11/12/2007 8:45 AM
I've been given a bit of a problem... 960,000 sq. ft. building (almost 30 mill cu. ft.) of manufacturing. Inside, about 10 heat treat lines, 4 Endothermic gas generators, Lots of heat, to say the least. The real problem... right now, we've got about 1/2 to 3/4 air changes per hour on the supply side and the building is approximately 1 mill cfm negative, with some CO Problems developing in the winter, once the 'summer' ventilation supply air is shut down. What kind of luck has the collective had with the use of 'run-around' systems to supply heat to ventilation units? Heat Wheels are out of consideration due to the amount of dirt and dust.
thanks!
Twangy
Pathfinder Tags: Energy industrial ventilation
Engineering Fields - Piping Design Engineering - New Member
Re: Energy Reclamation from HT Furnaces for Industrial ventilation
11/13/2007 12:53 PM
A wet based system may work for you. Heat recovery coils can collect the heat and transfer it to a storage tank. Then feed fan coil type make-up air units to condition the incoming air. Something like boiler economizers can be used on the exhaust stacks of your furnaces. You can use an ethylene glycol and water mixture as your heat transfer medium. Find your Rapid Engineering Rep and he can supply the AMU's with hot water coils and direct fired N. Gas for back up heat.