Stuck on Some Calculations

12/26/2016 6:31 AM

Hi all,

I'm stuck on a few calculations, and could use some advice:

1. How does one go about calculating the short circuit level (in MVA) for a three-phase fault on Bus 4?

2. For a solid earth fault on phase R conductor at Bus 4, how would I calculate the current fed into the fault (in p.u. and in kA) and the voltages of the healthy phases at Bus 4?

Thanks in advance!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#1

Re: Stuck on Some Calculations

12/26/2016 10:03 AM

Did you mean to post a diagram or other information about the system containing "bus 4" ??

Look at Wikipedia or other web sources/search engines for information on "3 phase electrical fault" or "earth fault" or "power system fault calculations".

Register to Reply
Guru

Join Date: Sep 2016
Posts: 973
Good Answers: 9
#2

Re: Stuck on Some Calculations

12/26/2016 10:04 AM

Simple, V=0.

Register to Reply
Participant

Join Date: Dec 2016
Posts: 3
#3

Re: Stuck on Some Calculations

12/26/2016 10:17 AM

Apologies, forgot to post diagrams I have been working on:

https://www.dropbox.com/s/zjubb5yupoknwzc/eracs.docx?dl=0

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Stuck on Some Calculations

12/26/2016 11:13 AM

How many points is a correct answer worth?

Register to Reply
Participant

Join Date: Dec 2016
Posts: 3
#5
In reply to #4

Re: Stuck on Some Calculations

12/26/2016 11:31 AM

? Have I missed something here -- is this not a forum to ask questions. I've taken the work as far as I can (see the attached doc), and am having issues with these. If someone has a suggestion for an alternative resource, do let me know...

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: Stuck on Some Calculations

12/26/2016 12:21 PM

It is certainly a forum to ask questions.

You asked a question and so did I.

So far, you have gotten two answers to your question and I'm sure you will get more, from many other people.

My question seems very simple, but only you know the answer. So far you have evaded answering it.

Maybe this will help:

Short Circuit Fault Calculations - Electrical Construction & Maintenance

Frequently asked questions on grounding and ground-fault current

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#7
In reply to #5

Re: Stuck on Some Calculations

12/26/2016 2:28 PM

I have looked at your diagram - at first sight, assuming generator at left is only power source, you need the voltage, impedance and MVA rating of that generator and the impedance, ratio and MVA rating of the the transfos bus1 to bus 2 and bus 4 to bus 5. This assumes impedance of 125 kV lines is negligible.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8
In reply to #7

Re: Stuck on Some Calculations

12/26/2016 3:53 PM

Look again, both generators show line current so both are generating. The thing that stands out the most is that the generator on Bus1 is connected to a transformer with Vector Group Dyn while the generator on Bus5 is connected to a Ynyn, and both feed the same bus! I do hope there's a phase shift in one of those transformers.

Until that little detail is cleared up, nothing can be said...

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#10
In reply to #8

Re: Stuck on Some Calculations

12/27/2016 7:03 AM

Two generators, you are right!

Two independent generators would adjust their frequency and phase to synchronise and meet the phase relations required by the loads and transformers (as do all parallel generators).

Is it a system grown organically from affordable parts or a theoretical example?

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#12
In reply to #8

Re: Stuck on Some Calculations

12/27/2016 8:54 AM

In my humble opinion, since the are two independent sources-it is not a single synchronized grid-and if the phase rotation is the same one could synchronized a second generator with an already energized grid by the first generator.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9

Re: Stuck on Some Calculations

12/27/2016 3:30 AM

As it is already underlined above no equipment data is presented. The loads and short-circuit current levels only it does not permit any accurate calculation.

Generator rated MVA and X"d ,Transformer rated MVA, Zk1, Zo, line R, X1, Xo, PQ source data all these are required.

__________________
Julius
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#11

Re: Stuck on Some Calculations

12/27/2016 8:34 AM

For calculations of this type I use "Inductance Calculations" by Frederick W. Grover

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#14
In reply to #11

Re: Stuck on Some Calculations

12/27/2016 9:15 AM

I agree, it is a very interesting book.

http://g3ynh.info/zdocs/magnetics/appendix/Grover46/Grover_errata.pdf

However, I am not sure it is connected to this required calculation [see o.p.]:“How does one go about calculating the short circuit level (in MVA) for a three-phase fault on Bus 4?”

__________________
Julius
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#15
In reply to #14

Re: Stuck on Some Calculations

12/27/2016 12:58 PM

From this book, one can calculate the energy stored in a bus system. Knowing this energy will permit calculation of the short circuit current under specified fault conditions. We do this when we design high current welding equipment.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#13

Re: Stuck on Some Calculations

12/27/2016 9:03 AM

You can calculate the 3 phase equivalent impedance from the fault data given, according to the (standard) ratio between fault types. I=E/Z

Is not question 2 answered on page 2?

Some algebra to separate the zero sequence impedance from the difference of the double line to ground & single line to ground equivalent fault impedance...

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#16
In reply to #13

Re: Stuck on Some Calculations

12/27/2016 6:55 PM

No algebra is required, any book on symmetrical components will have the sequence diagrams and the equations for all the possible types of faults; i.e., L-G, L-L, L-L-G, L-L-L, and L-L-L-G, in terms of line, phase, and sequence currents.

As presented by OP, there is insufficient information to accurately calculate the short circuit currents.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#17
In reply to #16

Re: Stuck on Some Calculations

12/27/2016 6:58 PM

It's all there, look at all 3 diagrams

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#18
In reply to #17

Re: Stuck on Some Calculations

12/27/2016 9:52 PM

I did, the necessary parameters are not given on the diagram, and I'm certainly not going to back-calculate to find them. Perhaps you can tell me what they are, given the information on the diagrams.

I'm particularly interested in the time dependent machine parameters such as X"d, X'd, Xd, Τf, etc.? How about the transmission line parameters like R+jX (that one is relatively easy), Transformer parameters like rated Voltage, rated MVA, per unit impedance, etc. Then there's the Loads on bus 2 and 4, they all seem to be quite inductive, probably large motors, but we are not told whether the machines are synchronous or asynchronous, nor any of the above parameters that describe them, or if they're just ordinary distribution loads.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#19
In reply to #18

Re: Stuck on Some Calculations

12/28/2016 8:13 AM

You can't calculate the individual quantities, just the lumped effect at the point of the fault. The professor conveniently placed the fault in the same place for all cases, and gave you much more other information that you don't need.

And, to answer the question, you do need to back calculate, that's the whole point.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#20
In reply to #19

Re: Stuck on Some Calculations

12/28/2016 12:52 PM

I agree. If the reported currents are correctly calculated;

If we shall neglect resistances and consider X2=X1

[and take the equivalent reactances X1,X2 and Xo]

Note:

IEC 60909-0 CH.4.2.2 Line-to-line short circuit states:

"During the initial stage of the short circuit, the negative impedance is approximately equal to the positive-sequence impedance, independent of whether the short circuit is a near-to-generator or a far-from-generator short circuit."

I hope the currents are calculated “at initial stage” [subtransient].

I"k2EL2=1.1*VL_L*SQRT((Xo-0.5*X2)^2+3/2X2^2)/(X1*X2+X1*Xo+X2*Xo)

Ik1=1.1*sqrt(3)*VL_L/(X1+X2+Xo)

Put X2=X1

Calculate X1[algebraically] and

Ik3=1.1VLL/sqrt(3)/X1

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#21
In reply to #20

Re: Stuck on Some Calculations

12/29/2016 12:49 AM

Sorry. In I"k2EL2 formula it is an error.

Actually the IEC 60909-0 formula(46) [in complex] is:

I"k2EL2=-j*c*Un*[Z(o)-a*Z(2)]/[Z(1)*Z(2)+Z(1)*Z(o)+Z(2)*Z(o)]

where : j=i=sqrt(-1) ; a=-0.5+i.sqrt(3)/2

If we neglect R the formula remains:

I"k2EL2=-i*c*Un*{iXo-[-0.5+i.sqrt(3)/2)]*X2}/(-X1*X2-X1*Xo-X2*Xo)

I"k2EL2=c*Un*{[Xo-i0.5*X2-sqrt(3)/2*X2]/(-X1*X2-X1*Xo-X2*Xo)

|I"k2EL2|=c*Un*sqrt[(Xo-sqrt(3)/2*X2)^2+0.25*X2^2)/(X1*X2+X1*Xo+X2*Xo)

If X2=X1 then:

|I"k2EL2|=1.1*VL_L*sqrt[(Xo-sqrt(3)/2*X1)^2+0.25*X1^2)/(X1^2+2*X1*Xo)

I'll would solve it by iteration. At first put Xo=0

I"k2EL2=1.1*VL_L*X1*sqrt[(3/4+0.25)/(X1^2) sqrt(3/4+0.25)=1

I"k2EL2=1.1*VL_L/X1 X1=1.1*VL_L/I"k2EL2

calculate Xo from I"k1:

Xo+2*X1=1.1*VL_L/I"k1 Xo=1.1*VL_L/I"k1-2*X1

Recalculate |I"k2EL2|

Suitable adjust X1 in order to fit |I"k2EL2|.

Recalculate Xo etc.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#22
In reply to #21

Re: Stuck on Some Calculations

12/29/2016 1:44 AM

Now another mistake:

Xo+2*X1=1.1*VL_L/I"k1 it has to be: Xo+2*X1=1.1*sqrt(3)*VL_L/I"k1

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#28
In reply to #19

Re: Stuck on Some Calculations

01/02/2017 5:12 AM

You also deserve a star for your initiative!

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#23

Re: Stuck on Some Calculations

12/29/2016 3:45 AM

I think X1=47.8 and Xo=8.87 for a less than 1% error.

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#24
In reply to #23

Re: Stuck on Some Calculations

12/29/2016 8:28 AM

Nicely done!

I think the purely algebraic solution would include the current X/R lumped, probably not at sub-transient conditions, and your results would be at the same time and condition as reported for the original two faults. You could assume fully symmetrical conditions, but at whatever unknown condition the original fault current was reported, your solution would be at those same conditions.

My guess is the 'professor' wanted his students to show their knowledge of the relationship between the driving voltages behind various types of faults, and picked a sneaky way to make them think.

Register to Reply Score 1 for Good Answer
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#25

Re: Stuck on Some Calculations

12/29/2016 8:01 PM

Way too much (unnecessary) math here, so I'm going "old school".

1. No need to calculate, it's already given as 415MVA in diagram 1.

2. As noted above, and given on diagram 2, 2.191kA is the actual fault current. In order to convert that into the per unit system it is necessary to choose some Base Quantities. For convenience we will use 100MVA as Base MVA and 131.93kV as the Base Voltage, from those two we can calculate the Base Current as 100MVA/(√3*131.93kV) = 0.437kA. The actual Amps (2.191kA) divided by the Base Amps (0.437kA) equals the Per Unit Amps, or 5.014pu.

NB- The short circuit values do not include the DC decrement, subtransient, and transient currents, which can only be calculated with additional information, including such things as the appropriate reactances, and the contributions from motors (if any) on the load side.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#26
In reply to #25

Re: Stuck on Some Calculations

12/30/2016 1:13 AM

O.K.I could live with this.

However something is still not so clear.

I don't know what it is 3F [Diagram 1]. I cannot reach more than 367.36 MVA- neglecting resistances.

Vrated=Vactual/pV=122.831/0.931=131.93 kV?

Only in the case the title of the Diagram 2 [ "Solid earth fault;phase to phase"] it has to be only" phase to phase"-then Ik3=Ik2*2/sqrt(3) Ik3=1.728*2/sqrt(3)=1.995 kA and MVA=SQRT(3)* 1.995*120=414.72 [close!] 120 kV?

__________________
Julius
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#27
In reply to #26

Re: Stuck on Some Calculations

12/30/2016 8:29 AM

I don't know why the 3 phase fault current is shown on a load flow diagram, but a quick check on the double line to ground at 365MVA puts it at the right magnitude, good detective work by Mr. RAM

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#29
In reply to #26

Re: Stuck on Some Calculations

01/02/2017 9:43 PM

You're right, it takes a bit of sleuthing to decode these diagrams, especially since 3 phase and single phase quantities are used without clear delineation.

Let's use Bus 1 as an example. The flow into it is listed as 50MW and 57.7MVAR, we can calculate its apparent power (S) as √(502 +582) = 77MVA, the same exercise on Bus 5 yields S=64. Adding them together yields 141, a number that doesn't exist on the diagram; but 3 x 141 = 423MVA which is in the ballpark of those "3F" numbers does, so that must be the 3phase fault current. For simplicity (and ease of typing) it is important to note that I used algebra when in fact these are vector calculations, but since the angles are all relatively small, so the error isn't that great.

NB- a three phase fault (grounded or not) is the largest and easiest to calculate (except under some very special circumstances) since it only involves positive sequence impedances. It's basically just combining the series impedances from the left generator to Bus 4, in parallel with the series impedances from the right generator to bus 4, driven by an infinite bus with a fixed voltage of 1pu.

Too bad the OP has not returned.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Register to Reply 29 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: