Posts: 6
#13
In reply to #11

Re: My Utility Company Wants to Change my Supply from 230VAC

03/13/2013 5:11 PM

Thanks Hop,

Although I do not fully understand it, your advice will be passed on during discussions with the Utility Co. and our local electrician. Unfortunately, that will not be until May or June, the next opportunity I have to go down to the islands.

Thanks again.

Register to Reply
Commentator

Join Date: Apr 2007
Location: South Africa Pretoria
Posts: 59
Good Answers: 4
#14

Re: My Utility Company Wants to Change my Supply from 230VAC

03/14/2013 4:02 AM

Morning

I think that you are getting a genuine 2 phase system 180 degrees out of phase with each other. If it is so then you have 110 V using L and N and 220V using L1 and L2

Have a nice day

Carel

Register to Reply
Power-User

Join Date: Sep 2011
Posts: 267
Good Answers: 7
#15

Re: My Utility Company Wants to Change my Supply from 230VAC

03/14/2013 4:47 AM

Definitely NOT TWO PHASE: http://en.wikipedia.org/wiki/Two-phase_electric_power

Bi-Phase maybe, but not Two-Phase.

In normal "single phase" systems, the power comes in as single phase, the only difference is the center tapped secondary and that can't change the phase from single to two phase.

___

The OP just so happens to be the Odd man out with probably more "infrastructure" than the residents. 4 structures and a generator. So he almost counts as 4 residents.

The cheapest choice is really to keep his property wired the same way as it was by installing a carefully selected transformer which can be re-purposed from converting the new supply back to the old system or the genset to the new system.

One should also look into the Gensets current transformer connections and, at least, determine if the current genset can be re-wired for "bi-phase" power.

Register to Reply
Member

Join Date: Mar 2013
Posts: 6
#16
In reply to #15

Re: My Utility Company Wants to Change my Supply from 230VAC

03/14/2013 6:01 AM

"The cheapest choice is really to keep his property wired the same way as it was by installing a carefully selected transformer which can be re-purposed from converting the new supply back to the old system"


Brings me back to Ignator's solution. Thanks

Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

carel (1); corbinstein (1); hevans1944 (2); ignator (1); KeepItSimpleStupid (2); PatrickH (5); PWSlack (2); Silverthorn (1); tcmtech (1)

Previous in Forum: Computer Scienced Graduate Get Into Electrical Design Engineer   Next in Forum: Bus Bar Calculation

Advertisement