Given the source impendance of a busbar, how do yoou calculate 3 phase fault levels of a downstream substation?
Re: Fault Levels
07/16/2007 1:43 AM
the panel boards supplier can help you doing such calculations, just pass him the data about the cables sizes & lengths.
good luck
Popular Science - Weaponology - New Member Popular Science - Cosmology - New Member
Re: Fault Levels
07/17/2007 2:34 AM
You must add ALL the impedences from the bus to each downstream point
to the given source impedence and calculate for that point.
Don't forget to add in the downstream motor contributions, (less their impedances),
to the point in question.
Re: Fault Levels
07/17/2007 5:55 AM
refer any BSC engineering basic book and do it yourself!!
BNDas
Re: Fault Levels
07/17/2007 7:26 AM
Mr. Das don`t consider your self so smart ..........do your business?
Then why are you putting your problen in this forum...you also must read Primary class book again stupid..........Don`t make ur self escape goat in this forum.
Everybody has rite to share each n every sort of electrical problem here .One may be fresh,little experience & might be stupid just like you...........so take care next time
Re: Fault Levels
07/18/2007 7:27 AM
I think one should not do homework in this forum.. or should have basic knowledge of electrical engineering to join. Mr Guest come in forum with proper identy before abusing others. Go to a school get some knowledge and come here. I didn't put my problem at all. one Q i put in forum to know if there is any one can reply. But, with a frustration I didn't see proper view. Any way, I have already put my view and welcom e value addition on the topic. See my communications today.
BNDas
Re: Fault Levels
07/21/2007 12:29 AM
hi,
I hope this will help you,
i.e. (a) suppose 6.6 kv busbar,30kA
then source impd will be=phase volt (kV)/1.732*fault current (kA)
=6.6/1.732*30
=0.127 ohm will seen upto upsteam
(b) if 415 volt,20kA bus then
Source impd=0.415/1.732*20
=0.0119 ohm will seen upstream
I think this will help u
Good luck
Tadagids