Downsizing Neutrals in the NEC

06/04/2015 8:10 AM

I said before (http://cr4.globalspec.com/thread/100088/Downsizing-Neutrals-BS7616)

that according to the NEC, you cant downsize neutrals (grounded conductors) compared to the phase (hot) wires.

I was wrong - for feeders.

NEC 2014, art. 215.2A2 allows you to size the feeder neutrals same as the EGC (equipment grounding conductors) from table 250.122, which is much smaller than sizing them same as the phase (hot) wires from table 310.15.

example: feeder carries 160 amps using phase wires of 3/0 THHN copper per table 310.15. Breaker is 200 amps. Table 250.122 allows the feeder neutral to be 6 AWG.

This is huge downsizing, even greater than allowed by British Code.

__________________
BSEE but always learning
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#1

Re: Downsizing Neutrals in the NEC

06/04/2015 11:54 AM

Does the NEC also specify a maximum imbalance for the feeders?

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#2

Re: Downsizing Neutrals in the NEC

06/04/2015 12:54 PM

You realize that sometimes there are special cases such as when it is impossible to imbalance the load except by a major fault. The thinking is this: if a load goes single phase, then the feeder and return line (a.k.a. neutral) had better be the same size or it will melt.

Now ask yourself this. Do you want to be responsible for burning down a building and possibly killing people because you were trying to mis-read the code? Do it right or don't do it.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#3

Re: Downsizing Neutrals in the NEC

06/04/2015 2:08 PM

This could cause burning of three or four air-conditioning units.

__________________
CRTL-Z
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#4

Re: Downsizing Neutrals in the NEC

06/04/2015 2:12 PM

Please don't do any design for me. I'm scared.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#5

Re: Downsizing Neutrals in the NEC

06/04/2015 5:21 PM

No. De-rating/Down-sizing of the circuit neutral is totally dependent on what the downstream loading configuration of the feeder circuit is going to be.

The amount of current that the neutral is going to be carrying determines the AWG size of the neutral conductor.

Example: A 4 wire 277V 3 Phase lighting circuit that utilizes a phase and a neutral for each circuit presents a significantly higher load on a feeder circuit neutral than a 3 phase transformer that is Delta or Wye connected.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Anonymous Poster #1
#7
In reply to #5

Re: Downsizing Neutrals in the NEC

06/05/2015 4:38 AM

Example: A 4 wire 277V 3 Phase lighting circuit that utilizes a phase and a neutral for each circuit presents a significantly higher load on a feeder circuit neutral than a 3 phase transformer that is Delta or Wye connected.

Which is true, but of course there is actually no load carrying neutral going to that transformer so connected!! You need only the 3 phase connections........maybe a ground cable?

What am I missing here?????

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#8
In reply to #7

Re: Downsizing Neutrals in the NEC

06/05/2015 9:07 AM

A 3 phase transformer can be connected WYE primary with neutral and DELTA secondary without a neutral. The neutral my or may not be grounded depending on the location and application.

Or;

A 3 phase transformer can be connected as Delta primary with no neutral and WYE secondary with a neutral.

Often a Delta primary has one corner grounded for the purpose of metering and protection. Some refer to this ground as a neutral.

The transformer connection may be as an "open Delta".

All this and the many other types of equipment connections that a feeder may service is why the feeder service application should always dictate the neutral size.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Anonymous Poster #1
#9
In reply to #8

Re: Downsizing Neutrals in the NEC

06/05/2015 9:43 AM

That is FAR more than you said before.

Your original post was simply careless and only 50% correct....and could be called missleading!!

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#13
In reply to #7

Re: Downsizing Neutrals in the NEC

06/07/2015 12:42 AM

......the very small 0mm2 neutral conductor.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#6

Re: Downsizing Neutrals in the NEC

06/05/2015 4:15 AM

Im just quoting the NEC. If its not sensible, then the NEC should be amended.

I will propose an amendment to it. Such as "....protected by Overcurrent Protection Device so that the load carried by the ungrounded conductor can not exceed its ampacity" ......

PS - no, i never have and probably never have used this in any design, altho in the BS7671 (IEC) countries like India or the middle East, this is standard practice. I just saw a job (apartments and commercial, high rise building) where the feeder was [3c x 300mm2 + 1c x 185mm2]. but that it an easily balanced load.

__________________
BSEE but always learning
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#10
In reply to #6

Re: Downsizing Neutrals in the NEC

06/05/2015 6:32 PM

Yes, the devil is in the details.

The NEC is no different than any other code book as it has multiple disclaimers, and references that require intense awareness and thorough scrutiny.

Although the NEC is a very good guide often local codes are much more stringent and override it.

Knowing where you stand, what applies, and how to apply it is difficult at times but catamount to survival.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#11
In reply to #10

Re: Downsizing Neutrals in the NEC

06/05/2015 6:59 PM

Speaking of details, the word you meant was "paramount" or "tantamount":

http://www.thefreedictionary.com/catamount

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#12

Re: Downsizing Neutrals in the NEC

06/05/2015 10:07 PM

Friends,

Yes, in many cases the NEC does allow the neutral to be smaller than the phase conductors because it is supposed to only be carrying the imbalanced portion of the load. However, the increasing prevalence of electronic loads, such as electronic lighting ballasts, makes downsizing problematic. In single-phase (2 hot wires and a neutral, with the voltage on the two hot wires 180-degrwees apart), there is no problem with neutrals and electronic loads. However in three-phase (3 hot wires 120-degrees apart plus a neutral), the neutral current theoretically can be 150% of the phase current!

The reason is that the the non-linear load of electronics can impose significant amounts of harmonics onto the conductors. The "triplen" harmonics do NOT cancel out when you add the phases together, so neutral current can and often is larger than each of the phase currents. Codes and listing agencies have begun addressing this with rules that limit the percent of harmonics that can be imposed on the incoming circuits (one reason is the harmonics increase heating in the transformers so they have to be oversized or be designed with a "k-factor").

The NEC rules and exceptions come primarily from experience and analysis of failures. Therefore, the NEC does allow downsized neutrals in many cases, but it will require full-sized or even upsized ones in some cases.

--JMM

Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#14
In reply to #12

Re: Downsizing Neutrals in the NEC

06/09/2015 4:25 PM

You might be interested in knowing that a recent (within a year or two) UL study has shown that concerns around harmonic generated neutral currents may not be as much of a big deal as the copper sellers would want us all to swallow. I will see if I can dig up a link on the issue.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#15
In reply to #14

Re: Downsizing Neutrals in the NEC

06/09/2015 11:26 PM

North of 60,

I'd be happy to see that, if you find the link. --JMM

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#16
In reply to #14

Re: Downsizing Neutrals in the NEC

06/10/2015 2:41 AM

In the conductor sizes where a smaller neutral is permissable and very often part of the exfactory composite bundle I use aluminium. Saves a heap. Those copper barons....

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (1); Anonymous Poster (2); Brave Sir Robin (1); Crabtree (1); jmueller (2); North of 60 (1); NotUrOrdinaryJoe (1); RAMConsult (1); SHOCKHISCAN (3); Unredundant (1); Wal (2)