Drain System for Air Handler

12/04/2007 11:28 AM

Hello I wanted to know if you can send me reference on how to design a drain system for an air conditioning Air Handler unit, which considerations do I have to take care of

Regards

__________________
Tu conoceras la Verdad y la Verdad te hará Libre......Jesus
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Nov 2007
Posts: 18
Good Answers: 1
#1

Re: Drain System for Air Handler

12/05/2007 3:29 PM

for a typical 92F db / 78F wb (Ft. Lauderdale), you can use 0.122gpm/ton of cooling, or for a 10 ton unit = .122 GPM

Register to Reply
Power-User

Join Date: Mar 2007
Location: San José, Costa Rica
Posts: 102
#2
In reply to #1

Re: Drain System for Air Handler

12/05/2007 7:12 PM

ok, thank you what about the column; it is correct to leave the difference in the siphon between the lower side and the pipe that goes in to the drain basin a difference in height similar to the static pressure of the air handler??

__________________
Tu conoceras la Verdad y la Verdad te hará Libre......Jesus
Register to Reply
Active Contributor

Join Date: Nov 2007
Posts: 18
Good Answers: 1
#3

Re: Drain System for Air Handler

12/06/2007 8:00 AM

add an inch or two to the trap above the total static pressure.

Register to Reply
Power-User

Join Date: Mar 2007
Location: San José, Costa Rica
Posts: 102
#4
In reply to #3

Re: Drain System for Air Handler

12/06/2007 3:28 PM

thanks a lot

__________________
Tu conoceras la Verdad y la Verdad te hará Libre......Jesus
Register to Reply
Power-User

Join Date: Mar 2007
Location: San José, Costa Rica
Posts: 102
#5
In reply to #3

Re: Drain System for Air Handler

12/06/2007 3:34 PM

One last question the height of the trap equals total pressure plus one inch or two as you said??

__________________
Tu conoceras la Verdad y la Verdad te hará Libre......Jesus
Register to Reply
Active Contributor

Join Date: Nov 2007
Posts: 18
Good Answers: 1
#6
In reply to #5

Re: Drain System for Air Handler

12/06/2007 3:42 PM

yep.. that'll keep a bit of water in the trap

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: Drain System for Air Handler

12/11/2007 3:22 PM

thank you

Register to Reply