03/14/2016 2:29 AM
Hello Experts,
What are the advantages/ disadvantages of ungrounded wye / grounded wye in the YNd11(Wye Primary-delta secondary) transformer?
Re: Ungrounded Vs grounded wye in transformer primary
03/14/2016 3:30 AM
Home work alert!
At least have the decency to tell us what you think it is and we can correct you.
Effort man, effort!
03/14/2016 4:26 AM
Hi Smith,
Say If a fault between the breaker at the upstream of the transformer and the transformer (YNd11) with Y solidly grounded) should occur, would the fault current flow into the neutral of the transformer or to the source ground ?
Would the residually connected CT work for ground faults if the neutral is ungrounded?
03/14/2016 6:59 AM
It depends on the fault, Mildred. If the transformer is correctly protected then it will be deenergised before any damage is done.
Good moaning!
Good Answers: 42
03/16/2016 2:52 AM
I think the short-circuit current will be divided-according to each path impedance-into 2 parts: one through transformer neutral and second to remote system neutral. What do you think?
Julius
Good Answers: 42
03/16/2016 4:58 AM
If the System is -well- grounded then if a short-circuit occurs downstream the CT a current will flow from the grounded phase conductor to the remote grounding point of the System and then the sum of currents of all phases will be the grounding current-it does not important if the neutral of the transformer connected downstream the CT is grounded or not.
Julius
Good Answers: 444
03/14/2016 12:00 PM
How did you answer this interview question?