Water Chiller Performance Calulations-Basic Cycle
Posted December 10, 2014 1:00 AM by larhere
Water chillers are commonly employed to chill water for air conditioning systems. This chilled water is circulated thru cooling coils. Air is passed over the coils to be cooled and dehumidified for indoor comfort. The basic components of a water chiller are a compressor and motor, an evaporator, a condenser and assorted piping and controls. In this article we will describe the performance calculations for the basic water chiller thermodynamic cycle.
As an example for our discussion, we will use a compressor with R134a, a flooded evaporator (refrigerant on the shell side) and a shell & tube water cooled condenser also with refrigerant on the shell side. For simplicity of illustration we will assume an 85% efficient centrifugal compressor and no pressure drop in suction or discharge piping. Chilled water enters the evaporator at 54 oF and leaves at 44 oF. Cooling water enters the condenser at 85 oF and leaves at 95 oF.
The evaporation is a constant pressure process and the evaporator saturation pressure must be at a temperature colder than the leaving chilled water temperature for the heat transfer to occur. The refrigerant leaves the evaporator shell as a saturated vapor and enters the compressor.
The compressor supplies work to raise the refrigerant to the condenser saturation pressure. The condenser saturation pressure must be higher than the leaving condenser water temperature for heat transfer to occur. The compressor work required is the product of the refrigerant mass flow times the vapor enthalpy at the entrance to the condenser minus the vapor enthalpy leaving the evaporator.
The heat rejected in the condenser is the sum of the heat transferred in the evaporator plus the work input of the compressor. The condensed refrigerant leaves at the condenser saturation pressure, passes thru an expansion device that reduces the pressure to evaporator pressure, and enters the evaporator. In the expansion process, some of the liquid flashes to gas and the refrigerant entering the evaporator is a two phase mixture.
The chilled water is cooled in the evaporator by evaporating the refrigerant. The evaporator heat transfer capacity is equal to the building load. The refrigerant mass flow that must be delivered by the compressor is equal to the building load divided by the difference in enthalpy of the entering and leaving refrigerant conditions.
In the basic cycle, the liquid refrigerant leaves the condenser at its saturation temperature.
The refrigerant properties at various points in the cycle are:
Condenser Saturation Temperature, Tsat=97 oF
Evaporator Saturation Temperature, Tsat=42 oF
Enthalpy leaving Evaporator, hg=172.9 Btu/lbm (saturated vapor @ 42 oF )
Enthalpy leaving Condenser, hf=107.8 Btu/lbm (saturated liquid @ 97 oF )
Entropy entering Compressor, sg=0.412 Btu/lbm-R (saturated vapor @ 42 oF )
Enthalpy leaving Compressor, hg=181.3 Btu/lbm (ideal isentropic compression)
Isentropic enthalpy rise due to compression, ∆hcomp=181.3-172.9=8.4 Btu/lbm
Compressor efficiency, Ƞ=0.85
Enthalpy leaving Compressor hg=172.9+8.4/0.85=182.8 Btu/lbm
From these values several performance parameters of the cycle may be calculated on a per ton basis.
Capacity=12000 Btu/h-ton
Evaporator enthalpy rise=172.9-107.8=65.1 Btu/lbm
Refrigerant mass flow rate=12000/65.1=184.5 lbm/h-ton
Compressor work=184.5*8.4/0.85=1824 Btu/h-ton
= (1824 Btu/h-ton)/(3412 KW-h/BTU)=0.535KW/Ton
In future blogs we will discuss the performance improvements of subcoolers and economizers.
Editor's Note: CR4 would like to thank Jim Larson, GEA Consulting Associate, for contributing this blog entry.
Good Answers: 11
Re: Water Chiller Performance Calulations-Basic Cycle
12/10/2014 5:27 AM
Problem with surge for centrifugal compressor, and what's basic cycle? Meaning basic vapor compression or reverse carnot cycle?
" To infinity and beyond" - Buzz Lightyear
12/11/2014 12:07 PM
I'm using the vapor compression cycle. Can you elaborate on your comment "Problem with surge for centrifugal compressor"?
Good Answers: 11
12/13/2014 11:22 AM
Surge is phenomena with centifugal compressor when, it can not generate enough force causing a reverse flow instead of forward. This may help Carrier Chiller