Help with Electrical Diagram

05/02/2013 4:21 AM

Could anyone help me with a diagram, both mains and control, for a closed transition star/delta starter?.

Regards,

Colin Taylor

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#1

Re: Electrical Design Engineer, UK company

05/02/2013 5:02 AM

Does this help?

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Reply Good Answer (Score 3)
Participant

Join Date: Apr 2013
Posts: 3
#2
In reply to #1

Re: Electrical Design Engineer, UK company

05/02/2013 5:27 AM

Randall,

Yes, that does help me.

Thank you for your assistance.

Regards,

Colin Taylor

Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#5
In reply to #1

Re: Electrical Design Engineer, UK company

05/10/2013 3:11 AM

Avery good link.Real good search result.GA

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Help with Electrical Diagram

05/02/2013 10:27 AM

Just out of curiosity, why on earth would you want to go to that trouble, as opposed to spending less and attaining more control by using a solid state soft starter?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Participant

Join Date: Apr 2013
Posts: 3
#4
In reply to #3

Re: Help with Electrical Diagram

05/03/2013 3:53 AM

JRaef,

We have an existing installation which starts a motor using an open transition

star/delta starter. On changeover from star to delta we are getting a high current

peak of about 6 times full load current. It is being proposed to change the starter to

closed transition type to reduce the current peak on changeover.

Soft starter is not suitable for this application.

Regards,

C Taylor

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #4

Re: Help with Electrical Diagram

05/10/2013 6:06 PM
  • "Soft starter is not suitable for this application."

What makes you say that? There is NOTHING that the Closed Transition Star-Delta starter is going to give you that you will not get from a soft starter, but there is PLENTY that you will get from the soft starter that you cannot attain with the CTSD.

Number one benefit, not closed transition, how about NO transition!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Participant

Join Date: Apr 2013
Posts: 3
#7
In reply to #6

Re: Help with Electrical Diagram

05/11/2013 10:47 AM

There is a physical limitation on this installation, i.e. it is not possible

to fit a soft starter of the size required for this pump motor in the

area available.

Regards,

C Taylor

Reply
Reply to Forum Thread 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

cb-taylor59 (3); JRaef (2); Randall (1); V.I.Abraham (1)

Previous in Forum: NPN to PNP   Next in Forum: Field Test Procedure (through the Primary Injection) for Medium Voltage Circuit B

Advertisement