Anonymous Poster

Predictive Testing of SF6

08/25/2007 3:07 AM

We have many 115kV GIS in our industy. We are following vendor recommendation for maintenance. My question:

Is there any testing guidlines of SF6 to predict the condition of breaker inside like oil testing of transformer?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Apr 2007
Location: n. Switzerland
Posts: 133
Good Answers: 6
#1

Re: Predictive Testing of SF6

08/27/2007 2:44 AM

Not unless you open it up and inspect it, and as you surely know, one tries to avoid opening GIS because often you end up with more junk inside it than was there before you opened it...

These guys can help you:

http://www.dmsystems.co.uk/

http://www.pdtech.ch/index2.php?okatID=11

/rf_guy

__________________
Regards, RF_guy
Reply
Power-User

Join Date: Dec 2006
Posts: 442
Good Answers: 32
#2

Re: Predictive Testing of SF6

08/27/2007 12:08 PM

Ion Mobility Spectrometry has been used for this. See:

http://tdworld.com/mag/power_diagnosing_health_sf/

I am involved with a company that manufactures and sells IMS analyzers. They do not presently make an analyzer for this specific application, but may be interested in working with you to develop an analyzer.

If you are interested, let me know and I will get you in contact.

Tad

Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#3
In reply to #2

Re: Predictive Testing of SF6

08/28/2007 10:25 PM

Thank you for the information given in the link .It is quite informative and good to know the latest development. We have been replacing the bottles as per manufacturers schedule . The IR value of Poles give rough idea as to weather the bottle needs replacement earlier than manufacturer's recommendation .Some manufacturers provide gauge to know the SF 6 pressure inside which also can give idea but gas inside but cannot know about contamination of gas.

Reply
Power-User

Join Date: Aug 2007
Location: Heilonjang China. 2 blocks from you
Posts: 109
Good Answers: 5
#4

Re: Predictive Testing of SF6

08/31/2007 3:08 PM

Thanx. Some manufacturers provide guages to monitor the SF6 pressure and also signals that are alarm based to remined you incase the pressure is low.

Also others provide counters to monitor the number of oprating times of the breaker and give recomended operations after which the breaker is taken for maintainace or service.

If the gas leaks then find the leakage source, clear it and refill the breaker, but please never operate a braker whose SF6 pressure is in acritical state.

__________________
poy
Reply