Autotransformer Question

08/25/2018 9:07 PM

Dear sir,

We have a system where there are 6 nos of 50 MVA autotransformer.

They want it like two banks of three phase transformers.

What will be the three phase rating of the auto-transformers? Will it be 150 MVA and 150 MVA ie t banks of three phase (auto) transformers?

Regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster #1
#1

Re: Autotransformer.

08/25/2018 9:25 PM

These are: 132/220 kV auto-transformers.

Regards,

Reply
Power-User

Join Date: Sep 2016
Location: SPAIN
Posts: 233
Good Answers: 13
#5
In reply to #1

Re: Autotransformer.

08/27/2018 12:37 AM

Please keep any not relevant information for yourself.

__________________
Building the future!
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Autotransformer.

08/25/2018 9:52 PM

No homework..... It would be 50 MVA in 3 phases...The current would be tripled...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Anonymous Poster #1
#3
In reply to #2

Re: Autotransformer.

08/26/2018 12:29 AM

Is input MVA equals to output MVA in autotransformer? is 150 MVA in parallel with 150 MVA make it 300 MVA auto-transformer rating for our case of 132/220 kV step up auto-ransformer?

Regards,

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4
In reply to #3

Re: Autotransformer.

08/26/2018 6:08 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6
In reply to #3

Re: Autotransformer.

08/27/2018 5:07 AM

No, input MVA is not equal to output MVA for any transfo, the input carries the magnetising current as well as the transformed secondary current.

Transformers are rated [what is written on "Rating Plate"] by the output MVA. For transfos of MVA size, magnetising current is around 5% of full load: but for "plug-top" transfos rated 1VA, no-load VA may be twice the output VA.

I cannot see your arrangement. I suppose that each phase has two 50 MVA transfo in parallel. That is 100 MVA per phase. With 3 phases, that makes 300 MVA.

There is an assumption here that the paralleled transfos are so similar in impedance and voltage ratio that any circulating currents due to small difference of terminal voltage on-load do not affect the rating. A purchase of 2 or more transfo to operate in parallel must make it clear they are to operate in parallel, unless the whole specification includes ratio & impedance tolerances (& loss due to circulating currents) OK for parallel operation.

Since a 3 phase system is not made to be used as single phase, a 3 phase transfo (or group of transfos, operating as one) is rated by its 3 phase capacity, which is the total power it can deliver to a consumer.

Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#7

Re: Autotransformer Question

08/28/2018 1:05 PM

Yes, the 6nos single phase auto transformers will be 2nos three phase banks of 150MVA rating each. You are right.

__________________
Raghunath
Reply