Cascade PID Control with Multiple Slaves

07/26/2016 3:03 AM

Hi All,

I am trying to figure out how to develop a logic on Emerson DeltaV, where in we have master PID which reads an Input and supposed to drive 4 Slave PIDs in Master-Slave Cascade Loop, I have normally used configurations in 2 PIDs which are driven one as master and other as slave. But the current requirement is 1 master and 4 slave PIDs.

How to actually wire the BackCal Input and BackOutput in this configuration?

Application is for a Bioreactor where we need to maintain dissolved oxygen concentraion and Inputs are 4 different gases with different flow rates.

Regards

Madhusudhan

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Cascade PID Control with Multiple Slaves

07/26/2016 2:45 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#2

Re: Cascade PID Control with Multiple Slaves

07/27/2016 1:43 PM

I've seen some people who just copy back the Master Output for the BackCal Input and BackOutput (different names on different platforms).

This doesn't give you the advantages (if really available ) of having an idea of how the process is actually responding, and allows the operator to switch modes with perhaps smaller bumps, less monetary loss.

You may wish to externally constrain under what conditions the operator can make a control configuration change, to externally build in the protection these signals give you.

The other possibility is to build an equation that sums the effect of the normal or typical ranges of the 4 variables (MV), as a model for the total DO Process Variable you are manipulating. This could be complex, but perhaps 2nd order polynomial regression for each of the 4 components will work. This model will likely will need to be developed on an operating installation. You will have to estimate the cost of developing this to the possible benefit. If you are controlling a million dollar per day reactor, with highly variable feedstock, and O2 consumption, then the complexity may be justified.

If putting the process in MANUAL control requires a few tweaks with minutes to spare before the reactor becomes unprofitable, then simplicity is what you should first shoot for.

Register to Reply