Power transformer windings and transient voltage damage

11/01/2007 4:34 PM

Please can someone give me a technical explanation:

With say an 11kV autotransformer, why do hf transients appearing at the transformer cause damaging over-voltages across the last few turns at the neutral end of the winding, rather than being linearly distributed across the winding as a whole ?

Is this something to do with the distributed parameters of the winding (and especially the capacitance) acting something like a transmission line ?

Many thanks

Register to Reply
Pathfinder Tags: transformer transients
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Mar 2007
Location: Chicago suburbs, USA
Posts: 73
Good Answers: 21
#1

Re: Power transformer windings and transient voltage damage

11/02/2007 1:35 AM

The distributed inductances and capacitance of each turn to its neighbors, to other winding layers, to the LV winding, and to ground form a complex transmission line-like system. The result is that the transient voltage distribution across the HV winding is always nonuniform, with a shape that's highly dependent upon physical construction of the transformer and the risetime, shape, and duration of the incoming transient.

With a grounded neutral, incoming transients tend to cause highest turn-turn stress to appear across turns nearest the HV end of the winding. However, it's possible to develop similar voltage stresses on the neutral end of the winding under certain (chopped wave) transient conditions in systems that use a grounded neutral. In a system with an ungrounded neutral (i.e., star-star configuration) similar incoming transients can generate very high transient voltages on the neutral end of the winding. In either case, these conditions can occur when a nearby lightning strike create a high voltage impulse shortly followed by a bushing flashover.

An excellent review of the effects of lightning impulse, chopped wave, and oscillatory transients on power transformer winding voltage stress can be found in the newer editions of the J&P Transformer Book and in the technical literature.

__________________
Stoneridge Engineering - Wreaking Havoc with Electrons for over 40 Years!