heater mcb

09/23/2007 2:38 AM

whether i can use 125 Amps mcb for 72 kw,415 volt ,three phase heater beacause 72 kw heater coming 100amps only.or i need to go for higher rated mccb.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: heater mcb

09/23/2007 3:36 PM

Your are correct a 125A CB will suffice:

Assuming unity power factor, the heater will draw 10 Amps

I heater = 72*1000/(sqrt(3) * 415) = 100A

The CB should be rated to 125% of the continuous load:

100A *1.25 = 125A

Register to Reply
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#2

Re: heater mcb

09/24/2007 12:28 AM

All of the above is perfectly correct in theory....however....

Welcome to the Outer Limits!

You mention both MCB (miniature circuit breaker) and MCCB (moulded case CB). 125amps is the absolute upper limit for MCBs. This load sounds suspiciously like a water heater, and these can offer big inrush currents (+50% is typical) when the water is heated fom cold. The MCB will almost certainly be OK, particularly if you use a Type D MCB (motor rated) BUT leaves you with nowhere to go if problems do start to occur. (Note that water heaters can have lower power factor also, and voltages can vary by +/- 10%).

If finances permit, I would prefer to use a 125amp MCCB with an adjustable trip unit. This can be set higher if the water heater starts to misbehave (assuming you also give yourself some leeway with the cable rating).

If possible, always try to design yourself a way out.

Best of luck.

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply Score 1 for Good Answer
Associate
India - Member - New Member

Join Date: Sep 2007
Posts: 26
Good Answers: 1
#3

Re: heater mcb

09/24/2007 2:38 AM

The MCB rating also should be in accordance with the Local ELectricity Authority of that particular region . Different countries have different electricity rules and regulations .

For eg in UAE we follow a thumb rule

1 MCB Rating = TCL * 2 ( for normal loads )

2 For Chillers ,Motors and power facotrs we use MCB rating = TCL * 2.5

In this case 160 A MCCB is recommended.

Register to Reply
Associate

Join Date: Jun 2007
Posts: 28
#4
In reply to #3

Re: heater mcb

09/24/2007 3:57 AM

thanks for the help..........can anybody suggest me any book or site regarding selection of switchgears and design of panels.

Register to Reply
Active Contributor

Join Date: Sep 2007
Posts: 21
Good Answers: 1
#5
In reply to #4

Re: heater mcb

09/24/2007 6:21 AM

Heater elements are considered resistive loads with unity power factor, the actual load current could be calculated from the following equation for a three-phase active power:

KW=SQRT.3 * V * I

"I" therefore equals to KW/(SQRT.3 * V)

72KW at 415V translates to 100Amps or thereabouts.

A 125A MCCB will suffice. I doubt if there is any Mcb rated above 100A.

__________________
One does not need a mirror to look at what one is wearing on the wrist
Register to Reply
Associate
India - Member - New Member

Join Date: Sep 2007
Posts: 26
Good Answers: 1
#6
In reply to #5

Re: heater mcb

09/24/2007 6:54 AM

MCB are there fro 1 A - 125 A , but in this case it is secure to use 125 A MCCB

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); BabyGuinness (1); dhilju82 (2); prasobh83 (1); solaaderinwale (1)

Previous in Forum: If RDID has been tested to be UN-Safe why use it on people?   Next in Forum: ultrasonic drillers

Advertisement