Multimotors on a starter

10/04/2007 11:43 PM

I ran across an air condtioning unit that had three condensor fan motors wired through two contactors. They have one leg of all three motors running through one contactor and the other leg of each motor running through the other contactor. The contactors are three phase and the motors are single phase. The contactors are controlled from the same point so they both energize and de-energize at the same time. My question is; Is this legal according to the NEC? Thanks for your help in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Apr 2007
Posts: 414
Good Answers: 19
#1

Re: Multimotors on a starter

10/05/2007 1:25 AM

Article 430 of the NEC deals with motor circuits and controllers. Read it. It isn't very long. You should contact the Building & Safety department of your city or county and ask which edition of the NEC they follow. Read that edition to see if it forbids this arrangement. If both controllers meet all the other requirements, viz. capacity, proper grounding, etc. this setup shouldn't be disallowed.

Of course, if this installation will be subject to some sort of inspection, or if you suspect there is reason for concern with the other wiring, read the rest. The NEC exists to protect life and property, and many (not all) of the requirements are just common sense. Better to correct an out-of-code situation before it becomes a problem.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2
In reply to #1

Re: Multimotors on a starter

10/05/2007 2:31 AM

Excellent answer. I'll just add that it is not uncommon in the HVAC industry to see OEMs use cost cutting methods and components that would be considered "questionable" engineering practice but which are technically legal. A case in point is that you will also frequently see them use 2 pole contactors to switch 3 phase loads. Bad form, but not illegal.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Anonymous Poster
#6
In reply to #2

Re: Multimotors on a starter

10/08/2007 10:30 AM

Dependant upon 3 phase type.

Would work on Wye but not on Delta connection........two pole contactor definately illegal on Delta.

MR. GUY

Register to Reply
Participant

Join Date: Sep 2007
Posts: 4
#4
In reply to #1

Re: Multimotors on a starter

10/05/2007 11:38 PM

Thank you for your input.

Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#3

Re: Multimotors on a starter

10/05/2007 3:26 AM

sounds like both contactors disconnect power on each leg of the single phase motors,

where is the hazard or problem,? most home 220 volt air conditioners use a single pole

contactor perry

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#5

Re: Multimotors on a starter

10/06/2007 3:13 PM

Sounds like you are dealing with equipment supplied from a manufacturer (compared to something built on site). If this equipment is independently evaluated by a testing organization and listed by them, such as Underwriters Laboratories (UL), then the National Electrical Code normally accepts them as an approved factory assembly. The code requirement then is to apply and install them in accordance with any factory instructions and any limits from the listing.

Many times, the condenser fan motors will have their own internal overload protection, so there is no need for providing this within the motor controller. Since these are single-phase motors, the situation you describe appears to be OK. I assume that the contactors are rated for an inductive load, and sized to carry the motor nameplate amps. Just make sure that any replacement items are capable of doing the same job that the originals did.

--JMM

Register to Reply
Participant

Join Date: Sep 2007
Posts: 4
#7
In reply to #5

Re: Multimotors on a starter

10/10/2007 6:34 PM

Thank you all for your input

Register to Reply