Reverse Polarity Light when on Generator

07/20/2019 8:01 PM

A friend has a 60 ft, 18 month old Cat. It is fed by a single 50 Amp 120 VAC 60 Hz shore tie. It also has two 4.5 KW sine wave inverter chargers wired in parallel. They are fed by a 10KW Lithium Ion battery bank. Basically these work as large UPS, when the shore tie or generator drops off line, these immediately take up the load. The starting batteries are not included in this. All of these work fine. There is also a 15 KW Northern Lights Generator Output is 230 VAC 60 Hz split phase. I don't have the model number, but will get it Monday as well as contacting them.

There is no "as built" for the boat, it has been requested, but has yet to arrive. The genset output is fed to two 40 Amp circuit breakers labeled "Gen 1" and "Gen 2". The issue is the Gen 2 reverse polarity light flickers on dimly.

All the AC devices, including the 3 A/C units are 115 VAC 60 Hz.

I have checked all the outlets with a reverse polarity plug. They all check good. In addition the boat is wired like a shore side installation. The White (Blue it is a South African boat) is tied to ground, unlike military vessels.

First, Is this even possible? The builder has stated there must be a "loose wire". I went through the panel and GenSet and found none. I'm thinking that if there are no reverse wired outlets and all the devices check good. ( disconnect them and see if the light goes out) there is no problem. If all checks well, I see the only solution would be to wire each phase of the generator to each inverter, and allow the inverters to power the boat. Of course I will have to make up a new Buss transfer switch as Double pole double throw if it isn't already done this way

Any ideas will be welcome. This post is a weekend first, it has nothing to do with colon cleansing and super vitamins.

Thanx in advance

Register to Reply
Pathfinder Tags: Split Phase
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Reverse Polarity Light when on Generator

07/20/2019 8:53 PM

Sounds like the gen 2 wiring may be reversed...when off inverters sometimes reverse the polarity, so when it's off everything appears normal, but then on startup the problem surfaces...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Off Topic
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2
In reply to #1

Re: Reverse Polarity Light when on Generator

07/20/2019 9:10 PM

The wire to the rev pol light could be shorting...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#5
In reply to #1

Re: Reverse Polarity Light when on Generator

07/21/2019 9:46 AM

That's what I was thinking, but I think the reverse polarity tester plug should have shown that. My next step, next time I work on it, I'm going to just use the Gen 1 circuit. And see what doesn't work. Then do the same with Gen 1. The seeming "randomness" leads me to believe, that it is indeed a stray current caused by some device somewhere. This is definitely going to incur an overnite to St T!!!

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#3

Re: Reverse Polarity Light when on Generator

07/20/2019 10:37 PM

It would be interesting to see the configuration of the change over network that allows the 2 phase generator inputs - and inverters - to take over from the single phase shore input, ie. how have they isolated the two phases and made the single phase shore power then supply all items on board?

I'm a bit confused as to the purpose of RPIs on the genset, as they are normally there to guard against shore power reversal - the onboard connections, once done would not be expected to be able to be accidentally reversed and would therefore not require RPIs

The two phase output from the genset will probably have a common neutral, and the RPI would be connected between the neutral and ground, so a reverse polarity would more likely be evident on both phases, so, without access to a cct diagram it's hard to interpret what is occurring.

Having said that, reverse polarity indicators should have at least 25K ohms of series resistance to prevent stray currents causing spurious indication of a fault - are you satisfied that all of your indicators have this resistance.

You state that the light is only dim, so it is possible that stray currents rather than a true fault are the cause. Maybe you could try increasing the resistance to see if that helps.

I'm not sure what you mean in your last paragraph where you suggest supplying the inverters from the generators - do you mean via suitably sized DC chargers, as the inputs to the inverters would be DC not AC, and most likely down around 12V or so.

Register to Reply
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#4
In reply to #3

Re: Reverse Polarity Light when on Generator

07/21/2019 9:41 AM

All good points, especially these. It would be interesting to see the configuration of the change over network that allows the 2 phase generator inputs - and inverters - to take over from the single phase shore input, ie. how have they isolated the two phases and made the single phase shore power then supply all items on board?

I'm a bit confused as to the purpose of RPIs on the genset, as they are normally there to guard against shore power reversal - the onboard connections, once done would not be expected to be able to be accidentally reversed and would therefore not require RPIs

The two phase output from the genset will probably have a common neutral, and the RPI would be connected between the neutral and ground, so a reverse polarity would more likely be evident on both phases, so, without access to a cct diagram it's hard to interpret what is occurring.

It is split, not two phase, and the "center tap" of the genset does go to ground.

Having said that, reverse polarity indicators should have at least 25K ohms of series resistance to prevent stray currents causing spurious indication of a fault - are you satisfied that all of your indicators have this resistance.

I will indeed check that

You state that the light is only dim, so it is possible that stray currents rather than a true fault are the cause. That is what I'm thinking, and hope not. There is an outdoor fridge, ice maker, with outlets for a blender etc. Stray currents could be lethal.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#8
In reply to #4

Re: Reverse Polarity Light when on Generator

07/23/2019 11:42 AM

Capacitive coupling is the likely culprit, two wires run next to each other for a distance, one with ac, will couple enough current to light a high enough impedance lamp. If you do have reverse polarity, the lamp will come on full brightness. A loading resistor across the lamp will make the lamp dimmer, if it is really bothersome.

Register to Reply
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#9
In reply to #8

Re: Reverse Polarity Light when on Generator

07/23/2019 1:54 PM

Thank you: I sort of agree with your diagnosis. Any ideas as to why it only appears on one of the RPL's?

I have contacted Northern Lights...........awaiting there response. Didn't even get a "do not reply we will respond within 1-2 business days".

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1377
Good Answers: 105
#10
In reply to #9

Re: Reverse Polarity Light when on Generator

07/23/2019 5:22 PM

My guess would be the routing of the wires, one closer to a hot lead than the other, or longer...(?). Possibly a difference in the indicator manufacturing tolerances, don’t know if you can interchange them...

Register to Reply
Commentator

Join Date: Oct 2012
Posts: 85
Good Answers: 1
#6

Re: Reverse Polarity Light when on Generator

07/22/2019 7:01 AM

I am confused by your term 2 phase. My house (like most United States houses) has single phase power. Two hot wires and a neutral. Voltage from either hot to neutral is 115 volts. Voltage between two hots is 230 volts. Is this what you refer (not exactly correctly) to as 2 phase?

Register to Reply
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#7
In reply to #6

Re: Reverse Polarity Light when on Generator

07/22/2019 12:55 PM

No sir, someone else did. What you, me, and the boats generator are is "split phase". Two phase is like three phase, but is/was used in lighting circuits. Three phase has the phases 120 degrees separated, two phase is 90 degrees.

Register to Reply