THD Value 4%/5%/6%, What Should Be the Counter Measures?

06/19/2016 6:03 AM

Dear Friends;

At the power distribution system (380V 50HZ) of our Corrugator plant, we have Nokian PF controller. As the Nokian Controller also measures the harmonics, so I have found that controller displays the THD value some time 4% some time 5% and some time 6%. What do you think would I require any counter measures or this THD value is not harmful? I have checked the current of power factor capacitors and found within their limit.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#1

Re: THD value 4%/5%/6%, what should be the counter measures?

06/19/2016 7:31 AM

What we think in this instance is of little importance.

The harmonics expectations of your local power authority and regulator are what needs to be reviewed and understood. You could be causing all sorts of distortion in local radio frequencies, you could be causing all sorts of problems with injected ripple controllers used by some power companies.

You need to ask them.

__________________
Just an Engineer from the land down under.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: THD value 4%/5%/6%, what should be the counter measures?

06/19/2016 11:50 AM
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: THD Value 4%/5%/6%, What Should Be the Counter Measures?

06/20/2016 5:48 AM

In my opinion, you may follow the

IEEE Std 519-2014

IEEE Recommended Practices and Requirements for Harmonic Control in Electrical Power Systems

and/or:

IEC 61000-3-2: Limits for harmonic current emissions (equipment input current <= 16A per phase)

IEC 61000-3-4: Limitation of emission of harmonic currents in low-voltage power supply systems for equipment with rated current greater than 16 A per phase

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: THD Value 4%/5%/6%, What Should Be the Counter Measures?

06/20/2016 2:23 PM

In order to eliminate the harmonics here may found some of the recommendations:

http://www.engineering.schneider-electric.dk/Attachments/ed/guide/guide_harmonic_detection_and_filtering.pdf

__________________
Julius
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#5

Re: THD Value 4%/5%/6%, What Should Be the Counter Measures?

06/20/2016 3:09 PM

None of the links I've looked at in this thread mention the detrimental effects that the harmonics present in the outputs of many Variable Frequency Drives appear to have on the bearings of the motors being driven. I've seen more than one article recently that indicate that the harmonics contribute to pitting of the balls and races of the motor bearings. These harmonics are on the outputs of the VFDs, but energy laws specify that such harmonics at the output must cause (not necessarily the same) harmonics reflected back into the supply.

These reflected harmonics (as well as harmonics from other sources) could well have some detrimental effects on non-VFD powered motors and their bearings, at least when in the same plant.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); dkwarner (1); Just an Engineer (1); lyn (1)