Good day
We are running the conveyor Belt with 22KW, 525V, 30.9A, 4 poles Motor using 22KW 525V VLT Danfoss VSD (FC302). During normal operation, the motor is pulling almost half of its full load (14-15 Amps).
2 motors burnt within 4 days due to over-current/Temperature and the VSD didn't trip.
The motor data was correctly programmed and the Motor Thermal Protection was set on ETR TRIP-1 (Parameter 1-94).
The trip test that i did to Check whether the VSD can trip or not, which i am not sure whether is it the correct method, is that, i changed the motor current settings on the VSD from 30.9A to 10Amps, then i started the Conveyor Belt. during start up, it just flushed current limit on the LCD then keep on running with 14-15 Amps and it didn't trip.
My questions:
1. How do one test the VSD to ensure that it will be able to trip during over current condition?
2. Motor Temperature (parameter 1-9), what is the correct setting on the Motor thermal protection? because there are lots of Trips setting (ETR Trip 1 to 4) and others.
3. what can cause the VSD not to trip during over-current condition? is there any setting that i have missed?
Please assist.