Electric/Diesel Fire Pump-NFPA

04/01/2016 2:30 AM

Hi,

I just need to ask please if it is allowed in NFPA to connect an electric fire pump to a normal (utility) power source only (without the need to an alternate power source as generator) in case a diesel fire pump is used in conjunction with the electric fire pump.

Awaiting your reply.

Thank you a lot.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: electric/diesel fire pump-NFPA

04/01/2016 2:58 AM

So you have a dedicated full capacity diesel driven fire pump, and you want to know if you can install a second full capacity electric fire pump strictly as a backup system should the diesel pump fail.

There's no reason why you can't have redundant systems, as long as they both meet the applicable codes in the jurisdiction where they are installed. However the final decision(s) will rest with the AHJ (Authority Having Jurisdiction) and/or the Insurance Underwriter, whichever has the more stringent requirement(s). Be sure to get the owner's approval in writing as well.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Score 1 for Good Answer
3
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#2

Re: electric/diesel fire pump-NFPA

04/01/2016 3:55 AM

Most fire marshals would be delighted to have 2 fire pumps available for independent use.

I would think that clause 9.3 covers your query adequately.

Specifically sub clause 9.3.3 which states that "An alternate source of power for the primary fire pump shall not be required where a back-up engine driven fire pump, steam turbine driven fire pump or back-up electric driven fire pump with independent power source meeting 9.2.2 is installed in accordance with this standard".

Just make sure that your diesel pump meets all of the requirements of the regulations.

A decent chat with the local fire marshal should soon sort you out.

Reply Good Answer (Score 3)
Reply to Forum Thread 2 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!

Previous in Forum: Power Systems Modelling   Next in Forum: Sizing of DB for Outdoor Lighting

Advertisement