Grounding Questions

05/30/2013 7:33 AM

1. Shall we interconnect the ground grid for power system (for system and equipment grounding) and lightning protection system or keep them independent of each other ?

2. For Electronic equipment grounding shall we provide independent ground grid or use the plant ground grid ?

3. For transformer neutral grounding shall we provide two independent and separate ground connection to two separate ground electrodes and in turn connect the ground electrodes to plant grid ?

I checked IEEE 80 but could not get the reply. Is there anybody who can help ?

Register to Reply
Pathfinder Tags: grounding
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Grounding questions

05/30/2013 7:43 AM

A1. Best kept independent. One wouldn't want lightning surges appearing inside the plant power grid, would one (rhetorical question - NNTR)? Of course, what the undefined "we" does is a separate thing.

A2. Best practice is to terminate all instrument shields onto an isolated "clean earth bar" and run cables separately from this to the main plant earthing point. The reason is to keep fault current surges in the plant power earth conductors away from the instrument shields as far as is reasonably practicable so that, once the circuit protective device(s) have disconnected the fault, the maximum amount of plant stands the best chance of continuing to operate. Of course, what the undefined "we" does is a separate thing.

A3. Good idea. It enables the neutral-to-ground link device in one of them to be opened temporarily and the connection tested for continuity before closing it again. Of course, what the undefined "we" does is a separate thing.

British Standard 7671, along with many other national electrical standards, is always available to help.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#2

Re: Grounding Questions

05/30/2013 8:52 AM

Your local standards code dictate what you must do.

Beyond that, I am with #1 all the way. Terminally, one point grounding.

Think about it this way: you have a lightning system with its separate ground. Then a lightning hits. Its separate ground lifts a million volts, temporarily. As it dissipates, other grounds of yours get lifted by some amounts.

You tell me, what happens to your electronics get lifted by a fraction of a million volts, while other parts do not? I hope you do not expect a happy outcome?!?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Grounding Questions

05/30/2013 10:41 AM

Hire a qualified electrician.

Register to Reply
3
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#4

Re: Grounding Questions

05/30/2013 11:34 AM

Question 1--I don't want to argue...I just want to present facts:

IEEE Std 142-1991 para 3.3.3.2 says, essentially, bond. Reference the Lightning Protection Code ANSI/NFPA 78-1989.

A similar requirement (to that found in the 2011 NEC) is in Section 4.14 of NFPA 780-2011, Standard for the Installation of Lightning Protection Systems. Additional bonding between the lightning protection system and the electrical system may be necessary based on proximity and whether separation between the systems is through air or building materials.

(2011) NEC 250.106 states:

The lightning protection system ground terminals shall be bonded to the building or structure grounding electrode system.

Informational Note No. 1: See 250.60 for use of strike termination devices. For further information, see NFPA 780-2011, Standard for the Installation of Lightning Protection Systems, which contains detailed information on grounding, bonding, and sideflash distance from lightning protection systems.

Informational Note No. 2: Metal raceways, enclosures, frames, and other non-current-carrying metal parts of electrical equipment installed on a building equipped with a lightning protection system may require bonding or spacing from the lightning protection conductors in accordance with NFPA 780-2011, Standard for the Installation of Lightning Protection Systems.

I do find it amusing that different countries have their own unique types of lightning (apparently), therefore requiring wholly different methods in this arena.

Question 2 and Question 3--If this equipment is located within the same facility it must all have a common bond.

Register to Reply Good Answer (Score 3)
3
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#5
In reply to #4

Re: Grounding Questions

05/30/2013 11:50 AM

re: above

Register to Reply Good Answer (Score 3)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6
In reply to #5

Re: Grounding Questions

05/31/2013 12:10 AM

Lightning protection system should have at least 2 down conductors and earth points.

__________________
pnaban
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#7
In reply to #4

Re: Grounding Questions

05/31/2013 1:43 AM

Actually, lightning does differ from country to country due to altitude, air pressures, humidity etc. It is also dependant on soil types and soil structures, i.e iorn ore deposits, other metals that may be found in the ground. And of course structures on the ground surface that may attract lightinng by giving off streamers.

But in reply to the question, all earths need to be bonded together, increased spacing and surge arrestors, may be required on/for critical circuits.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8
In reply to #7

Re: Grounding Questions

05/31/2013 2:00 AM

Does a body of water nearby will attract lighting?.

__________________
pnaban
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#9
In reply to #8

Re: Grounding Questions

05/31/2013 3:09 AM

Lightning always finds the least path of resistance to ground. Lightning does not strike the ground, a steamer rises from any upright object, i.e person, giraffe, tree, building, pole, mast etc. If the resistance to a streamer is low, that item will be struck, but streamers may emanate from any of the items. If the object is a tree around the water edge, then it could be struck and the water will disipate the charge. If a sail boat is out on the water, the mast acts as as a lightning rod, a streamer will emanate from the mast top and it will be struck, but a low lying puddle, pond, lake etc would in all probability be too low and many streamers would appear across the water surface. It is what is around the body of water that would be struck. Lightning strikes occur at sea frequently. The most common misnomer about lightning.......you can assume, but never predict where it will strike.

You can attract it to strike a certain place or point, but it is not always the rule. It follows the least path of resistance and that means air flow changes the path.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#15
In reply to #9

Re: Grounding Questions

05/31/2013 11:49 AM

Lightning does strike the ground in some cases. The main stroke of lightning will touch the path of least resistance in full force at some point...it doesn't just stop short of the intended path when a leader rises to meet it.

The leaders set the path of least resistance which the stroke(s) will follow.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #8

Re: Grounding Questions

05/31/2013 3:29 AM

It is more likely to be attracted to a nearby tree.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#11

Re: Grounding Questions

05/31/2013 5:15 AM

Dear Mr.bib,

The answer for your quiery

1. No. It should be independent.

2. No. Plant grid should not be linked.

3. No. Two seperate earth is better option.

DHAYANADHAN.S

Register to Reply Score 1 for Off Topic
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#12
In reply to #11

Re: Grounding Questions

05/31/2013 5:33 AM

Can you offer back up on the statements pleas? I am intrigued by this but I assume you have a valid point. I am not to sure what it is or why, but I am interested in this point. I look forward to your explanation. Thanks.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#14
In reply to #11

Re: Grounding Questions

05/31/2013 11:45 AM

Re: Question 1--The plethora of documentation held at various national levels stating that lightning and protective grounding systems shall be bonded provides more than enough evidence to state that the OP should do so. The IS which I have access to, however, reserves section 8 and does not address specifically the issue. Using an out such as not being regulated by one agency, and saying one could do otherwise just because one agency didn't say no is not a good reason to proceed with that plan. It is not prudent.

However, even regarding the IS for questions 2 & 3:

Whether using TN, TT, or IT systems...the intent is to keep the impedance between exposed parts as low as reasonably achievable. If not it is necessary to provide local equipotential bonding for an entire installation or a part thereof, an item of apparatus or a location. IS:3043-1987 18.0.10

Within a particular part of a zone where extraneous conductive partsare simultaneously accessible with either other extraneous conductive parts or exposed conductive parts or both...it is necessary to carry out local equipotential bonding between the parts concerned in order to obtain satisfactory low impedance. IS: 3043-1987 18.3.4

The somewhat weakly-worded and short-sighted (frankly, short) IS may not address the situation specifically, but the derived meaning is still there. If exposed parts are acessible at any one point they must share a common bond. Personnel safety prevails over operations.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#16
In reply to #14

Re: Grounding Questions

05/31/2013 12:16 PM

Dear Mr. Pete, Even though Section 8 of IS 3043 does not address much on Lightning Protection, there is a specific IS (IS 2309 - Code of Practice for the protection of buildings & structures against lightning), which specifically states that the lightning protection grounding system MUST be bonded to all other plant services earthing. This also substantiates what you have mentioned too.

Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#18
In reply to #16

Re: Grounding Questions

06/01/2013 1:56 PM

Yes, I found those rules with a bit more searching. They are now in my library and next on my reading list.

__________________
common knowledge...less common than common sense
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#13

Re: Grounding Questions

05/31/2013 11:31 AM

1. I am from India and my country Standard on Lightning Protection says that the Lightning Protection Grounding System and the all the plant services grounding system MUST be interconnected (vide IS 2309)

2. Vide IEEE 1100, the electronic equipment grounding MUST be bonded to the system grounding.

3. Vide the Indian Electricity Rules, 1956, there shall be two separate and distinct connections with two independent earth electrodes for neutral.

The above are what is practiced in India. You may refer to your relevant country codes.

Register to Reply
Member

Join Date: May 2013
Posts: 7
#19
In reply to #13

Re: Grounding Questions

06/03/2013 8:24 AM

1. Are you referring to clause no. 12.3.3 of IS:2309 ? You are right. Though, it does not specifically mention grounding grid. And IS:3043 does not specifically mention any such bonding.

2. I think you are referring to Cl. 8.5 of IEEE:1100. Again there is no specific mention of the same in any IS. And the instrument vendors insist for independent ground grid.

3. Your clarification is OK. However, I asked if the two independent earth electrodes are to be bonded to the plant earth grid or not. From all the standards I understand that the same is to be bonded to the plant earth grid. However, again there is no specific mention of the same in any IS or IE Rules. And electrical inspectors define it differently.

Also I wanted to know is there any technical advantage if I connect the neutral first to the independent earth electrode and then connect the earth electrode to the plant grid.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#17

Re: Grounding Questions

06/01/2013 10:39 AM

Sorry if I am late.

BS6651/1999 Code of practice for protection of structures against lightning

"17.3 Common network for all services

A common earth termination network is recommended for the lightning protection system and all other services. It should be in accordance with the recommendations of this code of practice and should also comply with any regulations applicable to the services concerned. The resistance to earth should, in this case, be the lowest value needed for any of the individual services."[BS6651 recommends 10 ohm for lightning protection grounding].

NFPA-780/2004

"4.14 Common Grounding.

4.14.1 General. All grounding media in or on a structure shall be interconnected to provide a common ground potential.

4.14.1.1 This interconnection shall include lightning protection, electric service, telephone, and antenna system grounds, as well as underground metallic piping systems."

In my opinion, the lightning strike current flows perpendicularly to the Earth surface towards the Earth depth. A conductor laying parallel with the surface will present a large reactance and in a few feet almost no current will flow towards the outside. In order to equalizing the outside potential with inside potential both grounding systems have to be bonded together.

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#20
In reply to #17

Re: Grounding Questions

06/15/2013 2:04 PM

Well, that pretty much covers most of the civilized world.

__________________
common knowledge...less common than common sense
Register to Reply
Register to Reply 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); bjb (1); cuba_pete (4); dhayanandhan (1); electricalexpert65 (2); IQ (3); leveles (1); lyn (1); pnaban (2); PWSlack (2); The.Tinkerer (2)