Gas Nozzle Size, Pressure, Flow Equation

05/19/2013 11:05 AM

Hello. I have little confusion about gas flow rate and pressure relation according to gas nozzle hole size. gas feed is a natural gas.

example - 1 if nozzle hole size is 3 mm dia

nozzle working pressure 100 m bar

so what would be the flow in meter cube/hour ?

if i want to dobble the the gas flow rate

option - 1 can increase pressure to 200 mbar or ?

option - 2 can i increase nozzle hole size area to dobble?

we are looking for the equation to give us a relation between flow , pressure , & hloe size for nozzle.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Gas nozzle size, Pressure, Flow equation.

05/19/2013 11:17 AM
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Gas nozzle size, Pressure, Flow equation.

05/19/2013 3:05 PM

Q ≈ k (ΔP)0.5 d2.5 [Darcy-Weisbach]

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Commentator

Join Date: Jan 2006
Location: Western flank of the Pennines in Lancashire England
Posts: 93
Good Answers: 8
#8
In reply to #2

Re: Gas nozzle size, Pressure, Flow equation.

05/20/2013 3:57 PM

Darcy-Weisbach applied to the flow of a fluid down a pipe not through a jet

Register to Reply
Commentator

Join Date: Jan 2006
Location: Western flank of the Pennines in Lancashire England
Posts: 93
Good Answers: 8
#3

Re: Gas Nozzle Size, Pressure, Flow Equation

05/20/2013 2:43 AM

Try this. The units are imperial but the conversions are easy.

Q=1658.5 x Cd x A x sqrt(p(in wg)/(SGx sqrt(jet pressure(absolute)/Atmospheric Pressure(absolute)) x sqrt(jet pressure(absolute)/Atmospheric Pressure(absolute)).

Cd is the coefficient of discharge of the gas jet and an reasonable estimate can be made based on standard literature.

If you want to double the flow through the same jet then you need 4 x the gas pressure.

The flow through your jet assuming Cd=0.9 would be 3.75m3/h

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: Gas Nozzle Size, Pressure, Flow Equation

05/20/2013 2:53 AM

...or 20.4 x the original nozzle diameter.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Jan 2006
Location: Western flank of the Pennines in Lancashire England
Posts: 93
Good Answers: 8
#5
In reply to #4

Re: Gas Nozzle Size, Pressure, Flow Equation

05/20/2013 4:01 AM

Assuming the the burner associated with this jet is an atmospheric injected burner (Bunsen burner) then altering the jet size will adversely affect the flame picture leading to poor combustion. Not a good move.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 1460
Good Answers: 30
#6
In reply to #3

Re: Gas Nozzle Size, Pressure, Flow Equation

05/20/2013 11:00 AM

Is this not overcomplicated? The OP mentions driving pressures of a few mbar and a 3mm nozzle. I cannot believe this approaches critical pressure conditions, and suggest that we are still in the range where the pneumatic equivalent of Ohm's law applies. Doubling the pressure will double the flow, though doubling the nozzle area cannot be guaranteed to halve the flow resistance.

Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Mar 2010
Location: Detroit, MI
Posts: 11
#7

Re: Gas Nozzle Size, Pressure, Flow Equation

05/20/2013 11:28 AM
__________________
The only way to know is to apply what you learn!
Register to Reply
Commentator

Join Date: Jan 2006
Location: Western flank of the Pennines in Lancashire England
Posts: 93
Good Answers: 8
#9
In reply to #7

Re: Gas Nozzle Size, Pressure, Flow Equation

05/20/2013 4:03 PM

The OP is talking Gas Engineering not rocket science. The maths describing a CD nozzle does not apply to a jet with only a few mb pressure drop across it. The formula outlined in my earlier post describes the flow through a jet of the type reered to by the OP.

Register to Reply
Active Contributor

Join Date: Mar 2010
Location: Detroit, MI
Posts: 11
#10

Re: Gas Nozzle Size, Pressure, Flow Equation

05/20/2013 7:13 PM

You should investigate mass flow through truncated nozzles. The ratio of specific heats k=(Cp/Cv) = 1.31 for Natural Gas (Methane). There is a presentation that references this type of nozzle flow. You'll understand better by reading the paper to solve your problem. It's a small pdf file: http://www.e-ope.ee/_download/euni_repository/file/3286/EMH5020_OSA2_loeng2e.pdf

Hope this helps

__________________
The only way to know is to apply what you learn!
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Gasman (4); lyn (1); phph001 (1); rls1230 (2); Tornado (2)