Continuous Sensing of Partial Discharge on 11KV Cables, Connected in Ring Circuit

05/05/2015 8:24 AM

Hi friends,

Does anyone have experience with MV cable faults?

We have various 11KV & 6.6KV XPLE/PILC cables,from 100mtr to 5km in length connected through substations in ring circuits. In order to check the healthiness, we do carry out DC hipot and VLF test to check leaking current and weak points if any. What I am looking for is, a online continuouse partial discharge / leakage current sensing system to be connected at both ends of the cable in substation and to generate readings. Through this one can figure out the weak cables connected in the ring circuit with having suspected developing faults. So that planned and scheduled outage can be made for further testing or rectification in order to avoid unexpected cable breakdown outage.

Any ideas and suggestions ?

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Continuous Sensing of Partial Discharge on 11KV Cables, Connected in Ring Circuit

05/05/2015 3:55 PM

A quick Google search on "partial discharge monitoring" produces half a dozen likely suppliers of systems that do what you are asking. Why not try contacting some of them?

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Continuous Sensing of Partial Discharge on 11KV Cables, Connected in Ring Circuit

05/05/2015 4:23 PM

These guys make and sell the systems....

http://www.martec.co.za

Informative paper on methodology....

click here...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#3

Re: Continuous Sensing of Partial Discharge on 11KV Cables, Connected in Ring Circuit

05/06/2015 6:04 AM

The ability to detect leakage is possible and some offerings for equipment to detect this are available with varying advantages and disadvantages for each type. You will have to get fairly involved with each technology and approach to make a decision as to which works best for your system.

I would like to address the idea of DC hipot for this type of cable however. We did a lot of it for customers when I was still working and the statistical data that we accumulated said that the customers who did it had more failures of cables than those that did not. While it is claimed to be non-destructive testing, it has a cumulative effect of lowering the life of the cable. We had a few customers who allowed us to use power factor testing of the cable insulation which was able to detect the leakage current and capacitance change in the cable and subject the cable to only a few percent above rated voltage AC rather than DC. We could see the approach of aging on the cable and predict when the cable needed replacement a few years before failure occurred. Customers that used power factor testing had far fewer emergency cable failures than those that used DC Hipot. I was personally convinced that DC hipot contributed to the failure of this type of cable even though the use of DC hipot is the industry standard for the the testing and cable industry.

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#4

Re: Continuous Sensing of Partial Discharge on 11KV Cables, Connected in Ring Circuit

05/06/2015 9:07 AM

i was also wondering why it makes sense to do DC hipot testing on cables normally used for AC? and why DC testing would contribute to accelerated failures?

__________________
BSEE but always learning
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: Continuous Sensing of Partial Discharge on 11KV Cables, Connected in Ring Circuit

05/15/2015 6:30 AM

In my opinion your cables are fabricated following IEC 60502-2.In Ch.20 Electrical tests after installation

no partial discharge is mentioned. Only

20.1 D.C. voltage test of the oversheath and

20.2 Insulation test.

However, there are some remarks:

NOTE 1 A d.c. test may endanger the insulation system under test. Other test methods are under consideration.

NOTE 2 For installations which have been in use, lower voltages and/or shorter durations may be used. Values should be negotiated, taking into account the age, environment, history of breakdowns and the purpose of carrying.

So why to carry a such dangerous test for cables still operating?.