Anonymous Poster #1

Current Transformer Specifications

06/20/2019 10:56 AM

While specifying current transformers,

1. Why should the CT winding resistance should be specified for PS Class CTs? I understand it should be less. Why should it be specified by purchaser? Don't the manufacturer arrive at his value based on the design?

2. Why the magnetising current should be less than 30mA as most of the specs calls for it? Why not more than that?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
7
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Current Transformer Specifications

06/20/2019 9:11 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Good Answer (Score 7)
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 807
Good Answers: 65
#2

Re: Current Transformer Specifications

06/24/2019 6:15 AM

Here is some information you find of value on the specifications of CTs.

https://electrical-engineering-portal.com/learn-how-to-specify-current-transformers

The CT secondary resistance is specified to ensure that at a fault of x times nominal current the CT secondary current will reflect the x times primary fault current without saturating or failing to be able to drive the secondary current into the protection devices. If a fault of 20 times normal current flows in the primary then the protection CT must be capable of delivering 20 times current into the protection relay to drive the relay to trip in a proportionally shorter time.

Normally by specifying the class and type of CT as well as the working voltage, Primary and secondary current, accuracy, then the manufacturer will provide the correct CT.

However one should always test the CT for compliance to the values as it is not unheard of to find out of spec items supplied. I worked in a test and compliance section for a number of years and every CT, meter and relay was tested before installation and there were rejections for non compliance.

__________________
Hare today, goon tomorrow!
Reply