2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 3:26 PM

Hi Guys,

I got (bought, stole, got it for free) two split system A/C units (make sanyo).

So 2 compressor units and 2 house wireless controlled units with the evaporator and blower unit in it.

I do not need A/C at the same time in the 2 rooms I refer to: one I sleep, dream and.. do not work in during day time.. and the other one is my living room that I use during the day to .... be in.

Both units are exactly the same.

I want to connect both on the same compressor unit and switch between the 2 house units with the remote control. I would love to not have to use extra valves.

Can I just parallel them en adjust the amount of freon, or isn't it that simple?

Installing 2 compressors is difficult and tiresome. Other lazy guys here? Tks

__________________
Plenty of room here
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: 2 split house (evaporating) units on 1 compressor of the size of 1 match.

05/11/2013 3:31 PM

I don't know any other way then solenoid valves to isolate unused evap coil.....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#2
In reply to #1

Re: 2 split house (evaporating) units on 1 compressor of the size of 1 match.

05/11/2013 3:50 PM

Was just thinking:

The active one gets rid of the cool and will work, because you sent air through it with the fan.

The other one will get to cool freon too, but has no way to get rid of it and not cool the room.

Eventually, maybe it could freeze and clog, however? Is that a problem?

Once we start that one up again, it will work after a while? Valves of course is one, but it complicates the switching sequence and adds more wires.

And does it need valves in both the pressure and suction line?

__________________
Plenty of room here
Register to Reply
4
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #2

Re: 2 split house (evaporating) units on 1 compressor of the size of 1 match.

05/11/2013 7:55 PM

The evaporator coil area is calculated precisely in a refrigeration system to work with the other components, changing any of these will throw the system into an imbalanced condition....adding solenoid valves to isolate the coils is no big deal....You only need them on the liquid lines...The control for the solenoids can be tied in to the fan unit control voltage, make the valves NC and when the fan unit is energized, the valve on the proper unit opens....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 4)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#9
In reply to #5

Re: 2 split house (evaporating) units on 1 compressor of the size of 1 match.

05/11/2013 8:37 PM

Automatically with 2 same units they are calculated for the same job and don't care which compressor feeds them.

The lines are also about the same length. Problem is that the fan is speed controlled, however I can get the power on the flap switch. (opens when switched on).

I have also the impression that perhaps the evaporator has a high pressure valve

(firing valve) instead of a capillary tube. Maybe this can hold up the liquid too, while it is sent to the other one? (how else do they get different settings - the compressor runs always at the same speed with my units)

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#3

Re: 2 split house (evaporating) units on 1 compressor of the size of 1 match.

05/11/2013 5:09 PM

no

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#4
In reply to #3

Re: 2 split house (evaporating) units on 1 compressor of the size of 1 match.

05/11/2013 7:41 PM

Hi Fredski,

Your answer is short today. Can you elaborate:

1. No to what question?

2. What can possibly or surely will happen?

They do it in multi split systems probably.

Thanks

__________________
Plenty of room here
Register to Reply
2
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 7:59 PM

ok a little AC101... the compressor is cooled by the returning refrigerant gas (you're referring to Duponts trade name, Freon. so you cant have 2 separate evaporators. you can have multiple evaporators but they need to share common refrigerant lines.....no mixing of refrigerants or refrigerant oils.also, for multiple evaporators you need a speed controlled compressor to handle staging of the loads. You can Mickey Mouse it but I think you'll just have a very poorly operating system and it will experience compressor failure if you get the superheat wrong. I just strongly suggest you get a system that was designed for your type of application. and if you don't keep enough air passing over the evaporators you'll experience icing and liquid flooding back to your compressor and it will grenade. other than that sounds like a great idea to me.

Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#7
In reply to #6

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 8:26 PM

Fredski, Thank you

What about just a switching valve only in the pressure line, so that only one gets the high pressure and just a T in the return?

The valve could be activated with the house unit. (kind of bi- stable flip flop)

If I fill enough refrigerant after vacuuming the lines, he environment should work, because the not working in house unit also send nothing throught the evapoartor anymore.

Unless? I am not a specialist in this matter. Just don't want to put my walls full of

not used condenser units. The central A/C time will be past soon because too expensive to cool the whole house. Remember before people were heating also only the rooms they occupied?

Central heating came because diesel was dirt cheap, less than $0.20 per gallon. Now $4.00 per gallon. It all depends on what you want to spend your money.

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#8
In reply to #7

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 8:35 PM

I have over 30 years experience in commercial AC, I'm a licensed contractor......just trust me on this one.

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#10
In reply to #8

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 8:41 PM

Thanks Fredsky. I cannot recall you ever gave me bad advise.

__________________
Plenty of room here
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#11

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 8:44 PM

My understanding is that some/many/most of the new, high-efficiency units have a solenoid built into the expansion valve which prevents the system from equalizing when it shuts down. If your units have this, you should be set in that department. My concern would be with lubrication - you want to make sure the lube oil doesn't have any place to fall out and not be returned to the compressor.

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#13
In reply to #11

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:19 PM

All piping is downstream towards the compressor unit. The extension is supposed to go up to the second floor.

__________________
Plenty of room here
Register to Reply
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#12

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:08 PM

This is a little diagram for you.....the system is piped with the suction lines tied together and the liquid lines tied together from the condensing unit you are going to use,,and the evaporator coils are isolated with the solenoid valves....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#14
In reply to #12

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:21 PM

traps?????

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#17
In reply to #14

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:28 PM

???

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#16
In reply to #12

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:25 PM

Hi SolarEagle,

I love it, but I need new glasses to read the comments. Or I can try looking through the bottom glass of a glass jam jar. I can imagine that you didn't want the others to read it. I start giving good points as long as I haven't vacuumed it and gasses it up.

If one of the ideas doesn't work, I start distributing (d)evil faces. Thanks, DGAG

__________________
Plenty of room here
Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#22
In reply to #16

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:40 PM

Yeah it's hard to tell sometimes...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Off Topic (Score 4)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#21
In reply to #12

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:38 PM

the refrigerant needs to maintain a specific velocity to hold the oil in suspension or the oil falls out and collects in low points. if the oil isn't all returned to the compressor it will fry. this thing is just such a bad idea!

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#23
In reply to #21

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:48 PM

Where do you see a drop in velocity ? ....all you're doing is switching coils with the solenoid valves....I assume the coils are the same size and only one at a time is being used....should be no problem

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#25
In reply to #23

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:54 PM

he said they'd be on 2 different floors of the house, sorry but trying to hammer the square peg into a round hole always makes a mess and this "after engineering" of marrying 2 systems together that were never intended to work this way is just a poor idea. hammer away I'm done with this thread for now

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Posts: 989
Good Answers: 14
#15

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:24 PM

just get a thermostically controlled duct diverter which is build like a Y and can divert cold air to either of two main supply lines and use your one compressor and air handler unit.

http://www.hvaccomfort.com/sys2/sys2.htm

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#18
In reply to #15

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:33 PM

Whoa, major ductwork, no no....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jun 2010
Posts: 989
Good Answers: 14
#35
In reply to #18

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/13/2013 10:12 PM

not really if the two existing air handlers are the same size, then you only have to run a supply line from the diverter to the main trunk line of the system you removed the air handler from.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#19
In reply to #15

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:33 PM

good thinking..but, the idea of air conditioning is less about delivering cool air, its more about moving heat from an area you don't want that heat in to a place that's less objectionable. he needs to remove heat not add colder air to a hot room. the whole idea is filled with problems, oil return, leakage of shut-off valves,superheat/charging, airflow and fan speedcontrol, etc, BAD IDEA get a system designed for the application

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#26
In reply to #19

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 10:24 PM

I did some research on the Sanyo website now. They sell those systems with a choice of compressors.

The in house units are the same as I have. Only the compressor units are different:

Have multiple outlets and perhaps a special manifold.

They have a inverter built in. Perhaps to adapt the speed and pressure the way you describe.(what makes good sense) I will call them on Monday and promise to come back with the results ASAP. Thank you all for the help. D.

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#29
In reply to #19

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/13/2013 3:50 PM

I had my hearing checked the other day - said I am not hard of hearing, I am hard of listening. A lot of people seem to have that problem, too. I don't do much A/C, mostly small to medium refrig and freez. Look like a good money saving idea that is going to cost way more than it will save. I'm with you on this one. Just put the 2 systems in as designed and turn off the one you are not using. Anything else is just going to lead from one problem to another, to another ... -- JHF P.S. GA on your earlier comment!

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#20
In reply to #15

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:33 PM

Hi,

This is what I do not have: Air handler. And this is what I don't want to have: ducts.

The floor is 8" concrete, no plenums.

My house is full of ducts in which a army can hide. Have thought of filling big plastic bags with cold air downstairs and bringing them to the bedroom. But when can I sleep then? I'll check the link. Thanks.D.

__________________
Plenty of room here
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#24
In reply to #15

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 9:52 PM

This is what I have now. Only monster ducts, slow speed air, with controlled damper and shut-offs.

Good when the apartments are rented out, but... not for me alone.

I like to switch between the 2 systems. Central air of poor man's air.

__________________
Plenty of room here
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#27

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/11/2013 10:37 PM

The idle evaporator (air unit) will have small amounts of refrigerant and oil hung up in it, even if equipped with a liquid solenoid valve for pump-down type operation. If the evaporators are above the compressor/condenser, this is not likely to be a big problem. You might need slightly greater charges of refrigerant and oil.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#28

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/12/2013 11:41 PM

Dvmdsc,

I believe such units have been around for about 15+ years--one compressor and 2-4 independent evaporator units (without ducts but with drip pans and condensate drains. My mind says Panasonic, but I don't remember the brand. Memory says the cost was fairly steep. Therefore, your concept should work. Of course, the attention to detail is a must and Fredski has some very valid points regarding trapping oil, etc.

--JMM

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2010
Location: OZ, otherwise known as Oklahoma were the wind comes sweeping down the plains.
Posts: 159
Good Answers: 4
#30

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/13/2013 5:58 PM

Installing two condenser units can't be that much more difficult than trying valve two evaporators to one condenser unit without having to deal with Freon leaks and the control hassle. Just turn the one you are not using off.

Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#31

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/13/2013 7:37 PM

FYeyes,

This is the only split I have in mind.

I needed a lot of persuasive power to convince my wife that this was a good place to install the condenser unit. For the next one, who will service the room(s) above, I have only the balcony floor that has no hiding space.

Sanyo hasn't responded yet.

Here the situation pics:

In the walls the concrete is recessed by 2 to 4 inches, thus

very difficult to attach heavy things.

The floor are 8" 3000 psi concrete with negative and positive

3/4" rebar. (concrete structure goes up higher)

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#32
In reply to #31

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/13/2013 7:54 PM

pictures!! great I feel for anyone in the future that needs to work on that hanging condenser! so why cant the outdoor unit be located on the roof, ground, or side of the bldg? what length run of lines are we talking about?

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#33
In reply to #32

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/13/2013 9:34 PM

Hi Fredsky,

Here is some wider view:

before the unit was installed. The condenser group is bolted on a welded frame that is anchored into the wall on 2 points and has a adjustable threaded rod to the ceiling.

I have put it there, because it is out of the way and pretty silent, has no rain and only a little bit of sun in the evening. The roof is very steep ( 45 degrees)

__________________
Plenty of room here
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#34
In reply to #32

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/13/2013 9:48 PM

Length of the run will be about 16 Feet. That is what's in the box. The systems comes pre-filled, but first I vacuum the lines for a while. # 1 has been installed for about one year now. 12,000 Btu - runs only 12% of the day. Avg. 1.7 kWh/day. Takes care of about 1/3 of the ground floor.

__________________
Plenty of room here
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#36
In reply to #31

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/13/2013 10:23 PM

Dvmdsc

Looks to me like a very well-done very efficient home. I read into your words that the walls are ICF construction, with the upper story cantilevered out on a structural slab. I applaud your work.

--JMM

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#37
In reply to #36

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

05/17/2013 9:52 PM

Thank you,

This are actually 3 - 3 bedroom 2 1/2 bath town houses under 1 roof. I like it a lot: spacious, very economical to live in (and with low maintenance). We extended our comfort on the patio lately with a big beer drinking table.

__________________
Plenty of room here
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#38

Re: 2 Split House (Evaporating) Units on 1 Compressor of the Size of 1 Match

07/07/2013 8:34 PM

For the Bahamas, being known as a touristic destination and no hotbed for .......

This is the solution, chosen and implemented. Thanks to Fredski

Thank you all for your input.

__________________
Plenty of room here
Register to Reply
Register to Reply 38 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

129CBRider (2); bigg (1); Circuit Breaker (1); dvmdsc (15); Fredski (8); Grand Poobah (1); jmueller (2); SolarEagle (7); Tornado (1)

Previous in Forum: What Can We Make Out of CO2   Next in Forum: Increase Large Ship Speeds by Over 30%

Advertisement