Transformers Question

07/24/2020 8:44 AM

Dear all

unit transformer (18/400)KV the phases is(R,S,T) connected to the generator.the other transformer also (18/400) KV but the phases opposite (T,S,R).can replace the second transformer instead of the first transformer without transport between the phases R & T in second transformer

thanks for all

Register to Reply
Pathfinder Tags: transformers
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#1

Re: transformers

07/24/2020 8:58 AM

If I understand your question, the answer is "No". You have to have the correct phase rotation to the load. Otherwise, 3 phase motors will turn backward.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2
In reply to #1

Re: transformers

07/24/2020 11:50 AM

But I love seeing large machines crashing into stop blocks and cutting edges spinning away from the material instead of into it.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#3

Re: Transformers

07/25/2020 12:27 AM

I assume you are talking about the markings on the transformer bushings, and not the phase relationship throughout the plant.

A single unit transformer, (not paralleled with another transformer), does not care about phase rotation. It will send the power through as it receives it.

If you connect the transformer markings reversed on the primary, and they end up reversed on the secondary (as we would expect of a standard unit), it will work fine. Just follow the system phasing through the transformer, generator phase 1 connects through transformer to phase 1 of switchyard transmission bus.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#4

Re: Transformers

07/25/2020 2:17 AM

When it comes to generator transformers, it doesn't matter if two terminals are interchanged, as the generator phase matching will ensure synchronising can still be done.

However, the problem could arise at the auxiliary switchboard level, if the auxiliary switchboards are supplied from the generator terminals and the two auxiliary switchboards have a tie feeder.

So, ensure that the generator transformer vector group test is done and the winding connections are identical for both the transformers.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

raghun (1); redfred (1); Rixter (1); rwilliams (1)

Previous in Forum: Surge Capacitor or Surge Arrestor in Switchgear Instead of Motor Side   Next in Forum: EMI/EMC Tests on a Simple Power Supply Panel

Advertisement