How can I calculate voltage drop for a bus bar?
Re: BUS BAR
10/30/2007 7:10 AM
Do you know Ohm law?
it can be suitable to the bus bar.
Re: BUS BAR
10/30/2007 7:24 AM
Similar to voltage drop calculation for cables you need:
- Busbar cross sectional area per each phase
- Busbar Length
- Busbar material (Copper or Allminium) then you can have the Ω/m value in standard conditions (of ambient temp. and altitude)
- Operating temperature and site altitude for calculating derating factors
A thousand-mile journey begins with the first step.
Egypt - Member - Ahmad Samak
Re: BUS BAR
10/30/2007 11:34 AM
I agree with you, but I think it should be noted that bus bar length is somewhat ambiguous to be defined. Such a length differs from that of cable. The effective length of a bus bar is defined by the path of which the current will flow, i.e. it is defined by the distance between the current-input point and the current-output point. Sure there may be several input/output points, this may be treated superposition or other arithmetic facilities.
Samak
Re: BUS BAR
11/01/2007 7:04 AM
Agree