Two Watt Meter Method Power Measurement

01/10/2016 4:12 AM

When I am using two watt meter method power measurement one of the watt meter is showing reverse reading

what can be cause and how to rectify it

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: two watt meter method power measurement

01/10/2016 4:46 AM

Are CT's used? Quick and easy solution if they are.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#2

Re: two watt meter method power measurement

01/10/2016 8:51 AM

ESO is always a possibility.

[I've suffered with this condition, too. ]

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: two watt meter method power measurement

01/10/2016 10:19 AM
Register to Reply
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4

Re: two watt meter method power measurement

01/10/2016 11:19 AM

It is important to realise that one wattmeter may read negative. If the power factor is exactly 0.5 then one wattmeter may read zero.

The power is the sum of the readings respecting the sign e.g. w1 + (-w2) = w1 - w2. If the circuit connects two generators, the sign of the sum gives the direction of power flow.

If the wattmeter has a pointer which can only move to full scale in one direction, then the voltage coil connections must be reversed and the reading used as a negative value. It is important to realise that if you connect the meters wrong, you get the watts wrong. That you have connections as on the connection diagram is essential.

The third of the references given by Lyn writes that the "two wattmeter" method is not much used because of this reversal. This is not true, the typical "2 element" watt transducer or instrument for "3 phase, 3 wire, unbalanced load" just has "two polarity" measurement elements, so the subtraction is automatic when the element outputs are added together.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9913
Good Answers: 1141
#5

Re: two watt meter method power measurement

01/10/2016 12:17 PM

If TonyS is too subtle, here are a few more hints:

1. Power = volts x amps

2. What happens to current waveform if you reverse the CT leads (or run the wire through in the other direction)?

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6

Re: two watt meter method power measurement

01/10/2016 4:56 PM

Assuming that you paid strict attention to both the voltage and current polarities (and got them correct), then the cause is improper thinking that leads to the conclusion that something is wrong when it isn't; i.e., not fully understanding the techniques that you are using.

You rectify the situation by paying attention to detail and learning the basics before attempting to analyze the results. 67Model explains the theory, reread his post.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#7

Re: Two Watt Meter Method Power Measurement

01/11/2016 9:08 AM

Taken from one of Lyn's links....and assuming 3-phase power...

"...When using the two-wattmeter method, it is important to note that the reading of one wattmeter should be reversed if the power factor of the system is less than 0.5. In such a case, the leads of one wattmeter may have to be reversed in order to get a positive reading. In the case of a power factor less than 0.5, the readings must be subtracted instead of being added...."

....not that I'm much wiser... I don't know the power factor...and I don't know which reading to reverse.... or which wires to reverse (amps or volts or both)...and having done so... which readings are then added or subtracted.....

I suppose I could work it out by myself with a bit more study....but not at the moment.

Food for thought for the OP. I mention it for what it is worth.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8
In reply to #7

Re: Two Watt Meter Method Power Measurement

01/11/2016 3:04 PM

Horace40,

I suggest you look at my post #4. I looked at a reference textbook before I wrote it and was careful what I did and did not say.

I do not think what you quote from Lyn's link is accurate or helpful to the "beginner". If the 3 phase load is perfectly balanced (power factor and current/voltage) then one wattmeter reads zero at 0.5 power factor.

I suspect that (again balanced) for power factors >0.5, both wattmeters read +, while for <0.5, one reads negative.

Also my reference said "reverse the voltage coil" ( to accurately read the negative value, if the needle goes backwards onto a zero stop) - that is far easier and less error-prone to do than breaking or switching a current circuit - also far safer than switching a CT current circuit!!

But a real situation is that the load is rarely perfectly balanced and one is measuring to get the facts (and likely to need a convenient way to switch voltage polarity while on load!!).

One phase could be near zero power factor and another resistive (you would have to move your two meters to get phase by phase readings to get a better "grip" on the loads). I would look closely at the idea that a negative reading always means power factor <0.5.

If I did not have the maker's connection diagram, I would proceed by connecting a suitable resistive load to a wall socket via the wattmeter (and step-down transfo if needed) (also voltmeter & ammeter as watts check). This would find standard polarities for a positive reading It would not matter if current and voltage polarities were reversed compared to the maker's diagram so long as you keep with the source - load side and terminal connections you have discovered.

67model

Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#9
In reply to #8

Re: Two Watt Meter Method Power Measurement

01/11/2016 7:00 PM

Hello 67model

I started my post before i saw yours. By the time I finished reading Lyn's links and writing my reply, your post (that answers some of my questions thank you) came in before mine was posted 7th on the list. Just unlucky timing.

What I quoted was 100% accurate - inasmuch that it was a direct 'copy-and-paste' from Lyn's link. See for yourself about half way down 1st page :-

http://electrical-engineering-portal.com/power-measurement-in-a-three-phase-system

A power factor of less than 0.5 might be a direct hit and a complete answer to the OP in terms of the limited info we have been given.

But if not, then the reasons in the link about reverse wiring and reverse readings are OK - but not explained clearly - leaving just as many queries - which is why I made the point - that hopefully can be answered by more knowledge gleaned from your post and others.

The OP should be able to make some sense out of it by now.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#10
In reply to #9

Re: Two Watt Meter Method Power Measurement

01/12/2016 6:28 AM

horace40

I did not mean to suggest you misquoted. But what was in the reference about 0.5 power factor was probably based on the load being balanced - without including that limitation.

regards,

67model

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#11
In reply to #10

Re: Two Watt Meter Method Power Measurement

01/12/2016 1:13 PM

I wonder what Kaydee the OP thought about it all?

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (4); horace40 (2); lyn (1); RAMConsult (1); redfred (1); Rixter (1); TonyS (1)

Previous in Forum: AC Motor   Next in Forum: Induction Motor Question

Advertisement