Solid Insulation Switchgear - 15kV

07/13/2022 12:59 PM

Hello

We proposed a 15kV switchgear with vacuum interrupters inside an SF6 insulated enclosure for a project. This is the tech we have used for the past 45 years.

The customer has requested we look into a solid insulated gear with vacuum interrupt. Although the technology has been around for a while, we have limited experience with it.

Anyone have any first hand experience? If so what are your impressions?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Solid Insulation Switchgear - 15kV

07/13/2022 11:08 PM

Although I don't have any direct experience, as you requested, with solid insulated switchgear, I found some info to peruse while you wait for somebody who does....

..."All live parts in the main circuit are molded with epoxy and then covered with a conductive layer connected to the earth. The complete solid insulation method will prevent a one-line earth fault, if it occurs, from developing into a between-phase short-circuit incident."...

...."The footprint is nearly 50% of that of conventional cubicle type switchgear, allowing the whole switchgear panels to be transported. Technologies to achieve high reliability and labor-saving will reduce the frequency of regular inspections that requires the shut-down of the main circuit down to once every six months ."...

https://www.meidensha.com/products/energy/prod_01/prod_01_04/prod_01_04_01/index.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#2

Re: Solid Insulation Switchgear - 15kV

07/14/2022 12:10 AM

I have specified & installed with contract electricians 15kV switchgear since about 1974, many lineups, GE and Westinghouse, some Allis-Chalmers, and seen many more, all between 500 and 1000MVA interrupting rating. These all have solid insulation systems which were trouble free for decades. 15kV seems awful low for a gas insulated system, I always assumed the complexity & cost would only make sense at 69kV and up, unless you had a serious space problem. These breakers, air magnetic, may have a softer interruption than vacuum breakers, but the application of surge arresters necessary to protect load equipment would always be required, so there was no consideration necessary for the switchgear insulation. So not sure what would drive an engineer to specify a GIS at 15kV level? I think 15kV switchgear insulation was typically rated 95kV BIL.

Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#3

Re: Solid Insulation Switchgear - 15kV

07/14/2022 5:49 AM
__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Feb 2014
Posts: 10
#4

Re: Solid Insulation Switchgear - 15kV

07/14/2022 4:15 PM

Thanks for the replies, we do a lot of IEC spec SF6 MV switches as they are very compact units. When space allows we also do ANSI metalclad air insulated gears with air magnetic CB´s.

We are concerned of the service life for the 15kV class SIS switchgears.

Thanks for the links to the writeups, I had read them prior to posting and found them very informative.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#5
In reply to #4

Re: Solid Insulation Switchgear - 15kV

07/14/2022 6:20 PM

Is the insulation system different than earlier designs from 40+ years ago? Typical installation included air conditioned room with filtered air makeup, positive pressure room, and in extreme cases, charcoal filtered air systems.

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

PALER (1); Randall (1); rwilliams (2); SolarEagle (1)

Previous in Forum: Lightning protection calculation   Next in Forum: Data for RH13 GI 9344 diode

Advertisement