D.G set problem

09/03/2007 10:06 AM

I have two DG set of 750KVA in Plant in synchronisation,max limit of current=900amp each.

when load is 1000amp both DG are run at 500amp each,due to this efficiency will reduces or not?

or i can select only one 1000KVA DG for plant .tell me the right thing

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jan 2007
Location: Sitting directly behind my keyboard in Albuquerque - USA
Posts: 592
Good Answers: 19
#1

Re: D.G set problem

09/04/2007 12:02 AM

Keep them as is, load sharing at 500 amp each. This is a very efficient load range. 1000 amp on the 900 amp machine will cause generator winding temperature overheat and may cause engine overload if the engine was sized EXACTLY for 750 kVA at 0.8 PF. If engine was oversized, (example; if 750 kVA at 0.8 PF meant you needed exactly a 10 cylinder engine, and the next size was really a 12 cylinder like a Cat 3412, then you have extra engine power). If your generator was rated at 80*C temperature rise above 50*C but your real ambient is 40*C then you have some extra amp overload capacity. If you generator was rated at 130*C rise above 40*C you will not have any overload capacity in your generator.

__________________
If it eats, it's going to be trouble!
Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#2

Re: D.G set problem

09/08/2007 11:31 PM

Dear Guest, There is no need to do any change in the existing setup. Good luck. Chaterpilar

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire