Measuring the Level of a Closed Vessel in a Process Under Vacuum

05/16/2013 4:16 AM

Dear All

I kindly request that you assist me in the challenges I have when it comes to measuring the level of steam condensate in a vessel that is under vacuum. The vessel is under vacuum pressure of 92 kpa and the tank has a height of 2m and using a differential pressure transmitter with a wet leg connected on the LP side and the HP side which is a flange mount type is connected to the base of the tank.

Thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: measuring the level of a closed vessel in a process under vacuum

05/16/2013 4:24 AM

Perhaps the condensate is boiling in the vessel, or even the pressure transmitter legs, in which case consider a different measuring technique, such as radar.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: measuring the level of a closed vessel in a process under vacuum

05/16/2013 4:48 AM

Consider replacing the vessel and any electrical condensate pump with a steam-operated Ogden Pump Set (usual disclaimer) that does not need separate level instrumentation in order to operate automatically.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#3

Re: measuring the level of a closed vessel in a process under vacuum

05/16/2013 8:11 AM

We have several vessels similar to yours (containing steam condensate under a vacuum). For all of them we use differential pressure transmitters with two diaphragms. We don't have any problems with them as long as you calibrate them regularly.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
3
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#4

Re: Measuring the Level of a Closed Vessel in a Process Under Vacuum

05/16/2013 8:52 AM

If you have a bottom mounted transmitter and are, indeed, able to maintain a full wet-leg to the top of the drum, it will have a higher level, i.e. higher head/pressure than the bottom connection. Therefore, the wet leg should be connected to the HP side of your transmitter. Also, the reading will be reversed, i.e. more differential will be seen when the level is low. The differential will be zero when the level in the drum equals the height of the wet leg.

Register to Reply Good Answer (Score 3)
Participant

Join Date: May 2013
Posts: 2
#7
In reply to #4

Re: Measuring the Level of a Closed Vessel in a Process Under Vacuum

05/17/2013 3:43 AM

Thanks biggs, the transmitter uses a negative range because the wet leg is always filled with water. The range of the transmitter is: lower range value = -29.0 Kpa and an upper range value of -10.0 kpa.

Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#5

Re: Measuring the Level of a Closed Vessel in a Process Under Vacuum

05/16/2013 5:30 PM

Agree with Bigg, It is logical to have your HP to your wet leg, cause that is going to be your High pressure, but it will still work exactly the same if you have the connections in reverse.More important is that you set your zero and span accordingly.On your current set up you are going to have negative values which may cause some confusion to the maintenance crew.

Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#6

Re: Measuring the Level of a Closed Vessel in a Process Under Vacuum

05/16/2013 9:20 PM

Condensate temperatures can exceed what the meter body can tolerate, so it not unusual to find drop leg impulse tubing (H2) on the high side port (low level tap) that isolates the transmitter from the condensate's temperature (which is what the wet leg also does on the other side), as shown in the Foxboro graphic below:

Here's Rosemount's example for configuration of DP level with a wet leg:

Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#8
In reply to #6

Re: Measuring the Level of a Closed Vessel in a Process Under Vacuum

05/17/2013 8:19 AM

I knew you'd check in with the best GA

Register to Reply
Anonymous Poster #1
#9

Re: Measuring the Level of a Closed Vessel in a Process Under Vacuum

05/17/2013 3:28 PM

So , just to be clear ---

this is what we have ( ? )

Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); bigg (2); eltech (1); Iris (1); PWSlack (2); Stacytk21 (1); Vulcan (1)

Previous in Forum: Hardwired Cable and Data Link Cable   Next in Forum: Solar Cell Output Becoming Weak

Advertisement