Effect 380V, 50Hz Motor to be Fed from 400V, 50Hz Supply in DOL Mode

04/06/2013 8:52 AM

Hi?

Please review the following conditions.

380V, 50Hz motor to be fed from 400V, 50Hz supply in DOL mode.

I would like to know any expected bad impacts on motor in this condition.

Please advise it. Thanks.

Register to Reply
Pathfinder Tags: motor 380 400 impact
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: Effect 380V, 50Hz motor to be fed from 400V, 50Hz supply in DOL mode

04/06/2013 8:58 AM

sure, it's close enough

Register to Reply
2
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4
In reply to #1

Re: Effect 380V, 50Hz motor to be fed from 400V, 50Hz supply in DOL mode

04/06/2013 12:35 PM

to help you understand (in north America) you want your supply voltage to be within 10% of the motors rating (usually on a plate or tag on the motor itself) so you're within the 10% of your 400V with 380V hope that helps you today and in the future

Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Effect 380V, 50Hz motor to be fed from 400V, 50Hz supply in DOL mode

04/06/2013 9:59 AM

No problem.

Register to Reply Score 1 for Good Answer
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Effect 380V, 50Hz motor to be fed from 400V, 50Hz supply in DOL mode

04/06/2013 12:08 PM

The motor will live a happy, healthy and contented life, fulfilled in its dream to perform useful rotational work to the end of its days.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: Effect 380V, 50Hz Motor to be Fed from 400V, 50Hz Supply in DOL Mode

04/06/2013 12:57 PM

IEC 60034-1 [Fig.12] states-if frequency is 50-51 Hz- the maximum permitted supply voltage in very good conditions [Zone A] it is up to 400V. Due to voltage drop on the supply cable the voltage at motor terminal will be always less. Therefore, I agree with Jraef and lyn the motor will run in very good conditions.

__________________
Julius
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Effect 380V, 50Hz Motor to be Fed from 400V, 50Hz Supply in DOL Mode

04/06/2013 4:34 PM

Don't worry. Chicken curry.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Participant

Join Date: Oct 2008
Posts: 2
#7

Re: Effect 380V, 50Hz Motor to be Fed from 400V, 50Hz Supply in DOL Mode

04/07/2013 3:29 AM

There will be no significant effect on the operation of the motor. it is safe to operate the motor at 400V.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8

Re: Effect 380V, 50Hz Motor to be Fed from 400V, 50Hz Supply in DOL Mode

04/07/2013 4:05 AM

Dear Mr.JBK,

The current drawn will be less by 5% for the same Load/Power. Voltage wise, No issue as it is safe. Heating Effect on the winding will be less, and so the Winding Temp.Rise will be accordingly Less.

DHAYANANDHAN.S

Register to Reply Score 1 for Good Answer
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); dhayanandhan (1); Fredski (2); JRaef (1); lyn (1); PWSlack (1); Sambab (1)