I said before (http://cr4.globalspec.com/thread/100088/Downsizing-Neutrals-BS7616)
that according to the NEC, you cant downsize neutrals (grounded conductors) compared to the phase (hot) wires.
I was wrong - for feeders.
NEC 2014, art. 215.2A2 allows you to size the feeder neutrals same as the EGC (equipment grounding conductors) from table 250.122, which is much smaller than sizing them same as the phase (hot) wires from table 310.15.
example: feeder carries 160 amps using phase wires of 3/0 THHN copper per table 310.15. Breaker is 200 amps. Table 250.122 allows the feeder neutral to be 6 AWG.
This is huge downsizing, even greater than allowed by British Code.