i have a question regarding the calculation of stresses on busbar in low voltage switchgear due ti short circuit currents.

assume the height and thickness of parallel bus bars, for example is 1 bar of 1/4" x 4" per phase, in a 3 phase system with the bars parallel to one another with the 4" sides facing:

there is an article which details calculation of forces " #162 electrodynamic forces on busbars in lv systems", the artical wa published by merlin gerin and identified as the cahier technique.

the artical seems to indicate that the forces are directly proportional to "dwght's constant". this constant is represented in a chart. the chart indicates that:

a. the farther the busbars are away from one another, for a given dimension of busbar, the greater are the electrodynamic forces.

b. the smaller the dimension of the facing sides of the busbars with respect to the thickness of the busbar, the greater the electrdynamic forces.

do you feel that the above is correct, or do you feel that the formula was mis-stated in the article, and the relationships should be inversely proportional?

i would appreciate it if you can respond.

thank you.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: electromagnetic forces on busbar in lv switchgear

09/27/2007 12:09 AM

i READ THAT AND IT SEENS TO ME THAT THERE SHOULD BE MORE TO CONSIDER THAN JUST WHAT WAS WRITEN! pROPORTIONAL? Perhaps yes, but absolutily NO! no matter what "Formula" one uses for figuring materials as such one should remember one thing and one thing only! Molecular structure of any substance on earth caries a certain amount of "power" of one form and we humans call this electricity!

So answer that: NO! each bar was made different from the other! There will be a difference in electromagnetic force for each material made! then wheather they are closer or not does not matter!

Reply Score 1 for Off Topic
Commentator

Join Date: Mar 2007
Location: Chicago suburbs, USA
Posts: 73
Good Answers: 21
#2

Re: electromagnetic forces on busbar in lv switchgear

09/27/2007 12:48 AM

Dwight's chart provides an "adjustment" for forces between conductors that are not "filamentary". Because current spreads across a larger area, the forces between a pair of conductive straps/bus bars tend to be less than that for a pair of filamentary conductors separated by the same distance. What Dwight's chart basically says is that, as you separate the busbars, they behave more similarly to a pair of filamentary conductors so that the correction factor ("k") approaches unity. Herbert Bristol Dwight originally presented a similar set of curves in his book "Electrical Coils and Conductors", McGraw-Hill, 1945 (a fairly scarce title now).

__________________
Stoneridge Engineering - Wreaking Havoc with Electrons for over 40 Years!
Reply
Associate

Join Date: Dec 2005
Posts: 39
#3
In reply to #2

Re: electromagnetic forces on busbar in lv switchgear

09/27/2007 9:16 AM

Sir, you seem to be very well informed on this matter. The original question seems a bit vague. This drew my attention, as I work for a TelCo that has power equipment dating back to cir. 1970. We rectify 3-phase delta 240AC to (-)54VDC. We average about 1200-1400 amps that float 3 parallel strings of flooded PbCa cells. We push all of this current to the Main Fuse Panel via 2 buss bars..each buss consists of 4 bars of 4" x 1/4" Cu. approx 30' inside the power room. From there it is sent to the switching equipment via multiple runs of 750 MCM cables of about 150' in 1 over head cable rack.

I have been wondering just how 'large' and robust of an electromagnet field is produced, and whether or not itcould produce malicious EMF in nearby cables or digital equipment... you seem to be the first person that I have confidence in your opinion..thanks

__________________
Life is a grinder, whether it wears you down or sharpens and polishes you up depends on what you're made of.
Reply
Commentator

Join Date: Aug 2007
Posts: 86
Good Answers: 2
#4

Re: electromagnetic forces on busbar in lv switchgear

09/29/2007 4:09 PM

If our enquirer has to ask if any force is directly proportional to the distance between the bodies involved,then I dont think he should do any engineering let alone busbars.

I hope he doesnt get any further from me or the repulsive force will become unbearable.

Reply
Guru

Join Date: Jul 2006
Location: Silicon Valley
Posts: 5356
Good Answers: 50
#5
In reply to #4

Re: electromagnetic forces on busbar in lv switchgear

09/30/2007 4:40 AM

Well aren't we cranky this morning, Mister Poopy Pants!

__________________
"Perplexity is the beginning of dementia" - Professor Coriolus
Reply Off Topic (Score 5)
Anonymous Poster
#6
In reply to #4

Re: electromagnetic forces on busbar in lv switchgear

10/01/2007 3:16 PM

please note that the problem exists in that the constant seems to indicate that the forces are inversely, not directly proportional. - you might try to read before you write.

Reply
Associate

Join Date: Dec 2005
Posts: 39
#7
In reply to #6

Re: electromagnetic forces on busbar in lv switchgear

10/01/2007 3:24 PM

my grandpa used to have a saying about flies and handles but for the life of me, I just can't seem to remember all of the specifics....

__________________
Life is a grinder, whether it wears you down or sharpens and polishes you up depends on what you're made of.
Reply Off Topic (Score 5)
Commentator

Join Date: Aug 2007
Posts: 86
Good Answers: 2
#8

Re: electromagnetic forces on busbar in lv switchgear

10/02/2007 7:23 PM

For exhaustive treatment of busbars,including the function to calculate 'k' the proximity factor,which has more terms in it than rocket science,(Dwight, 1917) go to:-

www.cda.org.uk/megab2/elecapps/pub22/sec1

If you want only info on electromagnetic stresses in place of 'sec1', put 'sec6'

This is a mind boggling treatise on busbars,by the Copper Development Association.I've never found out how many pages it has,I just dip into the bit I need,it even gives design data for hex insulated systems up to 32kV and 400kVA.Stand well back before switching on.

Reply
Reply to Forum Thread 8 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); BertHickman (1); LocTest Chris (2); oldeng (2); vermin (1)

Previous in Forum: Rated Torque of a Servo Motor?   Next in Forum: Flowrate to Drive DC Motor?
You might be interested in: Busbars and Busways, Panelboards and Switchgear

Advertisement