Leakage Voltage Across the Medium Voltage SCR in "OFF" State

04/28/2013 5:06 AM

Hellow every one,

Pls, can some one explain & also provide a document /Link to understand the below mentioned question related to solid state switching device(SCR).

Thanks.

What could be the Leakage voltage across the medium voltage solid state switch (SCR) in "OFF" State?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Leakage voltage across the medium voltage SCR in "OFF" State.

04/28/2013 6:05 AM

Leakage current I can understand...
A leakage voltage is pretty meaningless unless current flows....
If current flows in the OFF state then surely it's a dead SCR.

Beware of voltage readings on high impedance meters they can be very missleading.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Associate

Join Date: Apr 2013
Posts: 26
#2
In reply to #1

Re: Leakage voltage across the medium voltage SCR in "OFF" State.

04/28/2013 6:49 AM

Pls, see the following detail to batter understanding the Case.

  • We have a "SCR" connected at 7.89kv.AC rated system (Line voltag).
  • Line voltage are available at ANODE Terminal.
  • No Gate firing yet ( SCR is in OFF state).
  • we have measured the voltage at the LOAD terminal ( between Phase to Ground) around 500v at all three SCR .
  • These voltage suppose not to be pass before the firing.

I hope that now its clear to understand the case/condition.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#3
In reply to #2

Re: Leakage voltage across the medium voltage SCR in "OFF" State.

04/28/2013 6:56 AM

What instrument did you use to measure this voltage? Was the load connected when you made the measurement?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Associate

Join Date: Apr 2013
Posts: 26
#4
In reply to #3

Re: Leakage voltage across the medium voltage SCR in "OFF" State.

04/28/2013 7:54 AM

FLUKE-287 & Load was Isolated/Disconnected.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#5
In reply to #4

Re: Leakage voltage across the medium voltage SCR in "OFF" State.

04/28/2013 8:06 AM

I suggest you repeat the measurement with a dummy load - a 12V lamp will do nicely.

Pity you didn't use a Fluke 289 with the LoZ setting, which reduces the meter input impedance from >10MΩ to about 3.2kΩ.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Associate

Join Date: Apr 2013
Posts: 26
#8
In reply to #5

Re: Leakage voltage across the medium voltage SCR in "OFF" State.

04/28/2013 9:04 AM

we have connected an Incandicent Lamp( 220vac , 300W) across the Phase to Ground which is "busted" within seconds.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #8

Re: Leakage voltage across the medium voltage SCR in "OFF" State.

04/28/2013 6:00 PM

<..."busted" within seconds....> That's not very surprising, if it comes from a higher voltage supply!

An SCR is simply an electronic version of a switch.

  • If the SCR is off, then the voltage across it could be whatever is on the supply terminals to the equipment. At that time, the voltage across the load will be very low.
  • When the SCR turns on, expect the full line voltage to be across the load. If the load is not rated for the full line voltage, then <..."busted" within seconds...> would be the anticipated outcome.

The concept of "leakage" applied to the label "voltage" is abstruse.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#7
In reply to #2

Re: Leakage voltage across the medium voltage SCR in "OFF" State.

04/28/2013 8:57 AM

Be sure you have a sensible low load resistance value when you take these leakage-current measurements. If you measured 500V with your intended operating load resistance, perhaps your selected SCR part is too large. What part are you using?

__________________
Thanks, Win
Register to Reply
Power-User

Join Date: Nov 2012
Posts: 142
Good Answers: 14
#13
In reply to #2

Re: Leakage voltage across the medium voltage SCR in "OFF" State.

04/28/2013 11:05 PM

Not sure how you have the SCR connected, but having the load in the anode circuit would be normal.

With the SCR off, if you read the voltage between phase and ground from either side of the load or from the anode, you should get full line voltage.

To check for leakage through the SCR when off, either measure current through the load or voltage directly across the load.

With the SCR off, there should be no voltage impressed across the load but full voltage across the SCR. If there is a small voltage, then that voltage divided by the resistance of the load will give you a fair indication of the leakage current.

With the SCR conducting, you should get almost line voltage across the load and almost zero across the SCR. There will be a small voltage drop across the SCR when conducting.

In the event that you have the load in the Cathode circuit, try disconnecting the gate to see if you are getting some form of feedback via the gate

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6

Re: Leakage voltage across the medium voltage SCR in "OFF" State.

04/28/2013 8:47 AM

I believe we have another case of ESO here.

A SCR is a self latching electronic switch that cannot be actively turned OFF. It can only be turned ON. When the current drops below a near zero critical value or an anode to cathode reverse voltage bias happens and then the SCR turns itself OFF. By replacing the load with only a the high impedance load of a digital volt meter (DVM), the SCR will turn OFF and only the leakage current through the SCR will propagate through. Lets not forget that in this OFF state, the circuit leakage current will be larger than just the SCR leakage current because all alternate paths (wire insulation, circuit board contaminants, etc.) will sum together. Now the high impedance load of the DVM becomes a detriment because this current produces a voltage across the DVM.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Associate

Join Date: Apr 2013
Posts: 26
#9
In reply to #6

Re: Leakage voltage across the medium voltage SCR in "OFF" State.

04/28/2013 9:14 AM

Definitely "SCR" was turned into "OFF" state, otherwise we should received 100% voltage( i.e 7.89kv) insted of 500v at Cathode/load point.

While, during this measurement load( Motor) cable are isolated.

Register to Reply
4
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#10
In reply to #9

Re: Leakage voltage across the medium voltage SCR in "OFF" State.

04/28/2013 10:54 AM

Since you will not do the math to understand your problem, allow me...

With 500V appearing on a 10^7 ohm load (DVM) the leakage current is only 5*10^-5 amperes of current. So your first task is to identify if this current is less than the guaranteed maximum for these unidentified SCR. I suspect that it will be. If you now parallel your DVM with lower impedance device that is capable of handling 500V (putting a 220V lamp there was just foolish) you can now measure how much of a voltage drop you have with this lower impedance. This will now allow you characterize and verify your source impedance in an OFF state. From the data you've provided, if everything is linear (a big assumption with semiconductors) I calculated that you have about a 150 million ohm source impedance. That's a little low for high quality high voltage cable insulation from a single source, but well within fiberglass circuit board traces.

I recommend that you review of SCR design theory.

If I just reminded you of a sound diagnostic approach when dealing with high voltage systems, then happy hunting. If you never heard of a source impedance then step away from this system. You are not qualified to work on this or to say that it is working safely.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 4)
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11
In reply to #10

Re: Leakage voltage across the medium voltage SCR in "OFF" State.

04/28/2013 12:58 PM

Quote: Redfred

  • "... step away from this system. You are not qualified to work on this or to say that it is working safely."

Aside from getting my GA vote, this last part qualifies as the Understatement Of The Year!

Evidence:

  1. Testing voltages on a 7.8kV system, meaning the door is open and the line side of the SCRs are live. (Hopefully you at least had a high voltage Arc Flash suit on?)
  2. Using a Fluke 289 on a 7.8kV system in any way shape of form.
  3. Not knowing that the POTENTIAL voltage on the SCR load side is the LINE voltage, reduced only by the resistance of the SCR in the Off state (which is NOT infinity) and the impedance of the meter you might be using (plus the other factors mentioned by Redfred).

The Fluke 289 is rated at 1000V maximum, and even then only at Cat 3 safety. Had you encountered a shorted SCR, the potential would have been your line voltage, the meter might have exploded and/or the leads vaporized, which could have triggered an Arc Flash with enough heat and explosive potential to kill you and everyone not in the blast shadow of your corpse for about 5 feet from the SCR stack. Even if the SCR is good, the resistance is dependent upon the clamping pressure, so it varies in each installation and you cannot predict an exact amount of voltage potential on the load side. Anything over 10kohm is typically considered good, so had the SCR resistance been only 11kohm, the voltage potential would again have exceeded the rating of the Fluke meter and been a potential bomb!

I hope you bought a lottery ticket that day, you are one lucky individual!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#14

Re: Leakage Voltage Across the Medium Voltage SCR in "OFF" State

04/29/2013 4:10 AM

Hmmm,
Post #1.
I covered all the points subsequently raised, (despite not being told it was high voltage) but I don't get a GA?
Del
<shambles off a broken kitty shaking head in dispair>

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #14

Re: Leakage Voltage Across the Medium Voltage SCR in "OFF" State

04/29/2013 5:31 AM

Cheer up. There's a tin of tuna in the post.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Apr 2013
Posts: 26
#16
In reply to #14

Re: Leakage Voltage Across the Medium Voltage SCR in "OFF" State

04/29/2013 7:18 AM

Del the cat.

Unfortunately our friends understand wrong, Basically the question I raise is that,

What is the limit of leakage Voltage at Cathode/Load ( as per design/manufacturer limits) for a Medium Voltage( 13.8KV/7.89KV SYSTEM VOLTAGE) "SCR" while the "LINE" side is healthy but, SCR is still in OFF State ?

We noticed that the metering device (digital voltmeter connected at LOAD side secondary side of an open Delta P.T) was measuring around 500vac at the primary of PT even the SCR was in OFF state that suppose to be Zero volt. After that ,we start invastigation of this LEAKAGE VOLTAGE & posted this to CR4 friends.

Thanks

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #16

Re: Leakage Voltage Across the Medium Voltage SCR in "OFF" State

04/29/2013 8:19 AM

#10↑ and #11↑ explain all, which is why the replies have attracted so many GAs. The voltage on the terminals is simply a function of the resistance of the device in the off state and the resistance of the connected load, which seems to be a digital voltmeter with high input impedance. The voltage could still be anything from zero to full line voltage, which explains why the low-voltage filament lamp <...busted...> so readily.

The term <...leakage voltage...> is still abstruse.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#18
In reply to #16

Re: Leakage Voltage Across the Medium Voltage SCR in "OFF" State

04/29/2013 10:00 AM

Since you do not seem to be grasping the concept here, I'll try it this way:

Q: "What is the limit...? "

A: 100% line voltage, because under the worst case scenario, the SCR may not block voltage at all.

You are asking if there is a design spec on an allowable limit to the voltage leakage through the SCR, we are continually trying to tell you that the basic premise of your question is flawed. There is no such thing.

There will ALWAYS be a voltage potential on the load side of the SCR and what you read is TOTALLY subjective and dependent on what is connected to it, including the meter and any wires etc. Also in your case, you apparently have a PT connected to the load side, that alone provides additional paths for your leakage current to flow. So if you are attempting to use a volt meter on the load side of an SCR controller in order to determine if the SCRs are on or off, the concept is flawed if you are looking for the voltage to be some pre-defined number. The best you can do is to determine, empirically, that the value has not significantly CHANGED from some known value indicating the desired state.

And by the way, if you put your meter on the PRIMARY side of the PT, you may as well have put it on the SCR itself. You still performed a VERY dangerous procedure with a hand held device that was not rated for the task.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#19

Re: Leakage Voltage Across the Medium Voltage SCR in "OFF" State

04/29/2013 3:51 PM

Why do I hear a... "Psssst... Boom" happening soon?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#20
In reply to #19

Re: Leakage Voltage Across the Medium Voltage SCR in "OFF" State

04/29/2013 3:57 PM

Because this OP measured 500V. Then connected a 220V device to the 500V terminals and was surprised that it it died.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#21
In reply to #20

Re: Leakage Voltage Across the Medium Voltage SCR in "OFF" State

04/29/2013 4:09 PM

LOL...

That was a rhetorical question.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#22

Re: Leakage Voltage Across the Medium Voltage SCR in "OFF" State

04/29/2013 10:50 PM

When you block a voltage with a semiconductor, you have a leakage current. If you push it, it may define a leakage current path. But, there is no leakage voltage as far as I can see.

Explain your assertion.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#23

Re: Leakage Voltage Across the Medium Voltage SCR in "OFF" State

04/30/2013 9:47 AM

How about this:

Leakage voltage doesn't exist until you try to measure it.

Kind of like Schrodinger's cat.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: