150Hp Motor

10/10/2007 9:59 PM

can a 200KW Generator run a 150Hp pump motor using softstarter

Register to Reply
Pathfinder Tags: 150Hp Motor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: 150Hp Motor

10/11/2007 2:33 AM

Not likely. The general rule of thumb is that you need for the generator kVA to be 1.5 - 2x the motor HP (single motor application). So that makes it 225kVA minimum, i.e. for an uncoupled motor or something that needs little torque to start (pump, fan) but it also depends on the load. You may need more.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Commentator
Egypt - Member - Ahmad Samak

Join Date: Sep 2007
Location: Alexandria, Egypt
Posts: 86
Good Answers: 1
#2

Re: 150Hp Motor

10/11/2007 4:57 PM

When an electrical motor's rated power is given by Hp, then you have to know that this is the shaft (output) power, on the other hand, if the power of a motor is given by Kw then it is the input power.

As your motor's power is given by Hp, divide it by the efficiency to know the required input power to the motor (i.e. the output power from the generator). However, the efficiency of electrical motor is almost around 90%.

For DOL (direct on line motors), the answer of JRaef is fair. In case of soft starter, your generator can easily run that 150 Hp motor whatever the mechanical load is. That is, even if the generator is pre-loaded with the difference between full-load and motor rated power.

Good Luck... Samak

Register to Reply
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#3

Re: 150Hp Motor

10/12/2007 12:28 AM

The rated motor power is not necessarily equal to the real consumed power. If your motor does not use the whole rated power your generator might be able to drive it.

__________________
Aged man is not old man...
Register to Reply
Guru

Join Date: May 2007
Location: Ohio. USA
Posts: 578
Good Answers: 30
#4
In reply to #3

Re: 150Hp Motor

10/12/2007 8:34 AM

This is a good point. I have surveyed several electric motors recently in the 50 to 200 HP range that based on the amperage were operating far below FLA and rated HP. Do you have any similar pumps operating in a plant that you could effectively use their information to truly project actual required running HP, running amps and start up amps? Implementing something like this requires extra caution and safeguards though. If you haven't bought the motor yet maybe you don't really need a 200 HP motor. Is it a case where the pump manufacturer shows that to use ALL the pumps capacity 200 HP is required? These are just some of my random thoughts.

__________________
Everything I know about opera I learned from Bugs Bunny
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#5

Re: 150Hp Motor

10/12/2007 10:58 AM

Is this a continuous duty pump? Constant speed or variable speed? Type of pump, positive displacement, vane, etc? Starting head pressure or starting torque? Location, pad mounted, down-the-hole, etc? It would be good to know all the facets of the operation to give the best advice. If it is continuous duty pad mounted pump, why not just use a direct drive from the power source (engine, steam turbine, etc) to the pump?

Register to Reply
Anonymous Poster
#6

Re: 150Hp Motor

10/12/2007 4:34 PM

It takes a great deal more power to start the motor bring up the load than to pull the load at rated power.

If you can decouple the load with a clutch, have a small motor to spin up the big motor then turn the electriecty on. Then slowly put the load on the motor you can use a lot smaller generator but you need a lot smarter operator.

A 150 hp 3 phase motor is abut 2.5 feet in diameter and 3.5 feet long and draw a lot of current on start up. I don't know how many horse power the wind tunnel at Texas A&M has but it used to have to give the power company 3 day notice when it would start up and could only start between 3:00 and 4:00 am in the morning.


Gordon

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: 150Hp Motor

10/13/2007 2:20 PM

Wind tunnels ar in the neighborhood of 5000 to 15000HP, a little bit different that what we were discussing.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Aug 2007
Posts: 16
#8

Re: 150Hp Motor

10/15/2007 1:10 AM

hi everyone,

i'm a layman on this area, but as i know 1hp nearly equals 746w, so 150hp equals about 111kW, it should be fine using this generator.

Register to Reply
Anonymous Poster
#9

Re: 150Hp Motor

10/15/2007 2:17 AM

Hi everyone,

One KW is exactly 1.36 HP. This mean that 150HP is equal to around 110KW.

Maybe I this will help you to solve the problem ;)

Register to Reply
Register to Reply 9 comments