Generator Earth Fault Protection

03/30/2013 11:31 AM

What is the difference between 95% and 100% earth fault? And why 20Hz signal injection is used?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Generator earth fault protection

03/30/2013 11:37 AM

5%.

Maybe it's like just being a little pregnant?

Is there a real question here? What % fault would you consider acceptable?

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#2

Re: Generator earth fault protection

03/30/2013 12:39 PM
Register to Reply Score 1 for Off Topic
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: Generator earth fault protection

03/30/2013 1:35 PM
  1. 95% protection - only 95% of generator stator winding is protected (5% at "star point" end of winding is not protected).
  2. 100% - the whole of the winding is protected.
  3. Harmonics of fundamental and unbalance at fundamental cause star point not to be at zero volts. Measurement of voltage at star point gives some % of nominal on healthy system, limiting setting of relay to 5% or greater. Note that the usual construction of power transformers is not totally symmetrical and capacitance coupling from HV windings can cause an LV potential off-set.
  4. A short to earth less than 5% of turns from nominal earth potential at star point is not detectable. The displacement of the star point is less than 5% for a short to earth less than 5% of turns from earth end of winding.
  5. The solution, where generator is costly enough to warrant protection, is to bias the star point above ground at a frequency not found in normal service (and not a sub-harmonic) - Using a power source of about 20 Hz is common - and use a frequency selective relay. If the generator stator actually has a short to ground in the bottom 5%, a 20 Hz current flows and is detected.
  6. Note it is usual to earth the generator star point through a high resistance, which limits the current to say 10 amps at 100% of turns, to minimise damage by an earth fault arc - this earthing is not a problem with a big generator [I mean 100s of MVA] which is connected through its own transformer to the Grid. Note that big generators may use "graded" insulation, which is thinner at the star end, but saves space for more copper or cooling - smaller generators with full voltage insulation on all the winding have little risk of a fault where the the working voltage is 5% or less (near star end).

67model

Register to Reply Good Answer (Score 2)
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (1); lyn (1); nobodysomebody47 (1)

Previous in Forum: Power Line Phase to Neutral Contact No Fuse Blown, No Tripping   Next in Forum: Automation Systems

Advertisement