Water Pump Energy Consumption

10/09/2015 4:33 AM

what is mentioned as "power(Kw or Hp)" in electric water pump? Is this input power to the motor regardless of flow rate or head? If 1Kw pump used for 1hour what is the energy consumption?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#1

Re: Water Pump Energy Consumption

10/09/2015 5:25 AM

This was discussed at length in a thread started 15 Sept.

For your 2nd question, have a think about it!

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#2

Re: Water Pump Energy Consumption

10/09/2015 6:15 AM

The power rating (as noted on its name plate) of an electric motor is its output or shaft power. The actual amount of energy that it consumes will depend on the applied load. Less load will result in lower power consumption.

Contrary to what may be intuitive, the energy consumed by a motor rated at 1kW that is used for one hour at full load will not be 1kWh but will be somewhat more.

For example, a single phase 240v motor with a plate rating of 1kW and pf of 0.8 will draw roughly 8 amps or 1.5kW at full load, and will therefore consume 1.5kWh if run at full load for 1 hour.

You can generally determine this from the name plate by doing a bit of math.

For a single phase motor - Power (consumed) = Volts x amps x pf

For a 3 phase motor - Power (consumed) = √3 x Volts x amps x pf.

pf is often shown as cosφ on the plate.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#4
In reply to #2

Re: Water Pump Energy Consumption

10/09/2015 9:46 AM

But for OP's question - what is mentioned as "power(Kw or Hp)" in electric water pump? Is this input power to the motor regardless of flow rate or head? - we have no way of knowing. It could be the electric power, the shaft power into the pump or even conceivably the hydraulic power. The person who does (or should) know is whoever gave the figure, and OP should ask him. This was covered in the earlier thread.

To calculate electrical power (at rated output), pf doesn't come into it. Divide the rated power by the efficiency, not the pf. As it happens, efficiency 67% is about right for a 1kW motor, so electrical power 1.5kW is a fair estimate. BTW 1kW is not a standard rating, at least not for 3-phase motors. If it is for 1-phase I'll stand corrected.

pf comes in when calculating amps, but to get shaft power from volts and amps, need to multiply by pf (and efficiency) so it cancels.

In case it helps the OP, the actual shaft power into the pump is likely to be a bit less than motor rating (as it will fall between 2 standard ratings and the higher should be selected) and it varies with where the pump operates on its Q/H curve.

__________________
Give masochists a fair crack of the whip
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#9
In reply to #4

Re: Water Pump Energy Consumption

10/09/2015 5:21 PM

"To calculate electrical power (at rated output), pf doesn't come into it. Divide the rated power by the efficiency, not the pf."

Hmmm.. To quote some info straight from page 3 of this motor manufacturer's website " Single-phase electrical power is calculated as follows: Electrical power = Voltage x Current x Power Factor - 3-phase electrical power calculation in a circuit is slightly different: Electrical power = 1,732 • Voltage • Current • Power Factor".

This Allen-Bradley site concurs with the above.

The motor's efficiency is simply a ratio of it's mechanical output power divided by its electrical input power. The efficiency of a motor generally peaks at around 75% full load and then drops off, so using efficiency to calculate power consumption would wrongly suggest that said power consumption would be less at full load than at 3/4 load. It is, however, correct to use efficiency when calculating output power, multiplying the motor input power by the efficiency as a decimal will give a close approximation of output power.

You're correct that 1kW is not a standard motor, the number was used purely as an example to make the numbers less complex.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#10
In reply to #9

Re: Water Pump Energy Consumption

10/10/2015 6:59 AM

To quote some info straight from page 3 of this motor manufacturer's website " Single-phase electrical power is calculated as follows: Electrical power = Voltage x Current x Power Factor - 3-phase electrical power calculation in a circuit is slightly different: Electrical power = 1,732 • Voltage • Current • Power Factor".

That's correct, but it doesn't relate to output (shaft) power. It just tells us electrical input kW = KVA*pf.

Allen-Bradley could easily cause confusion IMHO. Sticking to 1-phase, as that covers everything we're discussing, and can we use V for volts as I mix up E for volts with Efficiency?

He says (1st formula) To Find Amperes when HP is known I = 746*HP/V/Eff/pf. He doesn't make it immediately clear, but HP here is shaft power.

He then says To Find Amperes when kW is known I = 1000*kW/V/pf. Eff is not in there, because kW here is electrical input. Confusing or what?

Further down he puts HP formula the other way round, giving output HP = V*I*Eff/746. This confirms HP is output in 1st formula. To be fair, he never uses kW for shaft power, so if kW is always read as electrical kW, it's OK. Fine if you're US based, but for metric types, need to keep a clear head!

The motor's efficiency is simply a ratio of its mechanical output power divided by its electrical input power. I know, that's the point of my posts!

The efficiency of a motor generally peaks at around 75% full load and then drops off, so using efficiency to calculate power consumption would wrongly suggest that said power consumption would be less at full load than at 3/4 load. When calculating electrical power at 3/4 load, you divide the 3/4 load, not the rated output, by efficiency, so input power is still lower, although efficiency is worse.

I thought that's what you'd done with the 1kW, I wasn't suggesting you don't know standard motor ratings .

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9911
Good Answers: 1141
#3

Re: Water Pump Energy Consumption

10/09/2015 9:30 AM

The actual work done is pressure x volume/sec. If the pump is just building up head, any power consumed is wasted.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5
In reply to #3

Re: Water Pump Energy Consumption

10/09/2015 10:07 AM

To be pedantic, the actual hydraulic power is pressure x volume/sec. The work done is pressure x volume.

__________________
Give masochists a fair crack of the whip
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9911
Good Answers: 1141
#8
In reply to #5

Re: Water Pump Energy Consumption

10/09/2015 5:18 PM

Correct, that's what I meant to say.

Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Water Pump Energy Consumption

10/09/2015 12:48 PM

If your INTENT in asking the question is related to the nameplate data from the MOTOR driving the pump, then as said, that is the SHAFT (mechanical) power that the motor is CAPABLE of, nothing more. A "pump" as a complete machine will not technically be "rated" in HP or kW, it will be base on head and flow, which DETERMINES the required kW or HP at the shaft when operating at the maximum design point. But generally since motors are only made on certain sizes but must provide AT LEAST that much shaft power, they end up over sized. How much depends on the design philosophy of the engineer and the economics of the sales dept.

Then once you have a motor selected, how much energy it ACTUALLY consumes becomes that flow and pressure discussion, coupled with the efficiency of the motor itself. In other words, looking at the nameplate kW or HP on the motor of a pump only tells you the MAXIMUM energy use, nothing actual. You have to measure it, or estimate it based on the known output of the pump.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7

Re: Water Pump Energy Consumption

10/09/2015 12:55 PM

A 1 kw motorized pump or a 1 hp motorized pump are what's called the nominal size, and is only an approximation of capacity and power requirement...actual measurement of power consumed and/or work produced will vary....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Codemaster (4); JRaef (1); Rixter (2); SolarEagle (1); spades (2)

Previous in Forum: Synchronous Generator/Motor   Next in Forum: Wiring a MCCB

Advertisement