Element Current Alerter or Open Circuit Element Alerter

07/09/2015 8:08 AM

We had app. 40 heating elements on industrial refrigerator system. The heating elements are 240V ac and when the element is on position the current meter shows approximately 8 Amp is uses on it. 40 contactor is switching the elements and 40 indicatror is shows the elemets is powered. The problem is different. If one or more element is a open circuit how can we identify? The system must be 2 indicator on eof them must be shows if the elements are powered and the second indicators must be shows to us which element is burned or open circuit. How can we solve this problem without spent to much money.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#1

Re: Element Current Alerter or Open Circuit Element Alerter

07/09/2015 9:18 AM

If you know how to use one of these, you can diagnose the problem in about 10 minutes.

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Participant

Join Date: Aug 2012
Posts: 4
#2
In reply to #1

Re: Element Current Alerter or Open Circuit Element Alerter

07/09/2015 9:33 AM

Tahnks a lot for the answer but the end user must be know which refrigerator has a problem and before the technical perseon perhaps they must transfer the goods to another box.

Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#3
In reply to #2

Re: Element Current Alerter or Open Circuit Element Alerter

07/09/2015 10:17 AM

but the end user must be know which refrigerator has a problem

Ummmmmm....... the refrigerator that has the problem is the refrigerator that isn't cold. I just diagnosed your problem from half a world away.

Send me your address so I can send you my consultancy fee invoice! My minimum is $250.00 USD. Please have a money order ready! I take cash also, just no personal checks!

A good quality DMM or Digital Multi-Meter like one in the picture below in the hands of a trained technician is all you need!

Read the manual and have fun, just watch out for the AC voltage.... It BITES!

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#10
In reply to #2

Re: Element Current Alerter or Open Circuit Element Alerter

07/09/2015 11:02 AM

There are several voltage & current monitoring devices with programmable alarm contacts available in the market today.

If you want a simple circuit for monitoring each refrigerator heating element I would install a current monitoring and indicating device in series with each heating element on every machine that displays the DATA locally.

If this is a production line I would install monitoring devices that have both programmable alarm contacts and remote communication capability in Ethernet, MODBUS, DH485, or RS232 so that the alarms and DATA can be viewed by the operator at the control hub/room.

Although there are many good companies that offer these products I suggest you go to OMEGA Engineering and obtain their free technical application guides then review the guide that fits your particular application. www.omega.com

If for some reason you have trouble understanding the information then contact OMEGA Engineering for free technical application support on their offered products.

As I stated before there are many other reputable instrument & control vendors that offer the equipment you need.

Once you decide what is needed by referencing the free technical guide(s) you can then decide which particular product manufacturer you want to use.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
2
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#4

Re: Element Current Alerter or Open Circuit Element Alerter

07/09/2015 10:24 AM

This should do the trick:

LP1 will light when power's on. The 100:1 current transformer will try to push about 80mA through the 300R resistor (when the heater is drawing current), producing 24V across it, and lighting LP2. This assumes LP2 draws very little current - you may find a suitable filament lamp which will do the job, without needing the resistor, or you may need to adjust the resistor value to get a bright enough light.

Getting an indicator to light when the element fails is more tricky.

Bill's in the post.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#7
In reply to #4

Re: Element Current Alerter or Open Circuit Element Alerter

07/09/2015 10:43 AM

Too late to edit, but you can probably use a 3000R resistor, and 240V neons for both indicators (but it would need a 25W resistor!).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Good Answer
Participant

Join Date: Aug 2012
Posts: 4
#13
In reply to #4

Re: Element Current Alerter or Open Circuit Element Alerter

07/10/2015 1:37 AM

The information is very useful but I need to learn what is the CT100:1 brand and model for order. Where can I buy and which product number can be order.

Register to Reply Score 1 for Off Topic
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#5

Re: Element current alerter or open circuit element alerter

07/09/2015 10:29 AM

GA.

These would connect into his existing system well, I just don't know if they have the technical experience to install them!

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8
In reply to #5

Re: Element current alerter or open circuit element alerter

07/09/2015 10:53 AM

I say they don't.

"If one or more element is a open circuit how can we identify?"

Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#9
In reply to #5

Re: Element current alerter or open circuit element alerter

07/09/2015 10:59 AM

Thanks MacGyver, I hope they do, or figure it pretty quick, in the worst scenario the learning curve will cost $9.80

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #9

Re: Element current alerter or open circuit element alerter

07/09/2015 11:07 AM

And the cost of a box full of "goods".

Besides, the wiring diagram on the back of each unit is in black and white, but the terminals are green and blue. ;>)

Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#20
In reply to #11

Re: Element current alerter or open circuit element alerter

07/10/2015 5:28 PM

Since he says it is a refrigeration system, all one has to do is look at the evaps and you can see which are not defrosting, put a meter on each element and there you are. If the evaps are clearing the ice and frost in each defrost cyccle, who cares if all of the elements are working! -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#21
In reply to #20

Re: Element current alerter or open circuit element alerter

07/10/2015 7:13 PM

Often you can't see which one is not defrosting until the ice is protruding from the coils, by then the element can be encased and it's damned hard to get to it.

Manually defrosting a coil is tedious, and it won't clear itself if there are other evaps. in the room.

If a coil freezes, its airflow will cease (I've seen them where the fan itself was encased in ice). If it is only one evap. in the room then you will soon know as the temp. rises, but many large freezers have multiple evap. units, so detection of a fault is not necessarily done quickly, and as many rooms have door switches to turn the airflow off when the door is open, then freezer staff are unlikely to be aware of lack of airflow from a coil.

There is also the possibility that these are humidifier rather than defrost elements.

Edit... I removed your OT vote as I don't consider your point OT at all.

Register to Reply
2
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#6

Re: Element Current Alerter or Open Circuit Element Alerter

07/09/2015 10:30 AM

You can do as Yahlasit has suggested or, if cash is really tight, you can add an extra indicator and a couple of diodes as below.

When the contacts are open, and provided the element circuit is complete, then the fail indicator will light, this also serves as a lamp test. If the element is open circuit, then the fail indicator will not light.

When the contacts are closed, the element and power indicator will be energised, the fail indicator will be extinguished.

To test any element, simply open the contactor, if the lamp fails to illuminate, the circuit through the element is incomplete, or the lamp is faulty, but this will be regularly tested as above (a separate lamp test switch could be added if required).

The diodes prevent the indicators lighting incorrectly.

A very small current will flow through the element when the contactor is open, ie a 2w indicator globe in series with the 2000w element will result in a current of about 8mA.

Provisos for this circuit:-

1. The fail indicator must be low wattage.

2. You must isolate the supply before servicing the elements as the feed to the element will be live via the fail indicator even when the contactor is open.

3. Be aware that the fail indicator will be illuminated whenever the isolator is closed and the contactor is open.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#12
In reply to #6

Re: Element Current Alerter or Open Circuit Element Alerter

07/09/2015 11:17 AM

Hello Spades, I'm a big fan of simplicity and your design will work wonderfully; but then I thought that an industrial operation that involves 40 freezers should render some profit, so they can afford an upgrade to their monitoring system. GA, I confess that my first thought was very similar to that of yours.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Participant

Join Date: Aug 2012
Posts: 4
#14
In reply to #6

Re: Element Current Alerter or Open Circuit Element Alerter

07/10/2015 1:40 AM

The circuit is useful. But what is the diode values and the indicator details? ie diode can bu use 1N4007 and etc if we give an order. The load is a heating elementand it works with a 240V ac and when it powered the current meter is shows 8 Amp. consumption on the line.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#15
In reply to #14

Re: Element Current Alerter or Open Circuit Element Alerter

07/10/2015 2:23 AM

The diodes can be just about anything rated at 400 peak inverse volts and adequate forward current to manage the indicator lamp amps (2 amps would be quite adequate). They are not carrying full element current. 1N4007 would be fine as would the lower rated 1N4004.

The lamps can be anything from a low wattage incandescent (up to about 5 watts) to neon to LED.

If using LEDs, then use full wave 240v AC indicator packages.

The AC will be half wave through the indicators, but this will not cause any problems.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#16
In reply to #6

Re: Element Current Alerter or Open Circuit Element Alerter

07/10/2015 7:03 AM

"The diodes prevent the indicators lighting incorrectly." Sorry if I'm being thick, but how?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#17
In reply to #16

Re: Element Current Alerter or Open Circuit Element Alerter

07/10/2015 8:57 AM

If the diodes were not present and the element was open circuit, then both indicators would light when the contact is open.

This is incorrect as both indicators should be off at this point.

The power indicator should only light when the contact is closed, and the fail indicator should only light when the contact is open and the element is intact. Only half voltage would be applied to each indicator, but this is sufficient to light them, particularly if they are LED or neon.

The diodes being in opposition prevent the error by blocking both half cycles through the indicators when the contact is open and the element is faulty, but otherwise allow them to light at the correct times.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#18
In reply to #17

Re: Element Current Alerter or Open Circuit Element Alerter

07/10/2015 10:05 AM

Oh yeah, thanks. I was being thick! . Been a long, hard week.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Power-User

Join Date: Jan 2015
Location: Johannesburg, South Africa
Posts: 248
Good Answers: 3
#19

Re: Element Current Alerter or Open Circuit Element Alerter

07/10/2015 2:50 PM

@kazimates, you say you have 40 indicators showing that the element is powered. You also say you have an Amp meter that indicate 8Amp, is this an Amp meter for every heater or is it 8 Amps for all. This is only 200 mA per heater and that add to 48 Watt per heater. I think you have an Amp meter for every heater already, that means that every heater is 2000 Watt heaters, so if the heater is powered and the amp meter reads 8 Amp the heater is working, if the Amp meter show nothing it means the heater is not drawing (allowing) current and that mean it is burnt out or technically called "Open circuit". I'm not sure what you mean by burned but if you refer to a short circuit, rest in peace because that will blow up something if you do not have a fuse on every circuit, if you have the fuse for the short circuit will be blown.

__________________
Tragedy for Engineers is thinking they know so much that they can not learn from any body else.
Register to Reply Score 2 for Off Topic
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Circuit Breaker (1); JohnDG (4); kazimates (3); lyn (2); Oomborrie (1); Original_Macgyver (3); SHOCKHISCAN (1); spades (4); Yahlasit (2)

Previous in Forum: Electrical Power   Next in Forum: Driving Headphones from a Speaker Output

Advertisement