Anonymous Poster #1

Over Voltage Ground Relay

09/26/2016 12:20 PM

The phase to phase voltages are consistent with each other. The phase to neutral voltages are not constant. Our system is ungrouded system. There is no ground fault but the numerical ground over voltage relay gets activated. The relay is set at 10V, 0.3s

Why the phase to neutral volatages are not consistent despite there is no ground fault. Two runs of single core cables are used from the transformer Delta secondary to the switchgear. The voltages at the switchgear are,
R-N - 3.876kV
Y-N - 4.096kV
B-N - 4.047kV
R-Y - 6.271kV
Y-B - 6.282kV
R-B - 6.234kV
What could be the possible reasons?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Over Voltage Ground Relay

09/26/2016 12:48 PM

..."look for electrical distribution systems in which one leg of a 3-phase supply powers both single-phase and 3-phase loads. You may find single phase loads not evenly balanced across the phases. Or, look for in-line reactors installed to correct imbalances. These reactors usually have taps for adjustment, and somebody may have adjusted them. Or, the imbalance they originally corrected may have shifted over time. Circuits with tapped reactors rarely stay in balance indefinitely."...

http://ecmweb.com/content/basics-voltage-imbalance

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Over Voltage Ground Relay

09/27/2016 7:14 PM

"The phase to phase voltages are consistent with each other. The phase to neutral voltages are not constant. Our system is ungrouded system."

If you have an UNGROUNDED system, you have, by definition, no ground referenced neutral. You cannot use this for single phase L-N loads. Any phase to ground voltage measurement is affected by the capacititance to ground, which will vary.

Please hire a QUALIFIED electrical engineer...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Over Voltage Ground Relay

09/30/2016 3:08 AM

In my opinion, 0.3 sec for 10 V it is very low. The system may function at sqrt(3)*3.8=6.6 kV for 1 min- the cables, at least. 20 V and 1 sec it seems to me be more reasonable.

__________________
Julius
Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#4

Re: Over Voltage Ground Relay

09/30/2016 1:35 PM

If the neutral isn't grounded anywhere, then why worry about the neutral to ground voltage?

__________________
Good moaning!
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: Over Voltage Ground Relay

10/01/2016 3:49 PM

As a second opinion:

why do you need a neutral since your transformer secondary windings are delta connected?

The 4th conductor could be a grounding wire[ungrounded?].

However, in your case, for 6.282 kV [phase_to_phase] it has to be only 3.627 kV [symmetric phase_to_ground]. In no case you cannot measure at the same time 4.096 kV maximum and 3.876 kV minimum.

In my opinion, the potential transformer ratio is different: for between phases [R-Y,Y-B,B-R] the PT ratio is 6.6kV/110 V and for phase_to_ground PT the ratio is 7.2kV/110 V.

__________________
Julius
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6
In reply to #5

Re: Over Voltage Ground Relay

10/02/2016 2:09 PM

Sorry. I meant[vice versa]:

for between phases [R-Y,Y-B,B-R] the PT ratio is 7.2kV/110 V and for phase_to_ground PT the ratio is 6.6kV/110 V. However, you have to check the PT ratio any way.

__________________
Julius
Reply
Anonymous Poster #1
#7
In reply to #6

Re: Over Voltage Ground Relay

11/03/2016 1:27 PM

The PT ratio is 6kV/0.11kV. The Potential transformer connected is of star-star (grounded at both sides). The Phase voltage measured at the secondary of the potential transformer is constantly fluctuating but the line voltages are normal. Is it the phenomena of ferroresonance?

Reply
Reply to Forum Thread 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (3); Anonymous Poster (1); Crabtree (1); JRaef (1); SolarEagle (1)