VFD Motor Terminal Heatup Issue

07/31/2015 3:01 PM

Dear Sir,

i am facing problem as, any one can help

Sl noProblemAction Taken
11.Terminal Heat up.VFD Motor,355kw;M2BA355MLB4;585Amps,415 volts;1487 RPM;1.Termination done
2. Motor Flash inside the winding leads -2 times2. change the motor with Spare
3. Still there is heat up of cable Heatup terminal box, it is found extended to winding leads3.Put the bimetallic washers
4. Laid the 1more Aluminium cable of 240sqmm form load centre (vfd) to motor of 190mts (previously 2run of 240 sqmm of aluminium from drive to motor of 190mtr; )
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: VFD MOTOR TERMINAL HEATUP ISSUE

07/31/2015 3:39 PM

you're over your head, you should never expect to find remedies from an internet forum, call in a professional electrician who services VFDS

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#2

Re: VFD MOTOR TERMINAL HEATUP ISSUE

07/31/2015 7:03 PM

IS this an AC or DC motor?

If DC; Check motor brushes for wear, tension, and correct grade, check motor bearings for binding, and check motor windings for faults.

If AC; Check motor winding(s) for shorts and ground(s).

Look carefully at the rotor, stator, armature laminations for damaged insulation and/or burn holes regardless of whether the motor is AC or DC.

Make sure the VFD and the VFD programming are 100% compatible with the motor. (Is the Volts-per-hertz correct,? Is the frequency correct? Is the drive and motor HP matched? Is the output voltage of the VFD correct? IS the VFD input voltage correct? IS the VFD internally shorted or otherwise damaged.)

If you do not know how to do any/all of this, hire a competent technician or rent a reputable technical service company to troubleshoot the problem.

Good luck and stay safe.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6
In reply to #2

Re: VFD MOTOR TERMINAL HEATUP ISSUE

08/01/2015 7:05 AM

No VFDs on DC motors. Maybe a PWMD....

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: VFD MOTOR TERMINAL HEATUP ISSUE

07/31/2015 7:46 PM

There is no hope of you ever solving this problem. None.Since we know nothing of the VFD or motor, except the motor is ABB.

Beg them for help.Be prepared with much more information.

Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#4

Re: VFD MOTOR TERMINAL HEATUP ISSUE

07/31/2015 8:47 PM

Aluminium wiring is notoriously difficult to terminate and requires connectors etc specially made for joining aluminium.

The problem is progressive joint oxidation, which, as it progresses, reduces the current carrying footprint, which make more heat etc = possible runaway positive feedback.

This does resemble your problem, so you might need some help from a pro

__________________
Per Ardua Ad Astra
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#7
In reply to #4

Re: VFD MOTOR TERMINAL HEATUP ISSUE

08/01/2015 8:53 AM

I doubt this is the problem. OP sounds like he is getting a new installation to behave so oxidising isn't it (yet)

It's not hard to terminate, no notoriety, if performed correctly.

Crappy Al joints show up as localised heating.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#9
In reply to #7

Re: VFD MOTOR TERMINAL HEATUP ISSUE

08/01/2015 9:25 AM

I based my comment on these.

<<Still there is heat up of cable Heatup terminal box, it is found extended to winding leads.>>

I interpreted this to be heating causes by a high resistance connection being transmitted down the wires. These are substantial connectors

<<3.Put the bimetallic washers>>

this sounds like some aluminium to another metal connection, which merits extra attention.

It would be a good idea to use one of those RI thermal readers, or even a FLIR cam

__________________
Per Ardua Ad Astra
Register to Reply
Guru
Canada - Member - New Member

Join Date: Jul 2013
Location: Canada but south of 49
Posts: 895
Good Answers: 20
#14
In reply to #9

Re: VFD MOTOR TERMINAL HEATUP ISSUE

08/04/2015 11:28 AM

Any and all aluminum connections need special attention, at any and all times. Even new connections that are not torqued correctly at installation.

__________________
Never stop learning
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: VFD MOTOR TERMINAL HEATUP ISSUE

07/31/2015 9:39 PM

It's really not a good idea to use a general purpose motor on a VFD since the insulation cannot handle the voltage spikes. Replace it with a VFD rated motor that conforms to the IEC 61800 series, particularly IEC 61800-4.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8

Re: VFD MOTOR TERMINAL HEATUP ISSUE

08/01/2015 9:04 AM

Just to confirm, you now have 9 x 240mm2 ( 3x 720mm2 per phase equivalent ) and the cable is still cooking?

Have you tried a DOL start to see what happens?

What size Trafo/genset are you using?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Member

Join Date: Jun 2012
Posts: 7
#10

Re: VFD Motor Terminal Heatup Issue

08/01/2015 1:50 PM

1. IT IS VFD MOTOR(MOTOR IS DESIGN FOR VFD APPLICATION)

2. FAN APPLICATION.

3. VARIABLE SPEED IS REQUIRED,SO WE ARE USING VFD DRIVE.

4. TAKING NORMAL CURRENT i.e. BELOW RATED CURRENT.

5. DOL IS NOT POSSIBLE

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#11
In reply to #10

Re: VFD Motor Terminal Heatup Issue

08/03/2015 9:58 AM

why are you screaming?

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#12
In reply to #10

Re: VFD Motor Terminal Heatup Issue

08/03/2015 2:46 PM

NOISY bugger!

__________________
Good moaning!
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#16
In reply to #10

Re: VFD Motor Terminal Heatup Issue

08/07/2015 5:14 AM

https://en.wikipedia.org/wiki/Variable-frequency_drive

Have a look at all the citations at the end as well and you may find your answer written in one of those. All sorts of issues discussed. I can't read it for you, sorry, it's your sick baby.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#13

Re: VFD Motor Terminal Heatup Issue

08/04/2015 7:15 AM
__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#15

Re: VFD Motor Terminal Heatup Issue

08/04/2015 2:35 PM

I NEVER recommend using aluminum conductors for running out to motors from VFDs. It is BEGGING for trouble. I do not know of a single VFD manufacturer who does not say that the motor leads should always be copper. I also do not know of a single manufacturer of VFD rated cables that uses aluminum.

One of the main problems with the connections between VFDs and motors is what is called the "reflected wave" phenomenon. This is a capacitive coupling effect in the adjacent conductors because of the high speed switching of the transistor pulses, which causes a voltage to be expressed on the conductors on top of the normal voltage, a "standing wave" if you will. That standing wave travels down to the first point of an impedance mismatch, usually the motor terminals, and bounces back, called "reflecting", where it then adds to the next wave coming at it and increases. The potential on those reflected wave spikes eventually increases to up to 3x the line voltage and breaks down the insulation in the motor windings.

But long before that happens, that first point of impedance mismatch is also the first place the problems begin. Most if not all VFD rated motors will have copper windings. Aluminum has a lower natural impedance than copper so it more easily passes higher frequencies present in the PWM output to the motor. But because the copper windings will have a higher impedance, that not only makes the standing wave creating more likely, the junction also BECOMES the low pas filter (of sorst) for the higher frequency harmonics, "filtering" them by turning them into heat. Using aluminum conductors almost GUARANTEES that there will be a sever impedance mismatch at the motor terminations, and sever heating.

RTFM...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

aurizon (2); Crabtree (1); DEVARAJ (1); Fredski (2); JRaef (1); Kevin LaPaire (1); lyn (1); RAMConsult (1); SHOCKHISCAN (1); Wal (5)