VCB

09/03/2007 5:38 AM

Detection of vacum in vacum circuit breaker?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#1

Re: VCB

09/03/2007 11:03 PM

inspect the bare copper parts through the glass. If there was any air inside they would be tarnished.

if it is a ceramic device, apply a high voltage and see if you get any current flow.

If there is a full vacuum it will not conduct at rated voltage. Any gas inside will undergo breakdown/ionization and a current will flow

__________________
Per Ardua Ad Astra
Reply
Anonymous Poster
#2
In reply to #1

Re: VCB

09/04/2007 1:35 AM

Dear aurizon

"apply a high voltage and see if you get any current flow."

How can we apply HV? Through Meggar? Is it the rated voltage? or How many times the rated voltage -to cause breakdown of gas? Pl clarify.

Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#3
In reply to #2

Re: VCB

09/04/2007 1:47 AM

well, they typically use vacuum relays to switch RF, since high circuit Q can cause peak voltages that would ionize the same sized air gap they use a vacuum path that has nothing to ionize to create a plasma carried spark. Now you can get electrons into the vacuum space, but they would arc around the sides more easily.

If there is air inside 1000 volts might cause a small current to flow as this air gets ionized.

The relay would be megger safe. Test a new relay and then the suspect relay with the same voltage. If they both have zero current, the suspect relay is good. If not, then there may be a gradual leak in the suspect relay and it has slowly filled with air.

__________________
Per Ardua Ad Astra
Reply
Participant
India - Member - New Member

Join Date: Aug 2007
Posts: 4
#4

Re: VCB

09/04/2007 4:07 AM

You can take berak down voltage test of Vaccum intruppter, by supplying high voltage graddully to the intruppter and check at what voltage it trip,from that u can check your braker is healthy or not for your specifed voltage level.

Musef Chisti.

Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#5

Re: VCB

09/04/2007 8:59 AM

Most vacuum breakers do not have provisions for detecting the pressure in the interrupter assemblies, as this would add another weak point for failure of the containment. The simplest test is to open the breaker. If the vacuum is compromised, the interrupter bottle will sizzle, then explode! The contacts are way too close to prevent arcing in air. This is why the manufacturer will always state in the safety notices that the door to the power cubicle (the area containing the vacuum bottles) should be fully secured when operating the breaker.

The recommended test is to remove the breaker from service, then apply at least rated voltage (for example, our 13.8 KV outdoor breakers are rated at 15.5 KV) across the open contacts. A High Potential Tester (Hi-Pot) is normally used for this purpose. If you test the insulation on your own power cables, then the same tester used for the cables will work. The minimum acceptable value of resistance depends on the voltage rating, but is typically 500 to 1000 M-Ohm or greater.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply