Anonymous Poster #1

Lighting Protection

04/25/2015 8:18 AM

Dear All,

For new lightning protection is it necessary to connect to exiting lightning protection?

Any advise.

Regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#1

Re: Lighting protection

04/25/2015 11:24 AM

If both lighting protection systems are located in the same building-or at least 3.6 m apart-then you must. See, for instance, NFPA 780 ch.4.14 Common Grounding.

If they are not, in my opinion, still it will be better to do so

__________________
Julius
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Lighting Protection

04/25/2015 7:31 PM

Read the local codes.

Follow them.

Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#3

Re: Lighting Protection

04/27/2015 12:38 AM

1. what does the client or your employer want? discuss the situation with them. make them happy.

2. I know NFPA requires lightning for "all structures." BUT...... if its a single story building in a low - lightning area, not storing explosives or combustible materials, common sense ALSO applies.

__________________
BSEE but always learning
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Lighting Protection

04/27/2015 3:37 PM

What's the lightning protection exactly? What standard are you working to? What's the building and site? What's the existing protection consist of?

Please provide more information.

__________________
jack of all trades
Reply
Reply to Forum Thread 4 comments
Copy to Clipboard

Users who posted comments:

1capybara (1); 7anoter4 (1); jack of all trades (1); lyn (1)