ABB UCGDN Tap Changer Drying Process

03/05/2017 4:36 AM

The diverter switch must be mounted directly as soon as removed from the drying chamber. In case of waiting and transporting, it is getting moisture again.

__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: ABB UCGDN Tap Changer Drying Process

03/05/2017 7:04 AM

And your question is?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#2

Re: ABB UCGDN Tap Changer Drying Process

03/05/2017 10:23 AM

The diverter switch was shipped from the factory to the field and assembled. This assemble process was carried out 4 times and the breakdown voltage of the insulating oil in the switch fell down to 16 kV in 3 months. Finally, the switch was dried and assembled near the power transformer and the result was taken.

Every piece of material to be placed in the transformer must be transported to be completely free from air and moisture.

I wanted to share this experience.

__________________
Either exist as you are or be as you look. Rumi
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#3

Re: ABB UCGDN Tap Changer Drying Process

03/06/2017 3:56 AM

Normal. That is why one needs to cycle the oil after build thorough an oil purification system, normally portable units, to dry out the oil, increase the dielectric of the oil, filter out contamination during the previous fill operation, and once completed, the tfx is enegrised, off load, to stay dry and warm.

It seems you have not followed the complete process after build, or followed the procedure when filling the tfx with oil.

Just hire in a small trailer mounted unit and purify the oil. It should take about 12-24hrs depending on the moisture content, to bring the oil back to around 53kV breakdown, if the tfx is small. I recall the breakdown voltage should be around 63kV but check you specs.

Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

engilis (1); IQ (1); TonyS (1)

Previous in Forum: CT Secondary Earthing   Next in Forum: Partial Discharge Test Device

Advertisement